    Quote Originally Posted by Derlyn View Post
    @GCE
    If one were to use a small enclosure with 2 fuse holders and 20 Amp glass fuses, would that also be seen as a sub db?

    Is there a way of reducing the conductor size without creating a sub db ?

    Derlyn
    This is what I considered doing ... because working with a 6 mm wire and in a new hob or oven is ridiculous.

    I also thought of mounting a galvanised box to the oven connect the 6 mm from the isolator into a one of the those fused terminals then 4mm from there to the hob and 2.5 mmm to the oven.
    Comments are based on opinion...not always facts....that's why people use an alias.

  2. #2
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    What I found when I arrived on site ... a piece of pvc sprag with 6 mm wires (open) with a connector block and a 2.5 mm twin wire feeding the hob.

    Something to consider ... in the past if the switches were mounted on the oven ... there would be connectors mounted on the top of the oven with female plugs ... then there would be loose wires with a male connector ... in the space between the hob and the oven ...everything is open wiring ... my question then would be why did I waste my time connecting all the wires in a junction box.

    In saying that ... in the past the oven and stove were secured to the counter and cupboard with the use of a tool ... so if I secure the oven and hob ... the space between the oven and hob because part of the fixed appliances ?
    Comments are based on opinion...not always facts....that's why people use an alias.

  3. #3
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Something you need to be careful ... people cut a hole in the side of the cupboard ... which would expose all the wires ... that creates a new problem ... and some people dont secure the hob nor oven ... once again makes it open wiring.
    Comments are based on opinion...not always facts....that's why people use an alias.

  4. #4
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    ANY ADVICE WELCOME

    Busy with a kitchen refurbishing job.

    The plans call for a socket outlet for the gas stove / electric oven combo unit.

    The stove has a plugtop.

    Photo's attached.

    What do I do ?

    Derlyn.


    Click image for larger version. 

Name:	20220218_124601.jpg 
Views:	1283 
Size:	49.6 KB 
ID:	8477


    Click image for larger version. 

Name:	20220218_124730.jpg 
Views:	1232 
Size:	63.9 KB 
ID:	8478


    Click image for larger version. 

Name:	20220218_125119.jpg 
Views:	1266 
Size:	53.3 KB 
ID:	8479

  5. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Derlyn View Post
    ANY ADVICE WELCOME

    Busy with a kitchen refurbishing job.

    The plans call for a socket outlet for the gas stove / electric oven combo unit.

    The stove has a plugtop.

    Photo's attached.

    What do I do ?

    Derlyn.


    ]
    The gas regs insist on a isolator which in my opinion is playing outside of their field of expertise , but unfortunately it is written as such and the gas installer could refuse to issue a gas COC . ( reg below)

    If you now install a socket and the gas coc is not forthcoming then you could be held responsible to rectify at your own cost.
    To me it is pathetic that they stipulate as such but it is out of our hands .

    Extract from SANS 10187-1
    9 Electrical equipment and other sources of ignition
    Where electrical equipment is placed within the safety distance as specified in figures 3, 4 and 6
    such equipment shall be in accordance with the requirements of SANS 10108.
    Electrical equipment, such as light switches and plugs, shall be at least 200 mm away from any
    burner and potential point of gas release. Where it is necessary to install a gas hob together with an
    electric oven, a three-point plug socket shall not be used to connect the electric oven. A proper
    isolator switch shall be in place above the level of the hob and it shall have at least 200 mm
    clearance from the hob.

    No electrical connection shall be made below the hob. See figures 3 and 4 for further connection


    The electrical regulations on freestanding stoves allow a 16Amp socket if the rating of the oven is below 16Amp
    I would send an email to the owner informing them of the conflict between the regulations and the possible consequences of installing a socket vs a stove isolator.
    If they respond and insist on a socket at least you cannot be held responsible at a later stage if the gas guys do not want to issue a certificate .
    Make sure it is in writing and keep it as a sale may go down in 12months time and it may come back to bite.


    Extract from SANS 10142-1
    6.16.3.3 Stove connection

    6.16.3.3.1 A stove designed to be a free-standing appliance rated above 16 A
    shall be connected through
    a) a stove coupler which shall comply with SANS 60309-1 and of dimensions
    as given in SANS 337 (a maximum of 45 A single-phase and 16 A per
    phase for three phase), or
    NOTE 1 Earth leakage protection is not required for the stove circuit when a stove
    coupler is used.
    NOTE 2 For a three-phase coupler, the earth connection needs special
    consideration.
    b) a socket-outlet that complies with SANS 60309-1 (industrial type) with
    30 mA earth leakage protection, however, the use of industrial type socketoutlets
    is not recommended for stove connections.

  6. #6
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Total electrical power consumption is 2900 Watts. +- 12 Amps.

    Have once again confirmed with the gas installers and they are happy with a socket outlet.

    Next question.

    When we inspect an installation to issue an ELECTRICAL COC, do we not inspect it according to SANS 10142-1 ?
    If it conforms to SANS 10142 -1, Municipal bylaws, electrical regulations in OHSA and manufacturer specs, I issue the COC. It's compliant.

    Should the gas guy need something altered on the electrical installation, he is welcome to make use of an electrical contractor of his choice to make the necessary changes. It does not have to be me. Seeing that he is insisting on something being altered, it's up to him or the seller to have it done.

    During 2018 some time I had the same issue when a gas inspector insisted I move the isolator.
    This happened after I had already delivered the COC to the transferring attorneys.

    I refused.

    Here is the email I sent to the attorneys after they also tried to force me. I refused.

    Hi Glenda

    I have noted Mr Schoeman's comments and need to respond.

    Firstly, I am not being difficult ...... Let me explain.

    Point 2 of removing the isolator and fitting a blank cover in it's place would cause the electrical installation to be non compliant.
    It would have been possible had the distribution board been in the kitchen, but on this particular installation, the DB is in the garage.

    Our regulations state that the isolator must be in the same room as the appliance.

    The only other option to satisfy the gas technician, in this case, was to move the isolator.

    This would have entailed the following.

    Cutting into the wall with an angle grinder in order to reposition a new box and conduit. This process creates a mammoth amount of dust throughout the house. We then have to contend with claims from tenants that their expensive electronic equipment has been ruined as a result of the dust.

    We then have to cement in the new enclosure and conduit and wait 2 days for same to dry before installing the isolator. After installing the isolator we have to repaint the cemented area and this often ends up with us having to paint the whole wall as a match in paint colour is virtually impossible when the existing paint is old.

    Should there be tiling involved, which is often the case, we have to get a tiler to come and make good.

    ALL of the above has happened to me in the past, whilst moving a stove isolator at the request of the gas technician and I have had to bear the costs.

    It might sound easy on paper to just move the switch, but in practice it's not that quick and easy. There are the above ramifications that need to be taken into account. I'm talking from experience.

    The gas technician is quite entitled to make use of the services of an electrician to move the isolator so as to comply with the gas laws, however, I shy away from this job for the above reasons.

    I note that the gas technician has issued the gas compliance certificate with an explanatory note.

    I have not read this note but sincerely hope that it does not contain the words D. Stuart or Derek's Electrical. Should my reputation be harmed in any way as a result of any explanatory note mentioning my name or my business name without my consent, there will be serious legal ramifications for whoever issued same.

    Going forward, should the same circumstances as 5 Place Gonubie occur, my stance will remain the same.

    Hope you understand

    Kind regards ... Derek.



    Never heard from them again.

  7. #7
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    If ever I come across a dedicated plug that's too close to a tap, I'm gonna do the same as what the gas guys are doing

    and refuse to issue a coc until the tap has been moved.

  8. #8
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,789
    Thanks
    3,331
    Thanked 2,694 Times in 2,271 Posts
    Blog Entries
    12
    Quote Originally Posted by Derlyn View Post
    If ever I come across a dedicated plug that's too close to a tap, I'm gonna do the same as what the gas guys are doing

    and refuse to issue a coc until the tap has been moved.


    You are not going to quote to move the dedicated socket outlet to a safe distance?

    A thought on the 10142-1 Edition 3 update i.r.o. taking cognisance of the gas installation standard - is there a reciprocal clause added to the gas installation standard?

  9. #9
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Derlyn View Post
    Next question.

    When we inspect an installation to issue an ELECTRICAL COC, do we not inspect it according to SANS 10142-1 ?
    If it conforms to SANS 10142 -1, Municipal bylaws, electrical regulations in OHSA and manufacturer specs, I issue the COC. It's compliant.
    .
    Sans 10142-1 ED3 has had a clause added under 5.2.4 as pasted below - You need to take it into account if there is a gas stove in position



    5.2.4 Positioning of equipment
    Electrical equipment which, under normal conditions will be
    a) exposed to flammable or explosive gas, vapour, dust or liquid, or to
    external influences such as direct sunlight, corrosive vapour or oil, or
    b) in a hazardous location,
    shall be so selected or enclosed that it is protected against harmful effects
    or it shall comply with the requirements of an applicable standard (or both).
    c) for combined gas and electrical installation, cognisance shall be taken of
    the requirement stipulated in SANS 10087-1.

  10. #10
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Seems like they've now got us by the S & C's. That wasn't the case in 2018.

    How many SANS regs other than 10142 - 1 must be taken into account when there's a gas stove in the kitchen.

    In this thread alone 10187-1, 10108 and 10087-1 is mentioned.
    While we busy with this topic, are there any more ?

    I hope each one of the above doesn't cost the same as SANS 10142 -1.

    Glad I'm slowly busy winding down. All these regs are getting a bit complicated for this toppie.

Page 2 of 3 FirstFirst 123 LastLast

Similar Threads

  1. [Question] Air Conditioner connections
    By SeanM in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 16-Dec-21, 08:19 AM
  2. [Question] Inverter connections
    By RegElec in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 24-Mar-21, 01:03 PM
  3. Stove/cooker connections
    By ians in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 30-Nov-20, 05:33 AM
  4. [Question] Connections/junctions (again)
    By Jacques#1 in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 22-Apr-10, 12:12 PM
  5. Municipal Connections
    By Alan in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 01-Jun-06, 10:47 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •