    High neutral earth reading

    Good day

    We are upgrading a 3phase installation for one of our local schools, the building was wired early 60's. A 3 phase, 4core 50mm swa cable comes into the kitchen without an earth wire?! The neutral - Earth reading is 1.78 volts and the earth wire tingles when you touch it! Everything was ripped out and the whole building rewired.
    My question now is, do I need to have an earth wire connected to the building if the db passes all the tests?

    I personally feel an earth wire is always a good thing to have, irrespective of the test results but my employer feels different about it..
    Please advise

    Greetings
    Thys
    Orania

  2. #2
    Full Member markthespark's Avatar
    Join Date
    Jul 2015
    Location
    Cape Town
    Posts
    52
    Thanks
    3
    Thanked 2 Times in 2 Posts
    Does the cable terminate in an oosterzee box or at the DB? It should be fitted with an earth tag. You can also consider knocking in an earth spike.

  3. #3
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,688
    Thanks
    3,315
    Thanked 2,682 Times in 2,262 Posts
    Blog Entries
    12
    Do you have loop test results?

  4. #4
    Full Member markthespark's Avatar
    Join Date
    Jul 2015
    Location
    Cape Town
    Posts
    52
    Thanks
    3
    Thanked 2 Times in 2 Posts
    A lot of the time the earth conductor is run separately and most times these get stolen.

  5. #5
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,587
    Thanks
    113
    Thanked 151 Times in 143 Posts
    Quote Originally Posted by markthespark View Post
    A lot of the time the earth conductor is run separately and most times these get stolen.
    Don't think cable theft is a problem in Orania.

  6. #6
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    231
    Thanks
    12
    Thanked 21 Times in 19 Posts
    The cable was not stolen, neither the tools or supplies I left overnight in the unlocked kitchen building just to cancel that as possible cause.
    By the way, the old part of the town is wired via the TN-S concept, I think the neutral-earth link had been removed somewhere and now runs on a TN system
    The school setup is as follows:
    Electricity come to the school grounds via overhead cable, 5 wires, and is terminated in a huge pole mounted orange kiosk, originally grey. The orange kiosk have an green and gold earth wire going into the ground, presumably to a earth peg. From here six swa cables go to the various buildings. No other earth wires exit the kiosk. The db in the kitchen get its electricity directly from this kiosk, the swa cable comes into the db with no earth and is terminated in the main db. The earth comes from anther sub kiosk with no earth wire??! going into the kiosk and the neutral and earth is also not bonded anywhere.
    Building was without electricity the whole day since I was working on the DB.
    Will do the loop test tomorrow and post the results here. Will also test at various times to see if there is any power fluctuation, if any.

  7. #7
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    231
    Thanks
    12
    Thanked 21 Times in 19 Posts
    Drumroll please, the loop test results are in. Red phase, 0.57 Ohms and 415.8 Amps. Yellow phase, 0.52 Ohms and 317.6 Amps. Blue phase, 0.45 Ohms and 489.1A
    Main breaker outside = 3pole 63A.
    Volts Red 230 volts Yellow 229 Volts Blue 236 Volts
    Max Z loop calculated, red 1.857 Ohms Yellow 1.817 Ohms Blue 1.873 Ohms
    Isc calculated, red 0.303 kA yellow 0.272 kA Blue 0.327 kA
    Hope this helps
    Greatings

Similar Threads

  1. [Question] Neutral on high current appliances
    By Alfred M in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 05-Mar-22, 10:01 AM
  2. High loop impedance reading
    By ians in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 06-Oct-21, 12:47 PM
  3. [Question] Reading are to high
    By Jaco DJ in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 25-Sep-15, 07:34 PM
  4. high loop impedance reading
    By ians in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 20-May-15, 07:00 PM
  5. Neutral leaking 220V to Earth
    By Etienne Swanepoel in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 19-Oct-14, 07:37 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •