I went and purchased the lastest addition to ensure that I am on the latest edition even though the changes appear small and the price over the top whereas they should just be issuing amendments to insert on loose pages
I have to disagree that a stove coupler is not required
I read the regulations to say that if the stove is a free standing unit it shall have a stove coupler
6.16.3.3 Stove connection
6.16.3.3.1Stove connections shall be connected by either 6.16.3.3.2 or
6.6.3.3.3. Amdt 1
6.16.3.3.2 A stove designed to be a free-standing appliance rated above 16 A
shall be connected by means of the following:
a) a stove coupler which shall comply with SANS 60309-1 and of dimensions
as given in SANS 337 (a maximum of 45 A single-phase and 16 A per
phase for three phase), or
NOTE 1 Earth leakage protection is not required for the stove circuit when a stove
coupler is used.
NOTE 2 For a three-phase coupler, the earth connection needs special
consideration.
b) a socket-outlet that complies with SANS 60309-1 (industrial type) with
30 mA earth leakage protection, however, the use of industrial type socketoutlets
is not recommended for stove connections.
6.16.3.3.3 The stove connections may be wireddirectly between the isolator
and the stove terminals, by means of a flexible arrangement, which are
mechanically secured and be terminated on either end. When the stove is
removed, the final section of hard wiring to the stove terminals has to be
removed and made safe. Amdt 1