Thread: Vov generators connected to distribution board supply

  1. #1
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts

    Vov generators connected to distribution board supply

    Most portable generators is vov configured and is not allowed to be connected to db board if not changed according to Sans.

    The changes that needs to be done.
    Use an earth electrode and connect the generator earth point to the earth electrode with a proper earth cable.
    Use the same earth as your supply earth from the portable generator to the changeover switch and distribution board.
    Also connect the earth of the earth rod to the supplier’s earth (same potential).
    Bridge out the neutral and the earth at the generator to have the neutral as close as possible to 0 V, in accordance with SANS 10292. The mts needs to have a separate RCD or connected to db main Rcd with mains power light indication and generator light indication.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,401
    Thanks
    39
    Thanked 331 Times in 278 Posts
    Quote Originally Posted by Alfred M View Post
    Most portable generators is vov configured and is not allowed to be connected to db board if not changed according to Sans.

    The changes that needs to be done.
    Use an earth electrode and connect the generator earth point to the earth electrode with a proper earth cable.
    Use the same earth as your supply earth from the portable generator to the changeover switch and distribution board.
    Also connect the earth of the earth rod to the supplier’s earth (same potential).
    Bridge out the neutral and the earth at the generator to have the neutral as close as possible to 0 V, in accordance with SANS 10292. The mts needs to have a separate RCD or connected to db main Rcd with mains power light indication and generator light indication.
    If you bridge out neutral and earth on a VOV generator you will damage the generator , which is why you cannot connect a vov genset to an installation.

  3. #3
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    Ok so all v-0-v generators are illegal if wired into a db board due to the fact that you will have live potential on neutral and most probably more then 25v between neutral and earth that is allowed according to Sans.Hundreds, probably thousands of small generators have recently been installed and are being installed into homes around the country via the "legal method" of connecting properly into the DB board via a proper change over switch. Do you know if v-0-0 genset exist and wat make of generators are v-0-0 configured to make it legal. I know quite a few people running 5.5kva generators that is v-0-v that have coc signed off for the installations. Do electrical contractors check wiring configuration of gensets before signing of

  4. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,401
    Thanks
    39
    Thanked 331 Times in 278 Posts
    VOV connected homes around the country and legal cannot be used in the same sentence - It is illegal - It is written in SANS 10142-1
    The COC is invalid and not worth the paper it is written on and probable done by a handyman.

    Extract from SANS 10142-1 Ed3
    7.12.2.7 A 230 V generator with a V-O-V earth connection (centre tap on
    winding which is earthed), shall not be connected to a fixed electrical
    installation.
    NOTE Such a generator may be used as a free-standing unit to provide power to
    specific appliances.



    On a vov genset

    Earth to neutral is 110v
    Earth to Live is 110v

    If neutral is bridge to earth it will sort across the coil


    There have been numerous threads on VOV gensets


    https://www.theforumsa.co.za/forums/...tor-connection
    https://www.theforumsa.co.za/forums/...ative-supplies
    https://www.theforumsa.co.za/forums/...-On-Generators

  5. #5
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,678
    Thanks
    124
    Thanked 160 Times in 150 Posts
    Quote Originally Posted by Alfred M View Post
    Ok so all v-0-v generators are illegal if wired into a db board due to the fact that you will have live potential on neutral and most probably more then 25v between neutral and earth that is allowed according to Sans.Hundreds, probably thousands of small generators have recently been installed and are being installed into homes around the country via the "legal method" of connecting properly into the DB board via a proper change over switch. Do you know if v-0-0 genset exist and wat make of generators are v-0-0 configured to make it legal. I know quite a few people running 5.5kva generators that is v-0-v that have coc signed off for the installations. Do electrical contractors check wiring configuration of gensets before signing of
    @ Alfred M

    I have done numerous generator installations and I have found that most new 5,5Kva units for sale now are NOT vov wound.

    The easiest way to check is to start the generator, plug in a small load, lets say a light bulb and then check the voltages with a multimeter. If the earth to neutral voltage is 0v then guaranteed it is not vov wound and it's quite safe to bridge the earth and neutral on the genny.

    If the earth to neutral is 110v with a load connected, then it is VOV wound and shorting the neutral to earth will not work as you are shorting out half of the stator coil on the genny. It can work if the centre tap earth connection is internally disconnected, but it's not as easy as it sounds.

  6. #6
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    Thanks Derlyn

  7. #7
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,505
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    I have always wondered why generator manufacturers made this V-0-V type of generator.
    It then dawned on me the reason.
    All these generators are manufactured for the USA market, in which 110V is the single phase voltage supply, the 0-V connection, however phase to phase is 220V AC that would be the V-V connection.
    It just so happens that the V-V matches our nominal 220V equipment.
    The reason for this is that due to the low voltage of 110V AC for domestic and industrial supply and substantial load, will cause the current to be high, meaning wire sizes and circuit breakers have to be beefed up to match.
    So high power loads, such as stoves, welding machines, power tools and heaters to name a few are connected phase to phase, and hence the generator was manufactured to accommodate the two different loads that may be required to run on the generator.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  8. #8
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,401
    Thanks
    39
    Thanked 331 Times in 278 Posts
    Quote Originally Posted by Justloadit View Post
    I have always wondered why generator manufacturers made this V-0-V type of generator.
    It then dawned on me the reason.
    All these generators are manufactured for the USA market, in which 110V is the single phase voltage supply, the 0-V connection, however phase to phase is 220V AC that would be the V-V connection.
    It just so happens that the V-V matches our nominal 220V equipment.
    The reason for this is that due to the low voltage of 110V AC for domestic and industrial supply and substantial load, will cause the current to be high, meaning wire sizes and circuit breakers have to be beefed up to match.
    So high power loads, such as stoves, welding machines, power tools and heaters to name a few are connected phase to phase, and hence the generator was manufactured to accommodate the two different loads that may be required to run on the generator.
    I was also under the impression that it is a safety issue - It is better on site to have a potential shock voltage of 110v to earth then 220v to earth

  9. #9
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    I have a few gensets for repairs in my shop and ran some test on them this morning with a grinder(850w) contected.Voltage readings.
    Unipower: L-E 153v, N-E 62v L-N 221v
    Macafric: 86v 143v 231v
    Ellies:. 206v. 0v. 229v
    So it seems that Ellies is the only v-0-0 South African manufatered others makes most probably imports

  10. #10
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,678
    Thanks
    124
    Thanked 160 Times in 150 Posts
    Yep. It's best to do that test on each individual genny. Very important to take the measurements only with a load connected.

    It will be very interesting to see what voltages you get with no load using a multimeter. The chances are good that you gonna get some strange readings even on the Ellies genny.

  11. Thanks given for this post:

    ACEsterhuizen (22-Sep-23)

Page 1 of 4 123 ... LastLast

Similar Threads

  1. Pump supply connected to City Power point of supply board
    By kosmonooit in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 10-Dec-21, 10:10 AM
  2. VoV generators connected to DB
    By Generators??? in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 01-Jan-20, 07:45 PM
  3. Moving a distribution board.
    By Leslie Clark in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 08-Oct-17, 02:26 PM
  4. 3 generators one supply
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 11-Jun-17, 04:03 PM
  5. [Question] Fused distribution board
    By pes in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 11-Aug-13, 08:01 AM