    Quote Originally Posted by Gensix View Post
    Update - The lithium battery will charge 30% quicker, so in some cases will help. But again it all depends on the load and whether the load is discharging the lithium beyond 80% or even fully discharging.
    IF you use a decent 1 C battery you can charge and discharge the lithium battery at the C rating.

    For example a 100 amp lithium battery with a 1 C rating can charge at 100 amps, it will be fully charged in 1 hour.

    A 100 amp 0.5C lithium battery can generally charge/discharge at 50 amps, it will be fully charged give or take 2 hours.

    It is not advisable because it will shorten the life cycles.

  2. #32
    New Member
    Join Date
    Oct 2022
    Location
    Assegay Durban
    Posts
    5
    Thanks
    0
    Thanked 0 Times in 0 Posts
    The general recommendation is to charge a lithium battery at no more than 30% of it's capacity.

    There is no danger of exceeding this with an alarm charger, or gate motor charger.

    There are however numerous other reasons why it is not recommended

  3. #33
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Quote Originally Posted by Gensix View Post
    The general recommendation is to charge a lithium battery at no more than 30% of it's capacity.

    There is no danger of exceeding this with an alarm charger, or gate motor charger.

    There are however numerous other reasons why it is not recommended
    The reasons ?

    They only produce a 0.5 amp trickle charge, which as noted cant improve charge time during load shedding?

    The c rating of the battery, using low quality cells?

    Reduced life cycles of the batteries maybe?

    Batteries installed in application where the battery supplier advertises as "drop in batteries", but the power supply has notice "not to be used with lithium batteries" , this seems to have become a common practise. Thermal scans have identified temperatures exceeding 180 degrees while the lithium batteries screams at a high pitch.

    Securi-prod says drop in and sherlo says not advisable.

    I can't think of any others off hand.

Page 4 of 4 FirstFirst ... 234

Similar Threads

  1. [Question] A better solution for alarm backup
    By ians in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 11-Feb-21, 03:58 PM
  2. 7 amp/hr alarm gate batteries
    By ians in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 03-Jun-20, 08:15 AM
  3. Alarm system question
    By adrianh in forum Technology Forum
    Replies: 4
    Last Post: 07-Mar-20, 12:21 PM
  4. fire alarm system supply
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 11-Jul-11, 04:26 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •