Results 1 to 6 of 6

Thread: When is a double pole isolator required for a fan

  1. #1
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts

    When is a double pole isolator required for a fan

    I believe this requires a thread on its own.

    When is a double pole isolator required?

    Lets use a common application ... the extractor fan connected to the light in the bathroom ... do you need a double pole isolator for this application if the light circuit is on earth leakage?

    A ceiling fan in a bedroom with a light ... do you need a double pole isolator if the light circuit is connected to the earth leakage ?

    If the extractor fan is in a bathroom but not connected via the light fitting?

    can you fit the double pole isolator in the roof next to the fan ?

    Can you use a 5 amp socket outlet instead of a double pole isolator ...between the light and the extractor fan?

    Can you use a standard socket outlet for the extractor fan located out of reach in the ceiling.

    can you use a combo breaker/isolator in the DB to feed the light circuit made up of lights and extractor fans.

    I am sure the reare other questions related to this topic.
    Comments are based on opinion...not always facts....that's why people use an alias.

  2. #2
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Also if the CB is a single pole but the correct markings for isolation then does it have to be double pole?

    Unless it specifically states to use a double pole or that the LIVE (N & L) must be switched.

    Sent from my SM-N960F using Tapatalk

  3. #3
    Full Member W-TDMI's Avatar
    Join Date
    May 2013
    Location
    George
    Posts
    39
    Thanks
    2
    Thanked 7 Times in 7 Posts
    All your answers is in the following sub sections:
    6.9.2 but more specific 6.9.3.1 and 6.16.1.3 and 6.16.1.4

    In short if its on E/L no isolator is required - If no E/L must have isolator 1.5m from fan OR Lockable in the open position if in the DB.

  4. #4
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by W-TDMI View Post
    All your answers is in the following sub sections:
    6.9.2 but more specific 6.9.3.1 and 6.16.1.3 and 6.16.1.4

    In short if its on E/L no isolator is required - If no E/L must have isolator 1.5m from fan OR Lockable in the open position if in the DB.
    What if you replace the light switch with a double pole and it is not 1.5m because the fan is the slab... but in the same room or at the entrance to the room/bathroom ?

    Or in a case where I had no choice but to fit a double pole relay/contactor ... has 30 amp double pole relay got the isolation properties of a manual isolator ?
    Comments are based on opinion...not always facts....that's why people use an alias.

  5. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by W-TDMI View Post

    In short if its on E/L no isolator is required - If no E/L must have isolator 1.5m from fan OR Lockable in the open position if in the DB.
    I disagree - A fan is a motor and falls under motor - A lockable in a DB will not be acceptable

    6.16.4.3 Extraction fans
    Where an extraction fan supply is switched with a luminaire, it shall be
    connected to the switched portion of the light circuit, provided that the fan
    circuit is connected by means of a SANS 164-3 or SANS 164-2-1 or
    SANS 164-2-2 socket-outlet or a switch disconnector.

    6.16.5.1.4 Each motor shall be supplied by a manually operated disconnector
    or any other manually operated disconnecting arrangement such as a
    withdrawable circuit-breaker, a removable link, a fuse or by the removal of a
    plug from a socket-outlet, which provides at least the same isolating distance,
    for the sake of safety, as a disconnector that is
    a) readily accessible and mounted on or next to the motor, or
    b) visible from the motor, or
    c) lockable in the open position, or
    d) housed in a lockable enclosure other than a distribution board.

  6. #6
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    For the record the plugs GCE refers to are found on page 335 ,,, annexure R.
    Comments are based on opinion...not always facts....that's why people use an alias.

Similar Threads

  1. Hammond pole attorneys
    By ians in forum General Chat Forum
    Replies: 13
    Last Post: 12-Oct-21, 09:14 AM
  2. Why double pole isolators
    By ians in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 04-Sep-21, 09:41 AM
  3. Hob Isolator
    By chriskrn1 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 22-Aug-16, 12:14 PM
  4. triple pole breaker for a single phase supply
    By washayag in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 28-Sep-15, 04:57 PM
  5. Double tube Double headscratch
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 14-Apr-11, 06:38 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •