    CpC half of phase?

    Hello

    Start off with hope all the KZN okes are doing ok and so sorry! Fortunately my folks in Balito are ok but the complex as a whole took a beating!

    My question:

    I have a chap stating that the CPC can not be less than half the phase C.S.A.

    Now I am trying to find that reg to see for my self. He just says look at tables on 167 and page 304 but I can't figure it out.

    Anyway I am not sure he is correct as then a 4mm² FTE has a 1.5mm² cpc then making that cable wrong which I doubt.

    But keen to see what you all think and if the cpc half the phase is correct?

    Sent from my SM-N960F using Tapatalk

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Expand on the abbreviations CPC and CSA

    You tend to come up with abbreviations that I struggle to work out

  3. #3
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Apologies!

    CPC, I got from UK stuff. It is Circuit protective conductor. Which here is the Earth cable.

    C.S.A i shortened to Cross Sectinal Area.

    Sent from my SM-N960F using Tapatalk

  4. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    The regs actually state that it should be the same size as the phase conductor ( 6.12.1.1 e) but may be smaller if CB instantaneous tripping current is less than 10 ( 6.12.1.1 f )

    If the earth wire forms part of the cable then it needs to comply to that spec ( 6.12.1.1 b ) - So in Twin and Earth , Armour cable ECC , surfix etc the earth is part of the cable and conforms to that standard.When the cable is manufactured/ designed it takes into account ( 6.12.1.1 d ) be able to carry the prospective fault current without excessive temperature rise of the conductor, within the disconnecting time,





    6.12.1 Earth continuity conductors
    6.12.1.1 An earth continuity conductor shall
    a) consist of compatible conductors,
    b) if it forms part of a cable other than a flexible cable, comply with the relevant
    requirements of the standard for the cable,
    c) if it forms part of a flexible cable, be of the same material as, and have a
    nominal cross-sectional area at least equal to, that of the largest phase
    conductor,
    d) be able to carry the prospective fault current without excessive temperature
    rise of the conductor, within the disconnecting time,
    e) if it does not form part of a cable or flexible cable, have a nominal
    cross-sectional area in accordance with table 6.25 and if it equals to the
    phase conductor size refer to table 6.28(a), as follows:



    f) using the same formulae above where the earth continuity conductor cross
    sectional area is 50 % of the phase conductor, thus m = 2, table 6.28(b) for
    the maximum length of copper earth continuity conductor for general
    purpose circuit breaker apply.
    Table 6.28(b) — Minimum size and maximum length of copper earth
    contuinity conductors rated at 50 % of phase conductor diameter, for
    general purpose circuit-breakers with instantaneous tripping current
    Im = 10 × In


    g) Where the proposed PE conductor with increased cross-section becomes
    uneconomical, an earth-leakage protection device may be added or
    deployed as additional protection, where the tripping threshold would be
    substantially lower.
    h) For aluminium conductors apply the formulae above with ρ = 37 × 10-3
    ohm.mm2/metre

  5. #5
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Hey GCE

    Thank you!

    For some reason i didnt get the notification !

    The bit on the cable being manufacturerd was my example to him but he didnt care haha. If the adibitaic calcs prove good which they do then i am happy.

    Intresting bit on the atuff mentioned before, thank you

    Sent from my SM-P605 using Tapatalk

Similar Threads

  1. Changing 3 phase electric DB to single phase. (Switchover etc)
    By Janbez54 in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 05-Jul-21, 07:59 AM
  2. Inverter diagram for one phase on 3 phase installation feeding 2 db’s
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 19-Aug-20, 06:44 AM
  3. single phase and 3 phase sockets on machines
    By ians in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 18-Jun-20, 07:53 PM
  4. Single phase generator feeding 1 phase of 3 phase db - discuss.
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 03-Jul-18, 10:06 AM
  5. Three phase to single phase generator advice needed
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 08-Apr-15, 10:12 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •