3 KVA inverter (around 13 amps) 16 amp and 1.5 would work however:
A 20 amp combo breaker with a green indicator light using 2.5 mm wire for the input.
32 amp changeover switch.
A 20 amp combo output with a red indicator light using 2.5 mm wire for the output.
16 amp breaker for the 3 socket outlets, wired using 2.5 mm twin+e
10 amp breaker for the light circuit fed from the inverter.
No earth leakage required for the inverter or the circuits (dedicated blue sockets for electronic equipment) and the inverter is mounted next to the main DB.
24 VDC system
2 x 100 amp/hr batteries in series
2 x 125 amp DC fuses (for the battery) mounted in an 8 way DB.
A look on the Alvern website (cable supplied by wholesaler) and a quick scan of the regs = 35 mm, right ?
the 230 VAC rating is 125 amps, does this apply to a 3 m length of 24 VDC
Applications
PERMOPOWER is manufactured to SABS 1507 specification, is flexible, and rated at 1000 volts. It can be used on all types of indoor and outdoor panel and power equipment. PERMOPOWER is an excellent replacement for large, rigid type stranded house wires, and is quick to install in ducts, shafts, switchboards, trunking, conduit, transformer connections, large borehole pumps and many types of wiring applications in confined spaces. Excellent product for harsh welding environments.