    Common code violations

    Some of the common code violations I see on a daily basis.

    depth and cable marker

    b) at least 0,5 m, the backfill around them shall not contain sharp objects and
    there shall be a marker tape that runs above the route of the cable, at a
    depth of between 0,3 m and 0,4 m.
    Comments are based on opinion...not always facts....that's why people use an alias.

  2. #2
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    This reg should be applied to twin+E not only open wiring.


    6.4.5.2 Each conductor of an open wiring system shall be visible where it is
    installed on, over, or next to beams that can be used for walking on, or it shall
    be suitably protected against mechanical damage.

    This reg would make twin above the beams ... without mechanical protection a code violation

    6.4.6.2 Unarmoured multicore cables do not require additional mechanical
    protection if they are installed
    a) under plaster in walls, or
    b) under raised floors, in spaces above ceilings, in partitions or in wall cavities,
    but only if they will not be damaged during installation.
    6.4.6.3 Unarmoured multicore cables need not be fixed in position in places
    such as in roof spaces above ceilings and where the cables are unlikely to be
    disturbed.
    Comments are based on opinion...not always facts....that's why people use an alias.

  3. #3
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    The inspection I am busy with had some of the following issues ... which are all common problems ... lets make this interesting ... add what you feel would be the code related to the violation of each item.

    1/ A junction box built into a wall ... I knock a hole into the new wall to gain access to the junction box in the existing wall ... The twin flex wire feeding the light in the roof was plastered.

    2/ Old steel piping used as the earth continuity ... I found light switches which had high resistance reading ... the steel screws were rusted.

    3/ Old steel pipe feeding the outbuilding was rusted ... which caused 2 code violations ... the first a high earth resistance reading and the second low insulation resistance reading.

    4/ Not one of the ceiling fans had an earth wire ... due to the steel piping ... no bonding strap was installed nor earth from the DB.

    5/ A 4 mm cable feeding an isolator inside the house and the pool DB (still looking to see if it is a code violation) ... the cable had and open connection with the screwits exposed and the cable from the isolator to a double socket outlet has a 2.5 mm wire between the isolator and the plug.

    6/ Faulty earth leakage unit ... the test button did not trip the unit ... and the earth leakage plug test didnt trip the unit.

    7/ Incorrect labels and missing labels.

    8/ What I thought was was illegal ... however as pointed out ... the use of cabtyre as part of an electrical installation is allowed as per ... as per 3.8.3 and 6.1.1.11 and 6.3.3

    9/ Another which I need to check ... the use of 1.5 mm surfix to connect ... lights but using a 15 amp double socket with a 15 amp mcb ... sothe cable runs from the DB to a socket outlet and to a pole light ... the socket outlet has string lights. plugged into it.
    Comments are based on opinion...not always facts....that's why people use an alias.

  4. #4
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    When doing the test report I believe it should be completed in a manner which makes it easy to identify the problem with the code violation.

    For example:

    1/ Day/night switch mounted on the left side of the outbuilding not compliant as per regulation 6.3.3.2 (a) (2)

    If the test report attached to the quote for repairs doesnt have a detailed breakdown like this ... you send it back to the "inspector" ... if the inspector cannot provide you a detailed breakdown like this you tell him to piss off ... and find someone who can.

    2 reason he cant provide the details ... maybe he is not up to date with the code or is incompetent to be issuing COc's.

    If you receive a quote with a list that looks like this :

    1/ No earth on the light

    2/ open wiring

    3/ label missing

    best you be looking for a suitably qualified inspector ...

    If you just looking for a cheap COC and dont give a rats ass about the buyer (as in most cases) then the second option is the way to go

    If you the buyer ... get smart and request a copy of the quote with the test report and the COC ... if it looks like the second option ... best you put a hold on the transfer and get a second opinion.
    Comments are based on opinion...not always facts....that's why people use an alias.

  5. #5
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,583
    Thanks
    113
    Thanked 150 Times in 142 Posts
    It all depends who I am quoting for.

    I do not do many COC'S anymore because the attorneys and estate agents think I'm smoking something when I insist on a commisioning fee and the balance cash on completion.

    I have pointed out to them that legally I cannot give them credit as I am not a registered credit provider but they couldn't care.

    Be that as it may, when I do, on
    the odd occasion, att quote on a coc for transfer purposes I give as little details as possible. You give too much detail, your quote gets given to the buddy to beat and he gets the job without even going to site to do an inspection.

    My regular clients dont need much detail. They know they getting value for money.

    Peace out .. Derek.

  6. #6
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Derlyn View Post
    It all depends who I am quoting for.

    I do not do many COC'S anymore because the attorneys and estate agents think I'm smoking something when I insist on a commisioning fee and the balance cash on completion.

    I have pointed out to them that legally I cannot give them credit as I am not a registered credit provider but they couldn't care.

    Be that as it may, when I do, on
    the odd occasion, att quote on a coc for transfer purposes I give as little details as possible. You give too much detail, your quote gets given to the buddy to beat and he gets the job without even going to site to do an inspection.

    My regular clients dont need much detail. They know they getting value for money.

    Peace out .. Derek.
    The problem is the way the system is operating ... people ask for a COC ... companies offer the "COC" at a fixed rate ... be it R650 or R850 or R1500 ... there seems to be no fixed fee

    I am busy with a test report/COC at the moment (on hold until next week) ... the estate agent offers the "COC" included in their fee ... so the customer decided to rather go with the estate agent "free" COC ... I told the customer to contact the estate agent and find out if this "free" COC includes any repairs required if any items fail on the "test report" ....... and that where the fight started.

    We all know how the free "COC's" work ... we all know nothing in life is free.

    One day when a public awareness program is launched (the truman bubble ) ... people will understand how it works.

    A tip ... if you are selling your house request a fee for the "COC" and a fee for the "test report" ... if the company or estate agent offers a free COC included in the price ... ask what it is going to cost to issue a test report including the repairs if required.

    It use to take me 45 minutes to fill out a 3 page test report and the 1 page COC (total 4 pages) ... I hear the new COC/TEST report is only 2 pages.

    Will update once I have collected the new documents.

    I can by many test reports that I receive to investigate ... the document is a generic document filled in by the same person in the office with the same test results.
    Comments are based on opinion...not always facts....that's why people use an alias.

  7. #7
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    771
    Thanks
    121
    Thanked 35 Times in 34 Posts
    Many client comes with wide eyes when you say how it actually works and the true cost and time scale....

    They think a CoC is a shop around for the cheapest and quickest to get that box ticked for the sale.... and I mean high degree people of acronyms longer than my arm dont understand it and then I explain the repercussions and the law then the eyes are even wider...

    Anyway my new thing I have also decided to do, much like my fitness and cycling is I do me and you do you and I do not compare my self to them as I am not them and they are not me...


    And want to do more research on who actually pays for it when it goes wrong, buyer or seller and from what Ians said got me thinking on it.

    Sent from my SM-N960F using Tapatalk

  8. #8
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    771
    Thanks
    121
    Thanked 35 Times in 34 Posts
    For me this one is a violation of new builds ( as not sure when it changed)

    As I understand it is that a socket circuit can not have a 20A breaker as it would then need a protected socket outlet.

    6.15.3 Single-phase circuits that only supply socket-outlets rated
    at 16 A
    Single-phase circuits that only supply socket-outlets rated at not more than
    16 A
    a) shall have overcurrent protection,
    b) shall use conductors that are rated at not less than 16 A, and
    c) shall, if the circuit protection is rated at more than 20 A, use only protected
    socket-outlets, with, as far as is practicable, discrimination between the
    protective devices for the circuit and the protective devices associated with
    the socket-outlets. The protective device of a protected socket-outlet shall,
    1) have a fixed rated current that does not exceed the rating of the socket-
    outlet,
    2) be mounted next to the socket-outlet that it protects,
    3) provide protection against overload currents,
    4) provide protection against short-circuit currents, unless short-circuit
    protection is provided by a separate device, for example, on the
    distribution board,
    5) if it needs the protection of a back-up short-circuit device, be marked
    with the required or maximum rating of the back-up device,
    6) if it protects more than one socket-outlet, be so installed that all the
    socket-outlets are connected in parallel, have the same rated current,
    and are mounted next to the device, and
    7) if it is a circuit-breaker, comply with the requirements of 6.8.2.

    Sent from my SM-N960F using Tapatalk

  9. #9
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Dylboy View Post




    c) shall, if the circuit protection is rated at more than 20 A, use only protected
    socket-outlets, with, as far as is practicable, discrimination between the
    protective devices for the circuit and the protective devices associated with
    the socket-outlets. The protective device of a protected socket-outlet shall,


    Sent from my SM-N960F using Tapatalk
    The way I understand it ... if you use a breaker bigger than 20 amp ... for example you can use a 25 amp breaker for 2.5 mm wire (commonly use din aircon installations) ... however you would then need to have overload protection at the socket outlet.
    Comments are based on opinion...not always facts....that's why people use an alias.

  10. #10
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    771
    Thanks
    121
    Thanked 35 Times in 34 Posts
    Ahhhh yes ok... more than.... with you now.
    Should have read it slower the first time hahaha. Makes sense as they say like max for a 2.5 is a 20A breaker.

    Sent from my SM-N960F using Tapatalk

Page 1 of 2 12 LastLast

Similar Threads

  1. Plugs having something in common.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 26-Sep-21, 05:52 AM
  2. Blank Code and Group code does not exist
    By Helizel in forum Accounting Forum
    Replies: 3
    Last Post: 19-Jun-20, 10:56 PM
  3. Not so common Quotes
    By adrianh in forum General Chat Forum
    Replies: 4
    Last Post: 03-Feb-20, 08:42 AM
  4. Replies: 0
    Last Post: 18-Aug-17, 10:40 AM
  5. Replies: 3
    Last Post: 09-Jan-15, 08:33 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •