Originally Posted by
GCE
You are reading the regulations to what may not be earthed - You need to read what must be earthed
If the light fitting has an earth terminal it must be connected to earth - The majority of fittings you mention above will have earth terminals
6.12.3 Earthing of exposed conductive parts
6.12.3.1 The following conductive parts shall be earthed:
a) all exposed conductive parts of an installation other than those described
in 6.12.3.2;
NOTE Metal enclosures on PVC conduit should be earthed if they can become live
and can be touched.
b) all conductive cable sheaths and armouring, wireways and catenary wires;
c) the earthing terminal of a socket-outlet;
d) the secondary winding of a transformer if it is not a safety transformer;
e) earthing terminals of all permanently connected electrical equipment and
appliances;
f) conductive parts of discharge luminaires and equipment that need special
earthing arrangements; and
g) all class I equipment.