Page 2 of 2 FirstFirst 12
Results 11 to 15 of 15

Thread: RCD and AFDD

  1. #11
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Quote Originally Posted by Derlyn View Post
    With a suicide cord, the earth leakage does not work and all other plugs on the same circuit as the one you are backfeeding into, have no protection.

    Not a healthy situation.

    Peace out .. Derek
    Agreed, I personally will not recommend or even use this type of connection. Some people who do not understand the implications love to live dangerously
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  2. #12
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Dont get me wrong ... I am not saying that it is a good practise (suicide cord) ...

    What makes a suicide cord so dangerous so that we can understand why people shouldnt use it even if it is recommended by generator suppliers as a quick easy fix.

    I am trying understand how a hybrid inverter works ... current flow to the inverter and back into the essential supply or grid.

    How the current flow affects the operation of the protective devices.

    The type of RCD which should be used for a specific application like and inverter.

    If AFDD with built in RCD might be a better option or not.
    Comments are based on opinion...not always facts....that's why people use an alias.

  3. #13
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    By the way I dont need to know that the plug has exposed conductors or if you dont switch off the main breaker its feeds back in the grid ... creating a dangerous environment ...

    what I am interested to know is the affect it has on the operation of the safety devices.
    Comments are based on opinion...not always facts....that's why people use an alias.

  4. #14
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    @Ians

    I always see an invertor as a supply, the same as the Supply Authority or a generator.

    If the invertor or generator is connected in parallel with the supply from the supply authority, then it has no effect on the safety devices of the installation.

    The devices dont know if they are being fed by the Supply Authority, a generator or an invertor. They just see a supply.

    Peace out .. Derek

  5. #15
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Being AC, it does not know the direction of current flow, so if it exceeds the rating, it will trip. DC on the other hand has a polarity not because of the current direction, but the direction does affect which side the spark shroud is on. On the wrong side, it catches fire.

    In Hybrid systems, there is a CT which measures the load current, and a CT which measures the supply current. It then subtracts the one from the other, and knows the amount of current the loads are drawing before the inverter. It then starts applying the feed back to the grid side, until the mount becomes zero(if there is sufficient PV power to do so).
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za