    If a light fitting is secured to the building, can you fit a 15 amp plug top and excluded it on a COC?

    If a cable enters a conduit buried in the ground or secured to the side of a building, can it be excluded from the COC if it plugged into a socket outlet?

    If a gate motor is fed from a plug top (230 VAC, not a transformer) in a bedroom in the house, fed through a wall using a piece of 1.5 mm cabtyre buried with no mechanical protection directly in the ground, can it be excluded from a COC.

    At what point is a circuit fed from a plug top excluded from the COC ?

    The way I understand it, if the cable is hanging loose and the appliance is not secured to the building it can be excluded, however as soon as you secure the appliance, cabling or wireway to the building it becomes a fixture.

    If the COC is required for the sale of a property, the appliance is regarded as a fixture and cannot be excluded from the COC.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    The answer to your questions above are contained in 6.16.1.10
    They cannot just be excluded other wise you could put a 80Amp socket outlet on the incoming mains ( if 80Amp supply ) and unplug the complete installation and just do a COC for the 1 socket



    6.16.1.10 The wiring between different parts of a fixed appliance that are
    installed separately is part of the fixed installation, even where it is supplied
    from a socket-outlet, unless such wiring is less than 3 m in length.

    Such wiring shall be protected by separate overload protection unless its
    current-carrying capacity is such that the circuit protection of the socket-outlet
    circuit will provide protection or that part of the appliance has built-in thermal
    overload protection.
    NOTE Where the length of wiring exceeds 3 m, the impedance and the functioning of
    the protective devices need to be considered to satisfy the overcurrent protection
    requirements in this part of SANS 10142.

  3. Thanks given for this post:

    Dave A (27-Mar-22)

Similar Threads

  1. Coc for new electrical installation
    By Lourie1251 in forum Electrical Contracting Industry Forum
    Replies: 26
    Last Post: 14-Aug-23, 09:20 AM
  2. Parts of the installation not covered by this report (COC)
    By ians in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 31-Jan-22, 07:30 AM
  3. [Question] Quotation for new electrical installation
    By CynthiaM in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 01-Jul-19, 01:40 PM
  4. [Question] Electrical Installation Guidelines
    By ThabiG in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-Sep-18, 01:25 PM
  5. [Article] New electrical installation regulations
    By QUINN in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 11-Jun-14, 03:01 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •