8.6.2 Continuity of bonding
Confirm the continuity of the bonding conductors between all exposed
conductive parts within arms reach (or see annex A) of each other. When a
test device or instrument is used, it shall have a supply that has a no‐load d.c.
or a.c. voltage of 4 V to 24 V, and a current of at least 0,2 A. In each case, the
resistance shall not exceed 0,2 Ω. Amdt 1