    Stove couplers

    I have never seen n stove couplers installed according to regs. The stove repair i done this week had 2 x 2.5mm surfix connected to stove from isolator.Click image for larger version. 

Name:	Fig-1-stove-couplers-1024x768.jpg 
Views:	485 
Size:	32.1 KB 
ID:	8488
    SANS 10142-1, Edition 2, requires that free-standing cooking appliances be connected via a stove coupler and that a switch-disconnector must be installed.

  2. #2
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    This client had a valid coc
    Click image for larger version. 

Name:	IMG_20220306_110353.jpg 
Views:	534 
Size:	39.8 KB 
ID:	8489

  3. #3
    Silver Member
    Join Date
    Mar 2008
    Posts
    373
    Thanks
    5
    Thanked 51 Times in 44 Posts
    Jo'burg - went 7 suppliers - None could get a stove coupler for me and all looked at me like I was mad.

  4. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by skatingsparks View Post
    Jo'burg - went 7 suppliers - None could get a stove coupler for me and all looked at me like I was mad.
    I will ask the question form a supplier we use but was under the impression that it is no longer a problem as somebody bought the molds from procast and continued manufacturing

  5. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by skatingsparks View Post
    Jo'burg - went 7 suppliers - None could get a stove coupler for me and all looked at me like I was mad.
    The old type cooker plug is still readily available along with the rings etc

    Socket complete with plug top comes out at around R1K

  6. #6
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Quote Originally Posted by Alfred M View Post
    I have never seen n stove couplers installed according to regs. The stove repair i done this week had 2 x 2.5mm surfix connected to stove from isolator.Click image for larger version. 

Name:	Fig-1-stove-couplers-1024x768.jpg 
Views:	485 
Size:	32.1 KB 
ID:	8488
    SANS 10142-1, Edition 2, requires that free-standing cooking appliances be connected via a stove coupler and that a switch-disconnector must be installed.
    Stoves do not need to be connected via a stove coupler anymore. They can be wired directly to the isolator through a flexible arrangement.

    I remove the stove connector on the wall.
    Rewire from the isolator with 4mm house wire leaving 2 metres of slack out the wall.
    Fit a dome lid where the plug was and use spraque ( flexible conduit ) between the dome lid and the stove.

  7. #7
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Derlyn View Post
    Stoves do not need to be connected via a stove coupler anymore. They can be wired directly to the isolator through a flexible arrangement.
    I seem to have a different set of regulations to you , or my understanding of 6.16.3.3 is different .


    SANS 10142-Ed3
    6.16.3.3 Stove connection
    6.16.3.3.1 A stove designed to be a free-standing appliance rated above 16 A
    shall be connected through
    a) a stove coupler which shall comply with SANS 60309-1
    and of dimensions
    as given in SANS 337 (a maximum of 45 A single-phase and 16 A per
    phase for three phase), or
    NOTE 1 Earth leakage protection is not required for the stove circuit when a stove
    coupler is used.
    NOTE 2 For a three-phase coupler, the earth connection needs special
    consideration.
    b) a socket-outlet that complies with SANS 60309-1 (industrial type) with
    30 mA earth leakage protection, however, the use of industrial type socketoutlets
    is not recommended for stove connections.

  8. #8
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Quote Originally Posted by GCE View Post
    I seem to have a different set of regulations to you , or my understanding of 6.16.3.3 is different .

    6.16.3.3.3 The stove connections may be wired directly between the isolator
    and the stove terminals, by means of a flexible arrangement, which are
    mechanically secured and be terminated on either end. When the stove is
    removed, the final section of hard wiring to the stove terminals has to be
    removed and made safe. Amdt 1


    Glad I'm not the only person that interpreted the above as meaning that a stove coupler is not necessary.

  9. #9
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    I went and purchased the lastest addition to ensure that I am on the latest edition even though the changes appear small and the price over the top whereas they should just be issuing amendments to insert on loose pages

    I have to disagree that a stove coupler is not required

    I read the regulations to say that if the stove is a free standing unit it shall have a stove coupler

    6.16.3.3 Stove connection
    6.16.3.3.1Stove connections shall be connected by either 6.16.3.3.2 or
    6.6.3.3.3. Amdt 1
    6.16.3.3.2 A stove designed to be a free-standing appliance rated above 16 A
    shall be connected by means of the following:
    a) a stove coupler which shall comply with SANS 60309-1 and of dimensions
    as given in SANS 337 (a maximum of 45 A single-phase and 16 A per
    phase for three phase), or
    NOTE 1 Earth leakage protection is not required for the stove circuit when a stove
    coupler is used.
    NOTE 2 For a three-phase coupler, the earth connection needs special
    consideration.
    b) a socket-outlet that complies with SANS 60309-1 (industrial type) with
    30 mA earth leakage protection, however, the use of industrial type socketoutlets
    is not recommended for stove connections.
    6.16.3.3.3 The stove connections may be wireddirectly between the isolator
    and the stove terminals, by means of a flexible arrangement, which are
    mechanically secured and be terminated on either end. When the stove is
    removed, the final section of hard wiring to the stove terminals has to be
    removed and made safe. Amdt 1

  10. #10
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Quote Originally Posted by GCE View Post
    I went and purchased the lastest addition to ensure that I am on the latest edition even though the changes appear small and the price over the top whereas they should just be issuing amendments to insert on loose pages

    I have to disagree that a stove coupler is not required

    I read the regulations to say that if the stove is a free standing unit it shall have a stove coupler

    6.16.3.3 Stove connection
    6.16.3.3.1Stove connections shall be connected by either 6.16.3.3.2 or
    6.6.3.3.3. Amdt 1
    6.16.3.3.2 A stove designed to be a free-standing appliance rated above 16 A
    shall be connected by means of the following:
    a) a stove coupler which shall comply with SANS 60309-1 and of dimensions
    as given in SANS 337 (a maximum of 45 A single-phase and 16 A per
    phase for three phase), or
    NOTE 1 Earth leakage protection is not required for the stove circuit when a stove
    coupler is used.
    NOTE 2 For a three-phase coupler, the earth connection needs special
    consideration.
    b) a socket-outlet that complies with SANS 60309-1 (industrial type) with
    30 mA earth leakage protection, however, the use of industrial type socketoutlets
    is not recommended for stove connections.
    6.16.3.3.3 The stove connections may be wireddirectly between the isolator
    and the stove terminals, by means of a flexible arrangement, which are
    mechanically secured and be terminated on either end. When the stove is
    removed, the final section of hard wiring to the stove terminals has to be
    removed and made safe. Amdt 1
    Seems as if they added 6.16.3.3.3 to confuse the hell out of us. Still trying to understand the reason for adding it.

    Yep. R1180 is a bit steep to find out that a geyser must now be on earth leakage.

    I'm guessing that one only needs to wire the geyser through earth leakage if one does any work on same.
    If not it can be left as is ? The same as new socket outlets.

Page 1 of 2 12 LastLast

Similar Threads

  1. New stove plug
    By ians in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 26-Jan-21, 01:11 PM
  2. Stove on E/L
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 27-Sep-20, 07:46 PM
  3. [Question] Stove connection
    By serial5228 in forum Electrical Contracting Industry Forum
    Replies: 19
    Last Post: 15-Jul-20, 07:37 PM
  4. COC for a gas stove
    By ians in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 23-Jan-15, 01:24 AM
  5. stove plate
    By murdock in forum Technology Forum
    Replies: 7
    Last Post: 31-Mar-10, 11:24 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •