    Had a question posed on a stove isolator position
    Contractor went in to carry out an inspection and issued a coc for a sale to go through.

    Kitchen is upmarket and fully tiled and as happens there is a gas hob with an isolator above it.
    The unit was built , as an estimate , around 2005.

    The seller tells the contractor that the stove is not part of the sale and is removing the stove, so no need to relocate the isolator.

    The seller removes the stove - The new owner takes possession and buys a gas stove and the gas installer will now not issue a gas certificate as the isolator is above the hob, as per pic.
    The stove is a freestanding stove.

    The new owner now wants the Electrical contractor to rectify the isolator position at the contractors cost as he reckons the COC is invalid.
    Part of the reason is because he saw the gas hob in the position when he view and signed the purchase agreement.

    Looking through the regulations , I keep switching between whether the contractor is correct or incorrect.

    What and why would you do differently

    Click image for larger version. 

Name:	A- stove isolator .jpg 
Views:	1206 
Size:	41.8 KB 
ID:	8469

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Usually a gas stove is supplied with a normal 3 pin plug in which case the socket outlet into which it is plugged into serves as the isolator.

    If the above is true then I would remove the isolator and fit a blank plate in order to satisfy the gas contractor.

    Derlyn

  3. #3
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    I saw a similar thing a couple days ago ... a socket below a tap ... the question was simple in that case ... was the tap installed before or after the socket outlet.

    I have situation right now similar to this ... a little more complicated ... there is a stove isolator above the removeable electric stove and the DB is also above the stove not higher than 2.2 m and no extractor ... I am waiting for a copy of the COC which was last week.

    The first question ... could you fit a stove isolator above a stove in the past ... if yes then there is no problem ... if the new owner purchased a gas hob and now you cant have a stove isolator above the gas hob ... whoever purchased the gas hob must pay to make it legal according to current regulations ... how could the inspector who issued the COC know the new owner was going to buy a gas stove.

    If the stove that was in place was removed as indicated to the inspector then he has done nothing wrong ... if the stove was not removed and still in place ... then the seller who indicated that the stove would be removed would be liable for the costs. If the inspector was smart he would have written note on the COC about the stove.

    We all know it is a really dumb place to have a stove isolator ... so close the stove using a plastic isolator ... really smart ... looking at the pic you dont need regulations to tell you its not right.

    Just a note ... the isolator would be behind the stove if it was an electric stove ... normally electric stoves have have a back piece for the switches
    Comments are based on opinion...not always facts....that's why people use an alias.

  4. #4
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Who would fit a fridge next to a gas stove ?
    Comments are based on opinion...not always facts....that's why people use an alias.

  5. #5
    Silver Member
    Join Date
    Mar 2008
    Posts
    373
    Thanks
    5
    Thanked 51 Times in 44 Posts
    In terms of electrical regs:- 6.16.1.2 c)preferably not above the cooking application
    Interms of gas regs - 200mm from edge of hob

  6. #6
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,789
    Thanks
    3,331
    Thanked 2,694 Times in 2,271 Posts
    Blog Entries
    12
    With the isolator that close above the hob, I can't help but think of 5.6.1 on environmental conditions or 5.3.8 on positioning of electrical equipment and wince a little. With SANS 10142-1 going on to specifically deal with the positioning of cooking appliance isolators (as mentioned in skatingsparks' post above), can we play that card though? Surely the drafters of the Standard have discussed this issue and decided on an advisory tone rather than an unambiguous determination.

    So from an electrical regs point of view, it's bad design and while the location of the stove relative to the isolator is inadvisable for any cooking appliance, sadly compliant from a SANS 10142-1 point of view. Even with a gas appliance present, at least up until the gas standard was added as a reference to SANS 10142-1 (speaking under correction, I believe it has been added but don't have an edition 3 copy of SANS 10142-1 handy right now to double check).

    From a gas regs point of view, never compliant.

    For the electrician the best CYA in the situation you presented is a photo of the situation as at the time of the issue of the (I assume a 9.2.b) CoC.
    If that photo had the gas stove in place and the electrician was relying on the statement by the seller - we don't rely on verbal statements from the seller; get it in writing.
    And add a note in the CoC.

    Just to add to the mix, what if there is fixed gas supply piping in place and no cooking appliance..?

  7. #7
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by skatingsparks View Post
    In terms of electrical regs:- 6.16.1.2 c)preferably not above the cooking application
    Interms of gas regs - 200mm from edge of hob
    For the record this reg is 6.16.3.1.2 c) ... I thought it had been removed under amdt 4 ... but then found it.
    Comments are based on opinion...not always facts....that's why people use an alias.

  8. #8
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    I dont believe the inspector is at fault because the new owner could have installed an electric stove and its preferred that you don't install the isolator above the appliance, but it was already there. How was the inspector to know the new owner would by a gas stove.

    The fact that he did buy a gas stove, now makes him responsible to bring the installation up to standard latest standards.


    The key word ... preferably

    Pg 186 ed(3.1)


    6.16.3.1 Switch-disconnector
    6.16.3.1.1 The circuit that supplies a cooking appliance through fixed wiring,
    a stove coupler (see 6.16.3.3), or an industrial type socket-outlet
    (see SANS 60309-1), shall have a readily accessible switch-disconnector.
    The switch-disconnector may supply more than one appliance.
    6.16.3.1.2 A switch-disconnector for a cooking appliance(s) shall
    a) be in the same room as the appliance(s),
    b) be at a height above floor level of not less than 0,5 m and not more than
    2,2 m,
    c) preferably not be above the cooking appliance(s),
    d) be within 3 m of the appliance(s), but within 0,5 m of the appliance(s) if the
    switch-disconnector's purpose is not clearly indicated, and
    e) not be fixed to the appliance.

    Note 5.2.4 c)

    5.2.4 Positioning of equipment
    Electrical equipment which, under normal conditions will be
    a) exposed to flammable or explosive gas, vapour, dust or liquid, or to
    external influences such as direct sunlight, corrosive vapour or oil, or
    b) in a hazardous location,
    shall be so selected or enclosed that it is protected against harmful effects
    or it shall comply with the requirements of an applicable standard (or both).
    c) for combined gas and electrical installation, cognisance shall be taken of
    the requirement stipulated in SANS 10087-1.

    https://thegasman.co.za/pages/lp-gas-regulations
    Comments are based on opinion...not always facts....that's why people use an alias.

  9. #9
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    My one is going to get interesting even though the DB and the isolator can be mounted above the appliance (the stove is electric) ... however I dont believe the DB is IP 44 rated.

    Who would mount a DB above a stove even if it is IP 67 rated) common sense would tell me it a ridiculous idea.

    6.6.1.7 A distribution board shall not be mounted
    a) in a bathroom, except outside zone 3 and unless the enclosure provides
    an IP rating of IPX5 (see 7.1.4.3.6),
    b) above a fixed cooking appliance or in a position where a cooking appliance
    could be put below it, unless the enclosure provides a degree of protection
    of at least IP44, or
    Comments are based on opinion...not always facts....that's why people use an alias.

  10. #10
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    I think we can have a week long discussion about the positioning of isolators and socket outlets in kitchens and after that, at some stage, each one of us is still going to find ourselves in a position where we are not 100% sure if the position of a certain plug or isolator is legal or not.

    Reading through the regs again, I cannot find anything regarding cooking appliances rated at less than 16A. Please correct me if I have overlooked something.

    How legal is it to have an undercounter plug supplying an appliance with the appliance( washing machine) pushed under the counter conceiling the plug? Same with a fridge in a cupboard with the plug directly behind it. Same with an extractor above the stove being plugged into a plug in the attic with it's lead running through the chimney into the attic.

    So many questions.

    Derlyn

Page 1 of 5 123 ... LastLast

Similar Threads

  1. Distribution board isolator
    By ians in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 16-Dec-21, 10:42 AM
  2. 2 x 10mm in Isolator.
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 27-Oct-20, 09:06 PM
  3. [Question] Hob an Built in Oven Isolator Switch
    By pedruid in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 11-Mar-17, 10:13 AM
  4. Hob Isolator
    By chriskrn1 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 22-Aug-16, 12:14 PM
  5. [Question] Position relocation
    By oaktree in forum Labour Relations and Legislation Forum
    Replies: 4
    Last Post: 10-Mar-15, 07:47 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •