    Quote Originally Posted by GCE View Post
    I was not querying his credentials - Rather take the time to look at the regs I have pasted and tell me where I have quoted the regs incorrectly

    If what I have pasted is correct then query the presenter

    To me it would appear that the presenter has an opinion that does not take the regulations into account -

    With regards to learning something - I did , I read the statements you made and went to check the regulations - I differ from your/presenters opinion and backed myself with stating the relevant regulations .
    So Alfred M - go read the regulations and show me why my statements are incorrect
    No no i never said you quoted or interpreted the regs incorrectly all i am saying is that we need to be open to new and better ways to do our job nothing in the presentation falls outside of the regs it is just taken a step further to ensure proper bonding and earthing. To me it would be safer to use 2.5 mm earth conductor even though your bonding resistance falls within the specifications of the regs. And to Derlyn that
    jumps to your defence bonding is to bring all exposed metal parts to the same potential and an earth conductor carries fault currents to the main earthing bar in the db. There is a difference in a geyser compared to socket wiring extra care needs to be taken on any electrical installations where water is involved and socket outlets are not dedicated curcuits but geysers are. To take a example that is in the regs it is not compulsory for lights to go through a rcd to me all curcuit breakers on a db should go through an rcd makes the installation much safer and it is all about safety. Your next question may be "what about nuisance tripping" nuisance tripping is an actual fault and needs to be addressed, by using more than one rcd critical curcuits can have their own rcd. There is always room for improvement and learning we all learn new better ways every day unless you are stuck in a rut. Now guys explain to me on the few slides i have posted what is not inline with the regulations.Remember there are different ways of doing things but there is always "best practice". The regs also states that any electrical installation needs to be reasonably safe so meaning that with application of good practice you could make it safer.

  2. #12
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Hi

    I have no problem with doing more than the regulations require in the interests of best practice and safety.

    I assume you are attending the unit standards so that you can write paper 1 and 2 to obtain an Installation License.

    If the question is asked - " Do you require an external bonding conductor to bond hot and cold water pipes - True or False " You will answer True , because that is what you have been taught when in actual fact the answer is false. You are now 1 point less.

    I have a problem when presenters are teaching opinions rather than sticking to the regulations. There is a huge failure rate on Paper 1 and 2 and I believe it is because presenters are teaching opinions not regulations.

    I have the same problem with presenters teaching refresher course on SANS 10142-1 where they tend to give there opinions and the guys go back to the work place and carry out inspections for COC , sign them off and when the AIA comes along and fails certain aspects that same presenter when tackled then says " it is only small bits that you have to fix , just go back and correct it."
    The presenter is not losing the money .He stands in front of the class and acts like the expert until he is tackled head on and then ducks and dives.
    I have witnessed it with a contractor that came horribly short because he trusted the presenter .
    I have tackled that presenter and he still continues teaching the crap that he does because he believes that he is the expert.

    Yes , I have a huge problem with presenters that teach opinions

  3. Thanks given for this post:

    Derlyn (21-May-22)

  4. #13
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    I did the Unit Standard course in April and it was heavily based on their opinion. So much so I did what was needed to be done but took a lot what they said with a pinch of salt and i have done my own research or asked and applied my own understanding to what the Sans book says.

    Even asked a couple questions here with what was said there haha.

    I argued a lot with them on the Sans book with regards to P1 and P2 as well. I was asked to actually speak more in private to not confuse the other students who may not know what I'm on about and then I was worried as these other students have down P1 and P2 so should know what words and topics I am on.

    Best thing i took from it was to CYA...Cover your A....





    Sent from my CPH2197 using Tapatalk

  5. Thanks given for this post:

    Derlyn (21-May-22)

  6. #14
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Lastly the Unit Standard course is not like course work or a set standard... It's basically complete a bunch of CoC's to what ever the teacher teaches...

    There is no STANDARD at all, not like how in Matric across the country every one did the same maths sylabus. (Albeit the 2 types of the IEB and CAP or what ever ) but none the less all the same sylabus.

    I spoke of this in another thread how there is no same standard so every single person is different and nothing is common....

    Sent from my CPH2197 using Tapatalk

  7. Thanks given for this post:

    Derlyn (21-May-22)

  8. #15
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    This is what I enjoy about this forum, we all have our opinions, then we have the regs. I don't always agree with everything in the regs, but they are there as a guideline to a legal document, at the end of the day if you ever end up in the front of a court room, the judge, prosecutor and lawyers have no interest in peoples options, you will be judged on the facts according to the SANS document, like it or not.

    No matter how thick your CV or large your portfolio, there is always space for improvement, one of the reasons I still visit this site.

    I believe these threads help create awareness and would encourage more people to interact, voice your opinion right or wrong, so long as you walk away with a clearer understanding of the regulations, you are one step closer to improving the industry as a whole.

  9. Thanks given for this post:

    Dave A (22-May-22)

  10. #16
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Back to the topic, something to think about, what if the mains water pipe is PVC/plastic or a piece of the copper pipe is replaced with polycop using brass coupling and elbows etc?

  11. #17
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Us toppies with 40 years plus experience in the field, not in the classroom, know what it's like attending to an earth fault at 2am and the whole installation is in darkness because some bright spark has fed all the lights through the earth leakage. Alfred M, it is safer for the lights to remain on, should there be an earth fault.

    I can also imagine you buying a new stove every six months when it starts tripping the earth leakage. New stoves are sold with specific instructions not to connect them through earth leakage, for a good reason. It's called nuisance tripping. Yes, my brother, there exists something called nuisance tripping.

    Most of us toppies who are active here on the forum are not as you say, stuck in a rut. We all have the latest copies of sans 10142 and strive to keep up to date with the latest regulations.

    We do however know where to draw the line as far as safety is concerned. One day when you start quoting against your competitors, you will realize that if you don't draw that line in the right place, you gonna come short. You either not gonna get any work or you not gonna show a profit, one of the two.

    I would never have the audacity to tell someone like GCE to learn something. Rather learn from him as much as you can. It will come in handy and that's a promise.

    Peace out.

  12. Thanks given for this post:

    Dylboy (21-May-22)

  13. #18
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    I can not wait until we install RCBO's and that becomes the norm. Heck even the AFDD with RCD protection will be one better haha.

    Sent from my CPH2197 using Tapatalk

  14. #19
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Also agreed that the forum is great to chat and learn from all. And gives us a Chanel to openly chat and discuss items and that on its own will make us better

    Sent from my CPH2197 using Tapatalk

  15. #20
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Isetech View Post
    Back to the topic, something to think about, what if the mains water pipe is PVC/plastic or a piece of the copper pipe is replaced with polycop using brass coupling and elbows etc?
    If all pipes are pvc then the geyser needs to be bonded as per 6.16.2 - Then that is where the grey area of Twin & earth not having a full 2,5sqmm earth will come in.

    6.13.2.2 Hot and cold water systems
    Where the hot water system includes electric components and the water pipes
    are of conducting material, hot and cold water systems shall be bonded
    together and also be bonded to the earth continuity conductor system

    6.16.2 Water heaters
    NOTE Water heaters include geysers, instantaneous water heaters including units for
    boiling water, heat pumps, solar systems, induction water heaters and the like (see also
    6.16.1). electrode water heaters, steam generators and boilers are not included (refer
    to 6.16.7)
    6.16.2.1 All water heaters shall be bonded in accordance with 6.13 and a.c.
    supply circuits shall be protected by earth leakage protection with IΔn not
    exceeding 30 mA.
    NOTE To mitigate nuisance earth leakage tripping, an additional earth leakage may
    be provided.

Page 2 of 5 FirstFirst 1234 ... LastLast

Similar Threads

  1. [Article] New earth bonding test
    By Alfred M in forum Electrical Contracting Industry Forum
    Replies: 34
    Last Post: 21-Apr-22, 06:02 PM
  2. Geyser on, geyser on. Does it save electricity?
    By Annetta in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 10-Aug-21, 03:56 PM
  3. Bonding tray of the year.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 19-Apr-21, 10:36 PM
  4. Bonding
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 22-Aug-19, 07:38 AM
  5. Earthing and the CoC
    By WallyL in forum General Regulatory Compliance Forum
    Replies: 11
    Last Post: 20-Jan-11, 12:06 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •