    Hi all has anybody used this specific drop in replacement i would appreciate any feedback on performance. I need to replace 22 Gel batteries that reached end of life with Lifep04 and had these units in mind.
    Click image for larger version. 

Name:	GETPOWER-HUBBLE-S-120-.jpg 
Views:	844 
Size:	13.0 KB 
ID:	8544
    Click image for larger version. 

Name:	GETPOWER-HUBBLE-S-120-spec-1232x800.jpg 
Views:	852 
Size:	79.1 KB 
ID:	8545

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Not sure if you mean 22 individual units or 22 feeding one UPS/Inverter

    Most of the drop in replacement type batteries have limitations with regards to connecting in parallel and also max voltage when connecting in series

  3. #3
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    Quote Originally Posted by GCE View Post
    Not sure if you mean 22 individual units or 22 feeding one UPS/Inverter

    Most of the drop in replacement type batteries have limitations with regards to connecting in parallel and also max voltage when connecting in series
    Sorry it is actually 24 100ah gel batteries 8 batteries per bank and 3 banks parallel to a Microcare 8kw bi- directional inverter. 3 banks as illustrated in drawing below that has a class t primary fuse at inverter positive. Sorry i cant take pictures the client dont allow pictures taken in his plant. I got the picture below on the internet as explanation picture below x 3 to the inverter.The wiring is not very neat they are using 16mm welding cable with 16x8 crimped lugs on the battery terminals.

    Click image for larger version. 

Name:	main-qimg-0f42e7ab0f88baa49eb164b6bbdbfc69-pjlq.jpeg 
Views:	843 
Size:	47.5 KB 
ID:	8547

  4. #4
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Why not install batteries designed for that application with a built in BMS, which can communicate with inverter.

    You need to understand the inverter specs and only then choose a battery suitable for the inverter. I would strongly advise against just dropping in replacement batteries.

    Something I see a lot while doing inverter audits for customers, general and battery setting not suitable for the type of batteries, like charge/discharge rates, battery cutout settings etc etc. Leaving an inverter in default setting, could destroy the batteries in a matter of months.

  5. Thanks given for this post:

    Cyon (26-May-22)

  6. #5
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    Quote Originally Posted by Isetech View Post
    Why not install batteries designed for that application with a built in BMS, which can communicate with inverter.

    You need to understand the inverter specs and only then choose a battery suitable for the inverter. I would strongly advise against just dropping in replacement batteries.

    Something I see a lot while doing inverter audits for customers, general and battery setting not suitable for the type of batteries, like charge/discharge rates, battery cutout settings etc etc. Leaving an inverter in default setting, could destroy the batteries in a matter of months.
    Thanks for the advice i did manage to find a manual for the Microcare inverter and did speak to the technical guys at Microcare in PE. The parameters could be set up for Lifep04.The main challenge in charging a Li-Ion battery is to realize the battery's full capacity without overcharging it. Constant current constant voltage (CCCV) I will set the inverter cut off voltage at 40% dod.
    Click image for larger version. 

Name:	LiFePO4-Battery-Voltage-Charts-Image-8.jpg 
Views:	835 
Size:	34.1 KB 
ID:	8548

  7. #6
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Quote Originally Posted by Alfred M View Post
    Thanks for the advice i did manage to find a manual for the Microcare inverter and did speak to the technical guys at Microcare in PE. The parameters could be set up for Lifep04.The main challenge in charging a Li-Ion battery is to realize the battery's full capacity without overcharging it. Constant current constant voltage (CCCV) I will set the inverter cut off voltage at 40% dod.
    Click image for larger version. 

Name:	LiFePO4-Battery-Voltage-Charts-Image-8.jpg 
Views:	835 
Size:	34.1 KB 
ID:	8548
    LiFePO4 batteries can go down to 10% DOD as per your chart or minimum of 12V.
    Voltage per cell, I think your battery has 4 cells in series
    Minimum discharge voltage = 2.5 V = 10V
    Working voltage = 3.0 to 3.2 V = 12V to 12.8V
    Maximum charge voltage = 3.65 V = 14.6V
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  8. #7
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    Quote Originally Posted by Justloadit View Post
    LiFePO4 batteries can go down to 10% DOD as per your chart or minimum of 12V.
    Voltage per cell, I think your battery has 4 cells in series
    Minimum discharge voltage = 2.5 V = 10V
    Working voltage = 3.0 to 3.2 V = 12V to 12.8V
    Maximum charge voltage = 3.65 V = 14.6V
    Thanks guys i appreciate the guidance and info. The ac load is 25amps single phase on inverter output and these new Lifep04 will be much more efficient than the 120ah deep cycle gel batteries so my thinking was to discharge only to 40% dod for the longevity of the battery bank as the client is paying R160k for the new batteries i have enough capacity to run down to 40% dod (24 batteries@120ah/battery) series/ parallel for 24v dc inverter input. I see on the existing installation there is 1x class T 30 fuse installed as primary disconnector on the positive side at the inverter or would it be better to put fuse protection between every bank and leave the class t fuse as main interrupter. I also see that this inverter can run at 200% 16kw if mains is present. There is also a ats changeover switch installed for a 30 kva diesel generator with one fase and neutral feeding the inverter. I was also thinking of using copper busbar with short leads to the battery terminals and get rid of the 16mm welding cable making the installation looking very untidy or am i overthinking the setup.

  9. #8
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    Quote Originally Posted by Justloadit View Post
    LiFePO4 batteries can go down to 10% DOD as per your chart or minimum of 12V.
    Voltage per cell, I think your battery has 4 cells in series
    Minimum discharge voltage = 2.5 V = 10V
    Working voltage = 3.0 to 3.2 V = 12V to 12.8V
    Maximum charge voltage = 3.65 V = 14.6V
    Thanks guys i appreciate the guidance and info. The ac load is 25amps single phase on inverter output and these new Lifep04 will be much more efficient than the 120ah deep cycle gel batteries so my thinking was to discharge only to 40% dod for the longevity of the battery bank as the client is paying R160k for the new batteries i have enough capacity to run down to 40% dod (24 batteries@120ah/battery) series/ parallel for 24v dc inverter input. I see on the existing installation there is 1x class T 300 fuse installed as primary disconnector on the positive side at the inverter or would it be better to put fuse protection between every bank and leave the class t fuse as main interrupter. I also see that this inverter can run at 200% 16kw if mains is present. There is also a ats changeover switch installed for a 30 kva diesel generator with one fase and neutral feeding the inverter. I was also thinking of using copper busbar with short leads to the battery terminals and get rid of the 16mm welding cable making the installation looking very untidy or am i overthinking the setup.

  10. #9
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    LiFePO4 have life cycles from 2,700 to over 10,000 cycles depending on conditions, so there is no advantage making the DOD at 40%.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  11. #10
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    One of the common battery failures or reduction in cycles in SA, high temperature.

Page 1 of 2 12 LastLast

Similar Threads

  1. [Question] Cable & Volt Drop
    By LuX10N in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 28-Mar-21, 10:01 AM
  2. Excel Drop down box
    By sterne.law@gmail.com in forum Technology Forum
    Replies: 8
    Last Post: 04-Oct-13, 01:09 PM
  3. Help please - voltage drop
    By Gei in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 21-Jan-12, 09:26 AM
  4. Vodacom signal drop
    By twinscythe12332 in forum Technology Forum
    Replies: 3
    Last Post: 11-Oct-10, 06:31 AM
  5. Drop your price.
    By Dave A in forum Entrepreneurship and Business Management Forum
    Replies: 9
    Last Post: 10-Oct-09, 08:51 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •