    Geyser earthing and bonding

    I notice a lot of people uses 1.5 and 2.5 surfix on geysers I know the answer to this, based on the amps and distance I can do this.. Also the cost of the cable is less My question is just if bonding and earthing requires at least 2.5 earth conductor is the geyser then leggily earthed and bonded or do I miss something somewhere?
    I prefer, at least, a 4mm conductor for geysers and aircons. Depending on the stove's requirements I use 4mm or 6mm

    Greetings and enjoy your weekend

  2. #2
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    771
    Thanks
    121
    Thanked 35 Times in 34 Posts
    My thought process is the geyser can be a 1.5mm² earth for earthing purposes, however the pipes need to be bonded with a 2.5mm² so if the roof is bonded then a short 2.5mm² to geyser pipes (hot and cold ) is ok.



    Sent from my SM-N960F using Tapatalk

  3. #3
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    Use copper Earth strap between hot and cold water pipes for earth bonding
    Click image for larger version. 

Name:	25681_740x.jpg 
Views:	415 
Size:	34.7 KB 
ID:	8517

  4. #4
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    Quote Originally Posted by Thys LOW Elektries View Post
    I notice a lot of people uses 1.5 and 2.5 surfix on geysers I know the answer to this, based on the amps and distance I can do this.. Also the cost of the cable is less My question is just if bonding and earthing requires at least 2.5 earth conductor is the geyser then leggily earthed and bonded or do I miss something somewhere?
    I prefer, at least, a 4mm conductor for geysers and aircons. Depending on the stove's requirements I use 4mm or 6mm

    Greetings and enjoy your weekend
    I am currently busy with the unit standard assessment and this presentation came up on the subject earth/ bonding of geysers see below slides of correct procedure
    Click image for larger version. 

Name:	Screenshot_2022-05-19-21-47-14-894_cn.wps.moffice_eng.jpg 
Views:	892 
Size:	32.8 KB 
ID:	8534

  5. #5
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    Quote Originally Posted by Alfred M View Post
    I am currently busy with the unit standard assessment and this presentation came up on the subject earth/ bonding of geysers see below slides of correct procedure
    Click image for larger version. 

Name:	Screenshot_2022-05-19-21-47-14-894_cn.wps.moffice_eng.jpg 
Views:	892 
Size:	32.8 KB 
ID:	8534
    Sorry i see the slides are not very clear but basically hot and cold water pipes needs to be bonded as close to geyser as possible even the geyser flange needs to be bonded to cold water pipe with bamba straps using brass bolts and nuts. Then 2.5mm green/yellow or bare copper conductor back to db main earth bar. Wiring needs to be dedicated with earth leakage protection and curcuit breaker and double pole isolator close to geyser flange. 2.5mm Surfix or flat twin+earth the earth conductor must not be used for main earth of geyser the earth conductor is not 2.5mm. Bathroom zoning was also part of this presentation,ip ratings and electrical installations in bathrooms very interesting.

  6. #6
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,302
    Thanks
    36
    Thanked 314 Times in 263 Posts
    Hi
    Couple of points that I would tend to disagree with

    hot and cold water pipes needs to be bonded as close to geyser as possible even the geyser flange needs to be bonded to cold water pipe with bamba straps using brass bolts and nuts Then 2.5mm green/yellow or bare copper conductor back to db main earth bar.
    I don't agree that strap needs to be used and back my statement up with with Note 2 under 6.13 as pasted below

    6.13 Bonding
    NOTE 1 The aim of bonding is to bring all the bonded parts to the same electrical
    potential.
    NOTE 2 No external conductor is required if compliance with the requirements for
    continuity can be proved by the test in 8.6.2.


    Wiring needs to be dedicated with earth leakage protection and curcuit breaker
    Agree that a dedicated circuit but more than one geyser can be on the circuit
    6.16.2.2 Dedicated circuits shall be provided for water heaters and there may
    be more than one water heater on each circuit.


    double pole isolator close to geyser flange.
    6.16.1.4 The disconnecting device shall be positioned
    a) within 1,5 m from the appliance,




    2.5mm Surfix or flat twin+earth the earth conductor must not be used for main earth of geyser the earth conductor is not 2.5mm.
    No where in the regulations is there a statement that says you may not use a wire size less than 2,5sqmm to earth a geyser

    To bond a geyser yes - but if the geyser is bonded due to the copper pipes been bonded elsewhere and the readings being OK , then I should be able to earth the geyser with less than 2,5sqmm

  7. Thank given for this post:

    Derlyn (21-May-22), Dylboy (21-May-22)

  8. #7
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,216
    Thanks
    60
    Thanked 102 Times in 97 Posts
    Back to the topic, something to think about, what if the mains water pipe is PVC/plastic or a piece of the copper pipe is replaced with polycop using brass coupling and elbows etc?

  9. #8
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,302
    Thanks
    36
    Thanked 314 Times in 263 Posts
    Quote Originally Posted by Isetech View Post
    Back to the topic, something to think about, what if the mains water pipe is PVC/plastic or a piece of the copper pipe is replaced with polycop using brass coupling and elbows etc?
    If all pipes are pvc then the geyser needs to be bonded as per 6.16.2 - Then that is where the grey area of Twin & earth not having a full 2,5sqmm earth will come in.

    6.13.2.2 Hot and cold water systems
    Where the hot water system includes electric components and the water pipes
    are of conducting material, hot and cold water systems shall be bonded
    together and also be bonded to the earth continuity conductor system

    6.16.2 Water heaters
    NOTE Water heaters include geysers, instantaneous water heaters including units for
    boiling water, heat pumps, solar systems, induction water heaters and the like (see also
    6.16.1). electrode water heaters, steam generators and boilers are not included (refer
    to 6.16.7)
    6.16.2.1 All water heaters shall be bonded in accordance with 6.13 and a.c.
    supply circuits shall be protected by earth leakage protection with IΔn not
    exceeding 30 mA.
    NOTE To mitigate nuisance earth leakage tripping, an additional earth leakage may
    be provided.

  10. #9
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,216
    Thanks
    60
    Thanked 102 Times in 97 Posts
    This is what I enjoy about this forum, we all have our opinions, then we have the regs. I don't always agree with everything in the regs, but they are there as a guideline to a legal document, at the end of the day if you ever end up in the front of a court room, the judge, prosecutor and lawyers have no interest in peoples options, you will be judged on the facts according to the SANS document, like it or not.

    No matter how thick your CV or large your portfolio, there is always space for improvement, one of the reasons I still visit this site.

    I believe these threads help create awareness and would encourage more people to interact, voice your opinion right or wrong, so long as you walk away with a clearer understanding of the regulations, you are one step closer to improving the industry as a whole.

  11. Thanks given for this post:

    Dave A (22-May-22)

  12. #10
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    Quote Originally Posted by GCE View Post
    Hi
    Couple of points that I would tend to disagree with



    I don't agree that strap needs to be used and back my statement up with with Note 2 under 6.13 as pasted below

    6.13 Bonding
    NOTE 1 The aim of bonding is to bring all the bonded parts to the same electrical
    potential.
    NOTE 2 No external conductor is required if compliance with the requirements for
    continuity can be proved by the test in 8.6.2.




    Agree that a dedicated circuit but more than one geyser can be on the circuit
    6.16.2.2 Dedicated circuits shall be provided for water heaters and there may
    be more than one water heater on each circuit.




    6.16.1.4 The disconnecting device shall be positioned
    a) within 1,5 m from the appliance,






    No where in the regulations is there a statement that says you may not use a wire size less than 2,5sqmm to earth a geyser

    To bond a geyser yes - but if the geyser is bonded due to the copper pipes been bonded elsewhere and the readings being OK , then I should be able to earth the geyser with less than 2,5sqmm
    GCE learn something .Look at the person's credentials who did this presentation!!!?
    Click image for larger version. 

Name:	Screenshot_2022-05-20-20-15-22-685_cn.wps.moffice_eng.jpg 
Views:	303 
Size:	34.4 KB 
ID:	8536
    Click image for larger version. 

Name:	Screenshot_2022-05-20-20-13-05-075_com.whatsapp.jpg 
Views:	488 
Size:	43.1 KB 
ID:	8537
    Click image for larger version. 

Name:	Screenshot_2022-05-20-20-12-38-399_com.whatsapp.jpg 
Views:	1083 
Size:	40.3 KB 
ID:	8538
    Click image for larger version. 

Name:	Screenshot_2022-05-20-20-12-22-232_com.whatsapp.jpg 
Views:	373 
Size:	35.7 KB 
ID:	8539

Page 1 of 4 123 ... LastLast

Similar Threads

  1. [Article] New earth bonding test
    By Alfred M in forum Electrical Contracting Industry Forum
    Replies: 34
    Last Post: 21-Apr-22, 06:02 PM
  2. Geyser on, geyser on. Does it save electricity?
    By Annetta in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 10-Aug-21, 03:56 PM
  3. Bonding tray of the year.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 19-Apr-21, 10:36 PM
  4. Bonding
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 22-Aug-19, 07:38 AM
  5. Earthing and the CoC
    By WallyL in forum General Regulatory Compliance Forum
    Replies: 11
    Last Post: 20-Jan-11, 12:06 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •