    Busy planning a job for tomorrow. Surface job in a larny complex. Newly built garage.
    Was planning to use conduit and camera boxes for connections and terminations as normal, but client doesn't want conduit.
    Insists on trunking.

    Quick question. I have checked SANS , but I need a bit of confirmation. Are terminations and connections on FTE allowed to be made in trunking ?

    Peace out .. Derek

  2. #42
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Morning!

    Good question...

    I would say yes if easily accessible and maybe a note saying where it is.

    I have often seen cables extended inside a 100x40 trunking. Even in UK.

    What did SANS say ?

    Only question I guess is what manufacturer says as that may be the ultimate say.

    SANS may not know but the manufacturer should.

    Sent from my SM-N960F using Tapatalk

  3. #43
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Derlyn View Post
    Good rising.

    Busy planning a job for tomorrow. Surface job in a larny complex. Newly built garage.
    Was planning to use conduit and camera boxes for connections and terminations as normal, but client doesn't want conduit.
    Insists on trunking.

    Quick question. I have checked SANS , but I need a bit of confirmation. Are terminations and connections on FTE allowed to be made in trunking ?

    Peace out .. Derek
    A question that has no straight black and white answer but I would say not unless you use a cable coupler

    We avoid joints in trunking purely due to fault finding afterwards and most of our specs from the consultants do not allow it.
    Saying that we have had to join on long runs and have used the proper IP rated " connector " ,which has the glands on either side, to prevent strain and also in case somebody is busy with his fingers in the trunking tracing a circuit.
    5.2.1 no touching without opening with the use of a tool
    6.3.7 - joints accessible ( trunking , yes if you can find It) , protected against strain ( going to be difficult unless you use a coupler )
    6.5.1.1 k - also refers to joints not accessible even when covers are open.
    Have pasted what I perceive to be relevant regs below


    6.3.7 Joints and terminations
    6.3.7.1 Joints and terminations of cables, cores and conductors shall be
    made in accordance with manufacturers' instructions or the appropriate part
    of SANS 10198.
    Flexible cables shall only be joined using termination boxes, cable couplers or
    manufacturers’ jointing kits.
    All joints shall be accessible, protected against strain, and protected in
    accordance with 5.2.1, except for joints made and sealed permanently and
    intended to be maintenance free.
    6.3.7.2 Joints and terminations shall not
    a) adversely affect the current-carrying capacity, the insulation resist-ance or
    the earth continuity of the cable, core or conductor in which they are made,
    b) be made in any connector, bend, elbow or tee-piece of a conduit,
    c) allow the strands of a stranded conductor to spread, or
    d) require strands of a stranded conductor to be cut away to allow connection
    of the conductors (for example, to terminals).
    5.2.1 Live parts
    It shall not be possible to touch any live part within arm's reach with the
    standard test finger (see SANS 60529)
    a) during normal operation, or
    b) when a cover is removed, unless the cover is removed with the use of a
    tool or a key.

    6.5 Wireways
    6.5.1 General
    6.5.1.1 When a wireway is installed

    k) where it is accessible to the public, protection shall be such that it is not
    possible to touch any live parts with either the standard jointed test finger
    or the 2,5 mm diameter 100 mm long rod (see SANS 60529). This
    protection also applies after opening any door or cover that can be opened
    without the use of a tool or key; and


  4. #44
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    With regards to using cabtyre in electrical installations ... I have found on many occasions that people use a 3 core cabtyre to connect a PEC ... the brown/ live ... blue/neutral and the yellow/green as the return live.

    Then you get the twin specialists red/live ... black /neutral and bare earth sleeved with a red or colour sleeve ... In fact recently I called out an inspector who had signed off and installation in a fast food outlet ... the earth wire was used as the return to the lights ... he seemed to feel he had done nothing wrong ... thats wher ethe fight started ... the wire was a twin 2.5 mm connected to a 16 amp breaker ... so he felt that the reduced wire sized was protected from overload ... but I pointed out the the earth only had one layer of protection.

    not keeping up to date with the regs for so long ... maybe things have changed and you can now use the earth as a return ... nothing surprises me anymore.


    6.3.3.2 The means of identification for an a.c. circuit may be by colours or by
    numbers, as follows:
    a) where colours are used
    1) a neutral conductor shall be identified by black only,
    2) an earth continuity conductor shall be identified by the bi-colour
    green/yellow only, or by being bare. Green/yellow insulated conductors
    shall NOT be used as live conductors under any circumstances,
    Comments are based on opinion...not always facts....that's why people use an alias.

  5. #45
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    With regards to joints in trunking ... I recalled being called out for condemning a project which had joints in every part of the trunking ... it was pointed out to me that if only a percentage of the trunking is used as a wireway .. IE 25 % full ... joints were allowed in the trunking ... that where the fight started ... you couldnt fit the cover on the trunking it was so full ... his argument was that when he did the joints the trunking was half empty.
    Last edited by ians; 15-Dec-21 at 12:37 PM.
    Comments are based on opinion...not always facts....that's why people use an alias.

  6. #46
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    404
    Thanks
    25
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by ians View Post
    If anything the regs are more relaxed ... so you might get into trouble for telling a customer they cant use cabtyre to wire their entire house ... or get confused about whether or not you have to install a double pole isolator for a ceiling fan or just put everything on earth leakage ... really dangerous stuff.
    "wire a house in cabtyre", really?

    Sent from my SM-A705FN using Tapatalk
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  7. #47
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Leecatt View Post
    "wire a house in cabtyre", really?

    Sent from my SM-A705FN using Tapatalk
    Yip ... read all the comments ... and the new regs ... it seems the SANS regs have evolved due to low cost housing and ready boards.
    Comments are based on opinion...not always facts....that's why people use an alias.

  8. #48
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    My advice would be to pass the FTE ... secure the 2 pieces with a cable tie or 2 (strain relief) fold it back and use my favourite cheapest joint ... the pipe with the 2 glands (protection from the test finger) if you have space ...

    Anyone recognise this ... looks just like something posted on this forum a while back ... at least now we have a standard to refer to when doing the coupling joint

    https://www.mce.co.za/#!itemdetails/...2Dffc60bcc91de


    or ferrules and silicon filled heat shrink ... FTE secured with cable ties.

    or if the budget allows https://www.mce.co.za/#!itemdetails/...2Dde778df52724

    just remember you cant run the power and camera cabling in the same trunking.
    Comments are based on opinion...not always facts....that's why people use an alias.

  9. #49
    New Member
    Join Date
    Feb 2022
    Location
    Somewhere
    Posts
    1
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Anyone to share the latest SANS document perhaps?

  10. #50
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,708
    Thanks
    127
    Thanked 160 Times in 150 Posts
    On top of each page is printed in red ( must be important ) This standard is exclusively for ECA.

    What does that mean ?


    On the bottom of each page, also in red, it says .. Photocopying or reproducing this standard constitutes a violation of SABS Copyright Rules.

    Does that mean that copying and pasting sections for discussion here on this forum is not permitted ?

Page 5 of 6 FirstFirst ... 3456 LastLast

Similar Threads

  1. SANS 10142-1 (ed3)
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 23-Apr-21, 06:29 AM
  2. SANS 10142-1:2017 (Ed. 2.00)
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 27
    Last Post: 23-Oct-18, 06:56 AM
  3. SANS 10142 Edition 2
    By Karel Kriel in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 02-Jul-17, 08:20 AM
  4. sans 10142-1:2012
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 23-Apr-13, 05:56 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •