    I have seen this and I dont agree with testing socket to exposed metal as a socket is earthed not bonded....

    However I say this but I am undecided on what to really think, spoke to one guy when doing the unit standards and he says its wrong too.

    But what does everyone else think ?
    I will try read it better later this weekend and see if I agree with it or not

    Sent from my SM-N960F using Tapatalk

  3. #3
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,789
    Thanks
    3,331
    Thanked 2,694 Times in 2,271 Posts
    Blog Entries
    12
    Doesn't this introduce a risk that we may fail to detect that accessible conductive parts may not be connected to the earth terminal?

  4. #4
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    That test is confirmed with the Resistance of earth continuity conductor.

    But that test is technically the conductor but we often test the metal class 1 stuff with it too. And the reading as to be of table 8.1.

    So earthed is items that carry electricity.
    Bonding is items that don't carry electricity.

    Fine line stuff this but the article makes sense to have it all at same potential and to verify that.

    I like the test but perhaps a voltage check and not 0.2ohm bonding check as voltage proves bonded per say and same potential.

    What you all think ?

    Sent from my SM-N960F using Tapatalk

  5. #5
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Does a geyser have an earthing terminal or is it a bonding terminal ?

  6. #6
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Geyser is earthing terminal but we bond the hot and cold pipes.

    So generally people bring 2.5mm earth cable to earth the geyser but then they take a lead off to hot and cold taps to bond so not to run extra bonding only cable.

    That is how I see it and the train of thought.

    In the UK they run separate bodming cables and say one is water, other is gas etc...

    Sent from my SM-N960F using Tapatalk

  7. #7
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Quote Originally Posted by Dylboy View Post
    Geyser is earthing terminal but we bond the hot and cold pipes.

    So generally people bring 2.5mm earth cable to earth the geyser but then they take a lead off to hot and cold taps to bond so not to run extra bonding only cable.

    That is how I see it and the train of thought.

    In the UK they run separate bodming cables and say one is water, other is gas etc...

    Sent from my SM-N960F using Tapatalk
    The bonding conductor needs to be minimum 2,5mm, however the earth continuity conductor need not be.
    The size of the earth continuity conductor will depend on the cable used to supply the appliance.

    So if a geyser is wired with 1,5mm FTE then the ECC will be less than 1,5mm sq.
    Now you bond the hot & cold pipes with 2,5mm and bond to the earthing terminal on geyser with 2,5mm.
    The ECC is also connected to same earthing terminal on the geyser.

    The bonding conductor is now 2,5mm and the ECC is less than 1,5mm.

    Acceptable ?

    I'm reading 6.13.2.2 and the above situation ticks the boxes.
    I suppose one would first have to define "earth continuity conductor system"

    What sayeth the other toppies ?
    Last edited by Derlyn; 15-Apr-22 at 02:13 PM.

  8. #8
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    ECC or Earth Continuity Conductor is the part of the earthing or grounding system which joins or bonds together all the metallic parts of an installation network: Conduit, ducts, boxes, metal casing of switches, switch-fuses, distribution boards, regulating and controlling apparatus, exposed metal work of machines and any metal framework on which electrical apparatus are mounted.

  9. #9
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    I am aware of the difference between an earth continuity conductor and a bonding conductor.

    The regulations state that the bonding conductor must be connected to the earth continuity conductor SYSTEM.

    I am, however, not 100% sure of where, physically, this connection should be done.

    Can it be made to any earth continuity conductor or must it be made directly to the consumer's earthing terminal. Hence my question regarding the definition of the earth continuity conductor SYSTEM.

  10. #10
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Ahhh I see what you are saying ! Intresting observation.

    I think somewhere it states about earth terminal connections... Will try look later

    Sent from my SM-N960F using Tapatalk

Page 1 of 4 123 ... LastLast

Similar Threads

  1. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM
  2. Bonding tray of the year.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 19-Apr-21, 10:36 PM
  3. Bonding
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 22-Aug-19, 07:38 AM
  4. [Question] Earth fault loop impedance test above 100A
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 09-Mar-17, 09:43 AM
  5. [Question] Earth Loop Impedance on COC test.
    By Jasond MIE in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 06-Mar-15, 01:42 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •