What are the requirements for a light fitting which has had all the switch gear and wiring removed and rewired to suit the LED lamps?
Would a supplementary COC be required, considering a light fitting is plugged into a 5 amp socket?
What are the requirements for a light fitting which has had all the switch gear and wiring removed and rewired to suit the LED lamps?
Would a supplementary COC be required, considering a light fitting is plugged into a 5 amp socket?
Yes. The light fitting is a fixed appliance and the coc covers the wiring up to the terminals of the fixed appliance.
The 6A plug in this case serves as an isolator.
Ask yourself this question ..... If I was doing a coc on the house and this light fitting was without a gland where the wire goes into the fitting, would I pass it even although it is fed by a plug ? My answer would be no. That means it's part of the installation.
It would have been another story had it been a standing lamp.
Rewiring luminaries as you describe is actually not legal.
All equipment used in an installation, including luminaries, must adhere to a safety standard.
Luminaries must comply with table 4.1 of SANS
Once you change the wiring in a light fitting it no longer complies and cannot be used.
Sent from my SM-A528B using Tapatalk
To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.
There's an electrical supplier in East London that retrofits the fittings before selling them.
What they do with all the electronic starters, I don't know.
Hi
There was a previous post started by you in 2019 - I have pasted the answer I used back then - Nothing has changed and you still need to comply to ARP 032 -2014 which is available from SANS stores at a price of +/- R 290.00
Retro fitting fluorescent fittings with LED tubes means rewiring the fitting.The minute you rewire the fitting you become the manufacturer and all the insurances and risks become yours.
You need to comply to ARP 032 - 2014
To migrate the risk it is cheaper to buy a channel that has been specifically wired for LED tubes - There is a minefield in the document.
The installation regulations SANS 10142 prescribe that only SABS approved equipment may be installed in an electrical installation. The moment it is altered, changed or modified from the original design there is no way of ensuring compliance unless you follow the Approved Recommended Practice (ARP 032 – 2014 which consists of 6 sections), or an applicable approved standard. That means as soon as you retrofit the fitting you are as liable as the manufacture of the original product. You need to ensure that you carry out the tests as prescribed in the Code on this work done by you.
Leecatt (16-May-22)
Off the subject I'm afraid. I was trying to "thank" CGE on Tapatalk for the above comment and I can no longer access this thread from there. If anyone knows what I I've done wrong kindly reply. 🤔
Lets get this right, if I take a lamp holder, connect a 1.0mm 3 core cabtyre I become the manufacturer and the light must comply with ARP 032 - 2014?
Time to go buy me a 5 ft LED light fit the same lamp holders and the gauge wire and keep it in my workshop for future reference. It probably be cheaper to just replace the fitting, the time to sit and modify the wires cost more than an LED shell would cost.
Would an LED retrofit then not pass an inspection report, because the light fitting was not designed for an LED retrofit lamp? Who would be responsible for the LED retrofit compliance the supplier or the person who installs the LED replacement.
At what point is the light fitting modification no longer compliant , as soon as you replace the lamp or if you disconnect the ballast and join the wires together? This could get interesting, it will certainly change the way you carry out inspection reports, considering the rate people are replacing lamps in everything from 2 FT to a 400 Watt high bay.
There have been massive LED retrofits from a person kitchen to large industrial sites. That COC you issued for the factory where they had a company into retrofit all those 250 Watt low bays, actually valid?
How many electrical contractors actually got involved in Lamp retrofits when Eskom where pushing it ?
It was all sorts of people that saw a quick buck - We refused to just change lamps and it could be the reason that ARP 032 was introduced.
We have been back to factories because the fluorescent replacement for 400w Metal halide caused the ignitor and choke to catch fire as they thought they were changing a 400w Mercury vapour.
One of the biggest suppliers/ contractors have been doing retrofits since year dot in our part of Town.
If I can design, build and install fully automated control systems for water treatment and waste water, disconnect everything in factory, from splitting the machines to installing 800-3000 amp supplies, I am sure my customers and the DOL can trust that I am capable of connecting 2 wires from a connector block to a lamp holder .