Thread: Stove couplers

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Quote Originally Posted by Alfred M View Post
    I have never seen n stove couplers installed according to regs. The stove repair i done this week had 2 x 2.5mm surfix connected to stove from isolator.Click image for larger version. 

Name:	Fig-1-stove-couplers-1024x768.jpg 
Views:	485 
Size:	32.1 KB 
ID:	8488
    SANS 10142-1, Edition 2, requires that free-standing cooking appliances be connected via a stove coupler and that a switch-disconnector must be installed.
    Stoves do not need to be connected via a stove coupler anymore. They can be wired directly to the isolator through a flexible arrangement.

    I remove the stove connector on the wall.
    Rewire from the isolator with 4mm house wire leaving 2 metres of slack out the wall.
    Fit a dome lid where the plug was and use spraque ( flexible conduit ) between the dome lid and the stove.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Derlyn View Post
    Stoves do not need to be connected via a stove coupler anymore. They can be wired directly to the isolator through a flexible arrangement.
    I seem to have a different set of regulations to you , or my understanding of 6.16.3.3 is different .


    SANS 10142-Ed3
    6.16.3.3 Stove connection
    6.16.3.3.1 A stove designed to be a free-standing appliance rated above 16 A
    shall be connected through
    a) a stove coupler which shall comply with SANS 60309-1
    and of dimensions
    as given in SANS 337 (a maximum of 45 A single-phase and 16 A per
    phase for three phase), or
    NOTE 1 Earth leakage protection is not required for the stove circuit when a stove
    coupler is used.
    NOTE 2 For a three-phase coupler, the earth connection needs special
    consideration.
    b) a socket-outlet that complies with SANS 60309-1 (industrial type) with
    30 mA earth leakage protection, however, the use of industrial type socketoutlets
    is not recommended for stove connections.

  3. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Quote Originally Posted by GCE View Post
    I seem to have a different set of regulations to you , or my understanding of 6.16.3.3 is different .

    6.16.3.3.3 The stove connections may be wired directly between the isolator
    and the stove terminals, by means of a flexible arrangement, which are
    mechanically secured and be terminated on either end. When the stove is
    removed, the final section of hard wiring to the stove terminals has to be
    removed and made safe. Amdt 1


    Glad I'm not the only person that interpreted the above as meaning that a stove coupler is not necessary.

  4. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    I went and purchased the lastest addition to ensure that I am on the latest edition even though the changes appear small and the price over the top whereas they should just be issuing amendments to insert on loose pages

    I have to disagree that a stove coupler is not required

    I read the regulations to say that if the stove is a free standing unit it shall have a stove coupler

    6.16.3.3 Stove connection
    6.16.3.3.1Stove connections shall be connected by either 6.16.3.3.2 or
    6.6.3.3.3. Amdt 1
    6.16.3.3.2 A stove designed to be a free-standing appliance rated above 16 A
    shall be connected by means of the following:
    a) a stove coupler which shall comply with SANS 60309-1 and of dimensions
    as given in SANS 337 (a maximum of 45 A single-phase and 16 A per
    phase for three phase), or
    NOTE 1 Earth leakage protection is not required for the stove circuit when a stove
    coupler is used.
    NOTE 2 For a three-phase coupler, the earth connection needs special
    consideration.
    b) a socket-outlet that complies with SANS 60309-1 (industrial type) with
    30 mA earth leakage protection, however, the use of industrial type socketoutlets
    is not recommended for stove connections.
    6.16.3.3.3 The stove connections may be wireddirectly between the isolator
    and the stove terminals, by means of a flexible arrangement, which are
    mechanically secured and be terminated on either end. When the stove is
    removed, the final section of hard wiring to the stove terminals has to be
    removed and made safe. Amdt 1

  5. #5
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Quote Originally Posted by GCE View Post
    I went and purchased the lastest addition to ensure that I am on the latest edition even though the changes appear small and the price over the top whereas they should just be issuing amendments to insert on loose pages

    I have to disagree that a stove coupler is not required

    I read the regulations to say that if the stove is a free standing unit it shall have a stove coupler

    6.16.3.3 Stove connection
    6.16.3.3.1Stove connections shall be connected by either 6.16.3.3.2 or
    6.6.3.3.3. Amdt 1
    6.16.3.3.2 A stove designed to be a free-standing appliance rated above 16 A
    shall be connected by means of the following:
    a) a stove coupler which shall comply with SANS 60309-1 and of dimensions
    as given in SANS 337 (a maximum of 45 A single-phase and 16 A per
    phase for three phase), or
    NOTE 1 Earth leakage protection is not required for the stove circuit when a stove
    coupler is used.
    NOTE 2 For a three-phase coupler, the earth connection needs special
    consideration.
    b) a socket-outlet that complies with SANS 60309-1 (industrial type) with
    30 mA earth leakage protection, however, the use of industrial type socketoutlets
    is not recommended for stove connections.
    6.16.3.3.3 The stove connections may be wireddirectly between the isolator
    and the stove terminals, by means of a flexible arrangement, which are
    mechanically secured and be terminated on either end. When the stove is
    removed, the final section of hard wiring to the stove terminals has to be
    removed and made safe. Amdt 1
    Seems as if they added 6.16.3.3.3 to confuse the hell out of us. Still trying to understand the reason for adding it.

    Yep. R1180 is a bit steep to find out that a geyser must now be on earth leakage.

    I'm guessing that one only needs to wire the geyser through earth leakage if one does any work on same.
    If not it can be left as is ? The same as new socket outlets.

  6. #6
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Derlyn View Post
    Seems as if they added 6.16.3.3.3 to confuse the hell out of us. Still trying to understand the reason for adding it.

    .
    I would think 6.16.3.3.3. is there as you do not need a stove coupler if the oven is built into the kitchen cupboards . You could put a stove coupler onto a built in oven as well and it would pass the inspection - you could also leave it off for built in cupboards .

    If it is free standing , you have no choice in my opinion.

  7. #7
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Derlyn View Post
    Yep. R1180 is a bit steep to find out that a geyser must now be on earth leakage.

    I'm guessing that one only needs to wire the geyser through earth leakage if one does any work on same.
    If not it can be left as is ? The same as new socket outlets.
    I have just bought Ed3.01 which was published at the end of 2021
    ED 3 was published July 2020

    ED2 was published in March 2017 and was the first time that earth Leakage on a geyser came into effect

  8. #8
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,789
    Thanks
    3,331
    Thanked 2,694 Times in 2,271 Posts
    Blog Entries
    12

    Are you sure you have correctly taken into account this bit?
    Quote Originally Posted by GCE View Post
    [I]6.16.3.3 Stove connection
    6.16.3.3.1Stove connections shall be connected by either 6.16.3.3.2 or
    6.6.3.3.3. Amdt 1
    Based on the "or", 6.16.3.3.3 is a stand-alone option and is not dependant on the content of 6.16.3.3.2

  9. Thanks given for this post:

    Derlyn (15-Mar-22)

  10. #9
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Dave A View Post

    Are you sure you have correctly taken into account this bit?

    Based on the "or", 6.16.3.3.3 is a stand-alone option and is not dependant on the content of 6.16.3.3.2
    Looked at it and thought about it - If the stove is built in , I would say the or comes into play and you can use either method - If the stove is freestanding then it states that it shall use a stove plug and the or bit would fall away

    Do we ignore the implication on the shall wording ?

    I was always taught that if the word SHALL is used it is non-negotiable if the word MAY is used then it becomes negotiable


    6.16.3.3 Stove connection
    6.16.3.3.1Stove connections shall be connected by either 6.16.3.3.2 or
    6.6.3.3.3. Amdt 1
    6.16.3.3.2 A stove designed to be a free-standing appliance rated above 16 A
    shall be connected by means of the following:
    a) a stove coupler which shall comply with SANS 60309-1 and of dimensions
    as given in SANS 337 (a maximum of 45 A single-phase and 16 A per
    phase for three phase), or
    NOTE 1 Earth leakage protection is not required for the stove circuit when a stove
    coupler is used.
    NOTE 2 For a three-phase coupler, the earth connection needs special
    consideration.
    b) a socket-outlet that complies with SANS 60309-1 (industrial type) with
    30 mA earth leakage protection, however, the use of industrial type socketoutlets
    is not recommended for stove connections.
    6.16.3.3.3 The stove connections may be wireddirectly between the isolator
    and the stove terminals, by means of a flexible arrangement, which are
    mechanically secured and be terminated on either end. When the stove is
    removed, the final section of hard wiring to the stove terminals has to be
    removed and made safe. Amdt 1

  11. #10
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,789
    Thanks
    3,331
    Thanked 2,694 Times in 2,271 Posts
    Blog Entries
    12
    Quote Originally Posted by GCE View Post
    Looked at it and thought about it - If the stove is built in , I would say the or comes into play and you can use either method - If the stove is freestanding then it states that it shall use a stove plug and the or bit would fall away

    Do we ignore the implication on the shall wording ?

    I was always taught that if the word SHALL is used it is non-negotiable if the word MAY is used then it becomes negotiable
    To my mind I tend to apply the hierarchy of nested logic operators (more mathematical and coding oriented, I suppose).

    This would deem 6.16.3.3.2 and 6.16.3.3.3 as separate subset options of the "or" logic operator set by 6.16.3.3.1.
    If the requirements of 6.16.3.3.2 is met fully, the result is TRUE (regardless of the result when tested against 6.16.3.3.3)
    Similarly, if the requirements of 6.16.3.3.3 is met fully, the result is TRUE (regardless of the result when tested against 6.16.3.3.2).

  12. Thanks given for this post:

    Derlyn (15-Mar-22)

Similar Threads

  1. New stove plug
    By ians in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 26-Jan-21, 01:11 PM
  2. Stove on E/L
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 27-Sep-20, 07:46 PM
  3. [Question] Stove connection
    By serial5228 in forum Electrical Contracting Industry Forum
    Replies: 19
    Last Post: 15-Jul-20, 07:37 PM
  4. COC for a gas stove
    By ians in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 23-Jan-15, 01:24 AM
  5. stove plate
    By murdock in forum Technology Forum
    Replies: 7