    Good day, i got called out to a victron installation with the following happening:

    The main switch of the home is a three phase earth leakage. the input to the inverter is on the line side of the earth leakage which is correct. the output side feeds to a sub main switch with an earth leakage feeding the plugs in the property as per regulations. but when the Grid goes down and switches to the inverter, the three phase earth leakage trips out and has to be switched on again by hand. There is a surge protections device installed on the AC side of the inverter and the PV panels also has an earth that is connected to the same surge AC surge protection device as no DC surge protection was installed. when i disconnect the earth from the solar panels, the tripping problem goes away. My question is, will the installation of a DC surge protection device for the solar panels stop the earth leakage from tripping or not? as the DC earth and AC earth still has to be bonded together anyway?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    You say the inverter is on the line side of the ELU which also acts as the main switch .

    If that is so , than how do you drop power to the inverter ?

    Trying to understand the set up

  3. #3
    Bronze Member
    Join Date
    Mar 2013
    Location
    Cape Town
    Posts
    111
    Thanks
    0
    Thanked 0 Times in 0 Posts
    they have a separate 63A single pole C/B installed near the inverter feeding the inverter input along with the changeover switch and output C/B. the remaining two phases that is not on inverter backup supplies the stove, geysers etc.

    I recon there should might be a voltage on the panels between + and earth which can be traced but if its something in the settings of the Victron, then ill have to walk away unless there are any other suggestions i can look at? i doubt that it can be cause of no DC surge protection as the DC earth and AC earth is all bonded together anyway

  4. #4
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Quote Originally Posted by Pieter00 View Post
    There is a surge protections device installed on the AC side of the inverter and the PV panels also has an earth that is connected to the same surge AC surge protection device as no DC surge protection was installed. when i disconnect the earth from the solar panels, the tripping problem goes away. My question is, will the installation of a DC surge protection device for the solar panels stop the earth leakage from tripping or not? as the DC earth and AC earth still has to be bonded together anyway?
    Where is the Earth to the PV panels physically connected to?
    The frame, or to one of the PV panel wires (Positive or Negative)?

    Alternatively there is water somewhere along the PV wires, maybe a disconnect box, or a junction box. If this is the case then itcould be dangerous, firstly electric shock, secondly an arc may arise from the DC and cause a fire.

    Check this site for more
    Solar fires – DC arc faults
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  5. #5
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Hello

    I do not know Victrons inverters.

    But its a premium inveter so my guess is that it would internally switch and join the inverters output N to the E as to bond it.

    So when it goes into Islanding mode the output N and E are bonded. But when the grid is on then that bond is broken.

    So I feel that may be a cause of the tripping is that switching.

    So my remededy or attempted remededy would be to chnage the ELU. To get the client to now pay for a 3phase ELU as a "lets see if this works" is another issue.

    If it always worked before and only now giving issues then I do believe a ELU change is in order. Also if it is a CBI one I am reading and catching wind of them failing or become too sensitive from all the load shedding.

    Anyway if you so find the answer please do let us know.

    Now this is a total guess but perhaps if there is a new applience plugged in that may have electronics in, the capacitors and chokes and all may push the ELU over when there is a switch with leading, lagging of currents and dips.



    Sent from my SM-N960F using Tapatalk

  6. #6
    Bronze Member
    Join Date
    Mar 2013
    Location
    Cape Town
    Posts
    111
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Alright this was kinda interesting. apart from the solar installation, the client also has a backup system for his geyser with a pc board in the db allowing the sun to heat up the water and if it's inadequate to reach the required temperature, it also takes from the grid the power it requires and it also has a bypass circuit breaker. when i bypass this pc board and switch off the grid to the home, the inverter changes over fine and nothing trips but when the pc board is not on bypass and i switch off the grid, it trips out the main switch which is the 3 phase earth leakage. So he is getting the guys out that did the geyser installation and he was so happy that he now wants 3 solar quotes on 3 of his 10 game farms urgently whoop whoop!

  7. #7
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Thats brilliant! Congrats on those opportunities to quote!

    Also thanks for the feedback! Intresting and well found on that issue !

    Something to keep a note on for future.

    Sent from my SM-N960F using Tapatalk

  8. #8
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Quote Originally Posted by Pieter00 View Post
    the client also has a backup system for his geyser with a pc board in the db allowing the sun to heat up the water and if it's inadequate to reach the required temperature, it also takes from the grid the power it requires and it also has a bypass circuit breaker.
    What make and model?
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

Similar Threads

  1. [Question] Can an Earth leakage be used as a main switch ?
    By Steven@platinum.co.za in forum Electrical Contracting Industry Forum
    Replies: 25
    Last Post: 15-Oct-21, 08:52 AM
  2. Earth leakage tripping with no load ?
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 26
    Last Post: 21-Oct-20, 07:16 PM
  3. earth leakage tripping issue
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 16-Jan-19, 12:13 PM
  4. [Question] Circuit breaker /Main switch / Earth Leakage identifcation
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 25-May-16, 10:10 PM
  5. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •