    Quote Originally Posted by ians View Post
    A lot of information to process in a weekend ... one thing for sure is the sans 10142 is lacking information ... fortunately getting hands on all the other drafts in the pipe line it will assist to guide me into the new year.

    Anyone have a list of the latest standards required for solar installations.

    SANS 10142-1 (ed 3.01)

    NRS 097-2-1-2017 (which ones are relevant ... I see there are a few)
    Hi

    SANS have published SANS 10142-1-2
    The wiring of premises
    Part 1-2: Additional special requirements for
    low voltage small scale embedded generator
    installations connected to THE GRID
    This document was approved for publication in November 2021.

    The scope of the document appears to contradict itself.


    1 Scope
    1.1 This standard covers special requirements in addition to SANS 10142-1 for electrical installation
    of Small Scale Embedded Generators (SSEGs) rated up to 1 000 kVA intended to supply all or part
    of an installation with nominal voltages not exceeding 1 kV AC or 1,5 kV DC.
    1.2 This document is applicable to SSEG installations intended to be connected in parallel to an
    electrical supply grid or electrical supply authority.
    1.3 This document also applies to the installation of the following:
    a) Solar PV installations;
    b) Energy storage systems;
    c) Inverter-based generation;
    d) Synchronous generators;
    e) Asynchronous/induction generators; and
    f) Any combination of the above that are connected to a single point of supply.
    NOTE 1 In this standard, the terms Small Scale Embedded Generator (SSEG) and Embedded Generator (EG)
    are used interchangeably.
    NOTE 2 Embedded generation is also known as Grid tied generation.
    1.4 This part of SANS 10142 does not apply to
    a) all alternative supplies e.g. Solar PV systems, wind turbines which is covered in 7.12 of
    SANS 10142-1: 2021, and
    b) stand-alone electrical generating systems.


  2. #22
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    I found this draft ... has this been published ?

    https://arepenergy.co.za/wp-content/...R-01102018.pdf
    Comments are based on opinion...not always facts....that's why people use an alias.

  3. #23
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Ya i am confused now, is it published or draft ? but also thanks for sharing and sparking more on this convo



    Sent from my SM-N960F using Tapatalk

  4. #24
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    It does contradict itself, says applies to solar pv then last paragraph states it does not apply... they setting them selves up for another 1000 bucks on Amendemmt 1....

    We get dragged by the heals in court and clients when get something wrong yet they release a document with more questions than answers ...

    Side note I have not been dragged but many an electrician has been brought over the coals when shit hits the fan but our "law book" can have errors....

    Sent from my SM-N960F using Tapatalk

  5. #25
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,262
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Quote Originally Posted by ians View Post
    I found this draft ... has this been published ?

    https://arepenergy.co.za/wp-content/...R-01102018.pdf
    The code has been published but it is quite a bit different to the draft.

  6. #26
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,262
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Quote Originally Posted by GCE View Post
    Hi

    SANS have published SANS 10142-1-2
    The wiring of premises
    Part 1-2: Additional special requirements for
    low voltage small scale embedded generator
    installations connected to THE GRID
    This document was approved for publication in November 2021.

    The scope of the document appears to contradict itself.


    1 Scope
    1.1 This standard covers special requirements in addition to SANS 10142-1 for electrical installation
    of Small Scale Embedded Generators (SSEGs) rated up to 1 000 kVA intended to supply all or part
    of an installation with nominal voltages not exceeding 1 kV AC or 1,5 kV DC.
    1.2 This document is applicable to SSEG installations intended to be connected in parallel to an
    electrical supply grid or electrical supply authority.
    1.3 This document also applies to the installation of the following:
    a) Solar PV installations;
    b) Energy storage systems;
    c) Inverter-based generation;
    d) Synchronous generators;
    e) Asynchronous/induction generators; and
    f) Any combination of the above that are connected to a single point of supply.
    NOTE 1 In this standard, the terms Small Scale Embedded Generator (SSEG) and Embedded Generator (EG)
    are used interchangeably.
    NOTE 2 Embedded generation is also known as Grid tied generation.
    1.4 This part of SANS 10142 does not apply to
    a) all alternative supplies e.g. Solar PV systems, wind turbines which is covered in 7.12 of
    SANS 10142-1: 2021, and
    b) stand-alone electrical generating systems.

    Just been having the discussion on what is covered by what. I originally thought a contradiction, but it has been pointed out that SANS10142-1 excludes alternative supply operating in parallel with the main supply to an installation.( 7.12.1.1 note 2 )

    Sans 10142-1-2 is for systems running in parallel , typical gridtie systems or running generators in sync with supply

  7. Thank given for this post:

    Dylboy (09-Dec-21), ians (09-Dec-21)

  8. #27
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Ahhh I see GCE, thank you for this.

    I feel now not much of great use as I do backup and no grid syncing. However may still be a good read as in the future PV systems can backfeed once all that is ironed out and I understand the process.

    so on the Christmas wishlist then haha.

    Sent from my SM-N960F using Tapatalk

  9. #28
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,262
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Quote Originally Posted by GCE View Post
    Hi

    SANS have published SANS 10142-1-2
    The wiring of premises
    Part 1-2: Additional special requirements for
    low voltage small scale embedded generator
    installations connected to THE GRID
    This document was approved for publication in November 2021.

    1 Scope
    1.1 This standard covers special requirements in addition to SANS 10142-1 for electrical installation
    of Small Scale Embedded Generators (SSEGs) rated up to 1 000 kVA intended to supply all or part
    of an installation with nominal voltages not exceeding 1 kV AC or 1,5 kV DC.
    1.2 This document is applicable to SSEG installations intended to be connected in parallel to an
    electrical supply grid or electrical supply authority.
    1.3 This document also applies to the installation of the following:
    a) Solar PV installations;
    b) Energy storage systems;
    c) Inverter-based generation;
    d) Synchronous generators;
    e) Asynchronous/induction generators; and
    f) Any combination of the above that are connected to a single point of supply.
    NOTE 1 In this standard, the terms Small Scale Embedded Generator (SSEG) and Embedded Generator (EG)
    are used interchangeably.
    NOTE 2 Embedded generation is also known as Grid tied generation.
    1.4 This part of SANS 10142 does not apply to
    a) all alternative supplies e.g. Solar PV systems, wind turbines which is covered in 7.12 of
    SANS 10142-1: 2021, and
    b) stand-alone electrical generating systems.

    It appears that the above document has now been removed from the SANS Store for purchase
    Nobody appears to have been informed that the document was going to be withdrawn , but there again , nobody was aware that it was due to be published before a final round of objections and comments were sorted out
    Will keep an eye out for further developments

  10. Thank given for this post:

    Dave A (17-Dec-21), Dylboy (15-Dec-21), ians (15-Dec-21)

Page 3 of 3 FirstFirst 123

Similar Threads

  1. When are the Grid tie Solar systems going to be allowed
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 17
    Last Post: 19-Aug-23, 09:41 AM
  2. solar systems
    By ians in forum Electrical Contracting Industry Forum
    Replies: 44
    Last Post: 11-Dec-22, 08:02 AM
  3. Inefficient solar systems
    By gombault in forum Energy and Resource Conservation Forum
    Replies: 11
    Last Post: 16-Dec-15, 06:12 AM
  4. low voltage systems and COC'S
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 29-Apr-13, 12:29 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •