Comments are based on opinion...not always facts....that's why people use an alias.
Been reading the replies -
My thoughts are that the Contractor is signing off as reasonable safe and would be referring to the code at the time of installation - The installation was around 2005 and no reference was made to Gas regs , this only came about in Ed 3 July 2020
The reference to gas regulations is also hidden away ( in ED3) under fundamentals 5.2.4 and unfortunately is not under fixed appliances and particularly stoves which I think should be rectified .
The gas regulations state the isolator shall be above the level of the oven and 200mm clearance from the hob.( Pasted relevant section below)
What is wrong with pulling the freestanding hob 200mm away from the wall , the isolator is above the hob and now 200mm away - Surely it is then legal ?
In terms of the OHS Act, the provisions of this part of SANS 10142 apply
only from the point of control to the point of consumption.
Because this part of SANS 10142 is continually updated, problems can arise
on which version of the standard will be applicable when a contract is
signed. The date of approval of the latest revision or amendment of this part
of SANS 10142 will be the implementation date of the revision or the
amendment. The applicable version of this part of SANS 10142 is the one
with the latest implementation date before the contract date. So contracts
signed before the approval of an amendment shall be carried out in
accordance with the provisions of the unamended standard. If an existing
installation is extended or altered, such extension or alteration shall comply
with the provisions of this part of SANS 10142 that were applicable at the
time of the erection of the extension or alteration.
The edition of the standard that was applicable at the date of erection of an
electrical installation is to be considered the edition defining the
requirements applicable to that particular electrical installation.
SANS 10087-1:2013 Ed6
9 Electrical equipment and other sources of ignition
Where electrical equipment is placed within the safety distance as specified in figures 3, 4 and 6
such equipment shall be in accordance with the requirements of SANS 10108.
Electrical equipment, such as light switches and plugs, shall be at least 200 mm away from any
burner and potential point of gas release. Where it is necessary to install a gas hob together with an
electric oven, a three-point plug socket shall not be used to connect the electric oven. A proper
isolator switch shall be in place above the level of the hob and it shall have at least 200 mm
clearance from the hob.
No electrical connection shall be made below the hob. See figures 3 and 4 for further connections.
The gas regualtions call for an isolator and do not allow a socket
9 Electrical equipment and other sources of ignition
Where electrical equipment is placed within the safety distance as specified in figures 3, 4 and 6
such equipment shall be in accordance with the requirements of SANS 10108.
Electrical equipment, such as light switches and plugs, shall be at least 200 mm away from any
burner and potential point of gas release. Where it is necessary to install a gas hob together with an
electric oven, a three-point plug socket shall not be used to connect the electric oven. A proper
isolator switch shall be in place above the level of the hob and it shall have at least 200 mm
clearance from the hob.
No electrical connection shall be made below the hob. See figures 3 and 4 for further connections.
This is interesting.
I have communicated with 3 gas installers regarding the above regulation and they are all of the opinion that a gas stove incorporating an electric oven in one unit, supplied with a 3 pin plug, does not need an isolator and can be plugged into a socket outlet.
The above regulation (9) only comes into play when the gas hob and electric oven are 2 seperate units. The oven must then conform to the regulations for electric ovens which requires that it has to have an isolator. The gas hob can however still be plugged into a socket outlet by means of the 3 pin plug provided.
Something else mentioned was that should the gas stove be of the type with a glass protector over the burners that is flipped up backwards when a burner is used, then the isolator may be on the wall above the stove.
Derlyn
Last edited by Derlyn; 14-Feb-22 at 11:24 PM.
Let me get some popcorn and beer ... this is getting interesting.
You live and learn ... my understanding has always been that a hob is unit dropped into a fixed counter top and under counter or eye level oven is fitted into a fixed cupboard ... in the past instead of installing 6 mm wire with a 40 amp breaker ... for a hob/eye level oven ... we would use a 4 mm wire and install a 30 amp breaker for each unit.
If the gas hob/electric oven has a standard 16 amp plug top ... firstly the warranty would fall away if you cut the plug off. If the manufacturer designs the appliance to be plugged into the wall why would you change the manufactures specs
Why are the units not being fitted with the new 164-2 type plug top?
Comments are based on opinion...not always facts....that's why people use an alias.
If you fit the isolator above the hob ... what happens if there is a fire on the hob? maybe the reg should change to 200 mm and not above the hob ... same with a DB ... why would you allow a DB above a stove even if it is IP 44 rated.
the last time I forgot the popcorn on the stove during one of these long threads ... by the time I got back to the kitchen the flame was already touching the ceiling ... lucky I had a fire bucket full of sand next to the stove .. .from the last time I forgot about the popcorn.
Comments are based on opinion...not always facts....that's why people use an alias.
This has been educational for me as I also was not 100% sure of all the regs regarding gas free standing stoves and gas hobs.
Thanks to GCE's original question which started this thread, I can now say with confidence that I now know what's cutting.
So, to answer GCE's original question.
I note from the photo that the gas stove is a free standing unit incorporating an electric oven. It would have been supplied with a plugtop so the solution would be to blank off that isolator with a metal blanking plate and plug the unit into a socket outlet. Problem solved.
I also agree that only cooking appliances rated at more than 16A need dedicated cooking circuits with isolators. That takes care of all the 2 plate hotplates, countertop mini ovens, microwave ovens etc.
Learn't a lot from this thread.
Have a good day
Derlyn
SANS 10087-1:2013 Ed6
9 Electrical equipment and other sources of ignition
Where electrical equipment is placed within the safety distance as specified in figures 3, 4 and 6
such equipment shall be in accordance with the requirements of SANS 10108.
Electrical equipment, such as light switches and plugs, shall be at least 200 mm away from any
burner and potential point of gas release.
Where it is necessary to install a gas hob together with an
electric oven, a three-point plug socket shall not be used to connect the electric oven. A proper
isolator switch shall be in place above the level of the hob and it shall have at least 200 mm
clearance from the hob.
No electrical connection shall be made below the hob. See figures 3 and 4 for further connections.
No logic in this (in bold.) when, right there AT the burner, A PIECE ELECTRICAL EQUIPMENT IS ALREADY INSTALLED RIGHT BY THE BURNER, AND USED TO IGNITE THE GAS RIGHT THERE AT THE BURNER. (IGNITER)
An electrical connection IS ALREADY MADE RIGHT UNDER THE HOB, WHERE THE CABTYRE ENTERS THE OVEN FROM THE PLUG TO BE CONNECTYED ON THE TERMINALS OF THE OVEN.
(my gas installer agrees, its a joke.)
GCE (15-Feb-22)