Originally Posted by
Justloadit
Just a note about all new electronic equipment.
They are usually fed with an SMPS (Switched Mode Power Supply) due to universal input, cost and physical size.
One way of getting to pass the EMI limit specifications is to add a small capacitor between the secondary negative line and the incoming rectified negative line, and some of the systems depending on the type may have a capacitor to earth to reference the secondary side to earth. You can usually note this when you touch the chassis of 2 computers and get a tingling feeling, or noted a spark when connecting 2 computers via USB or in the old days RS232. Use you AC tested to measure the voltage between your PC chassis and Earth to see this.
A number of these SMPS connected could increase the leakage current from Neutral to Earth when there is a spike somewhere in the electrical system, which could cause the RCD to trip.