It is a 4mm2 cable
It is a 4mm2 cable
For a 4mm2 cable , 3phase balanced load
10 Amp circuit breaker 209 meters max
15 Amp circuit breaker 139 meters max
20 Amp circuit breaker 104 meters max
25 Amp circuit breaker 83 meters max
30 Amp circuit breaker 69 meters max
Hope this helps, brother.
So for 100 meters of 4mm cable, the largest breaker you can use is 20 Amp.
Last edited by Derlyn; 02-Aug-23 at 06:52 PM.
Thanks Derlyn. Much appreciated