    Quote Originally Posted by Dylboy View Post
    They say the N and E shall (i think its a shall)be joined on the supplier side only so if that's the case for not perm joining the inveter output N to E I think they must rethink or at least I must be taught why it must be so.



    Sent from my SM-N960F using Tapatalk
    Basically ,only the supplier may earth the neutral - You can become the supplier on the load side of a generator or inverter .

    6.1.6 The neutral conductor shall not be connected direct to earth or to the
    earth continuity conductor on the load side of the point of control except as
    allowed in 7.16.4.


    You will see that this is also stipulated in municipal bylaws and Eskom bylaws since the day dot.

    The reason behind the reg is to prevent fires and I will take an extreme case as an example.

    My house is fed from the municipal cable network and I take 80 Amp single phase supply.The neutral is earthed at the substation transformer, 800KVA
    If I then install an inverter and bridge my inverter neutral to earth with a 6sqmm or 4sqmm wire as the inverter is only 1KVA, and that inverter neutral is direct connection to municipal neutral.

    If for some reason the municipal earthed/neutral comes loose or is stolen my house neutral/earth now becomes the earth/neutral for the 800KVA transformer and all imbalanced load will flow through my 16sqmm mains cable and then through my 4sqmm neutral to my inverter which is earthed
    That 4sqmm wire could be in my roof space , overheat due to the current flow and cause a fire .
    That earth neutral current flow could be as high as 200Amp on an imbalanced load.

    That is the though process for that particular regulation

  2. Thanks given for this post:

    Dylboy (04-Dec-21)

  3. #2
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    777
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Quote Originally Posted by GCE View Post
    Basically ,only the supplier may earth the neutral - You can become the supplier on the load side of a generator or inverter .

    6.1.6 The neutral conductor shall not be connected direct to earth or to the
    earth continuity conductor on the load side of the point of control except as
    allowed in 7.16.4.


    You will see that this is also stipulated in municipal bylaws and Eskom bylaws since the day dot.

    The reason behind the reg is to prevent fires and I will take an extreme case as an example.

    My house is fed from the municipal cable network and I take 80 Amp single phase supply.The neutral is earthed at the substation transformer, 800KVA
    If I then install an inverter and bridge my inverter neutral to earth with a 6sqmm or 4sqmm wire as the inverter is only 1KVA, and that inverter neutral is direct connection to municipal neutral.

    If for some reason the municipal earthed/neutral comes loose or is stolen my house neutral/earth now becomes the earth/neutral for the 800KVA transformer and all imbalanced load will flow through my 16sqmm mains cable and then through my 4sqmm neutral to my inverter which is earthed
    That 4sqmm wire could be in my roof space , overheat due to the current flow and cause a fire .
    That earth neutral current flow could be as high as 200Amp on an imbalanced load.

    That is the though process for that particular regulation
    That makes all the sense! Thank you for taking the time to explain! I should have thought of the PEN fault. I really appreciate it !

    Sent from my SM-N960F using Tapatalk

Similar Threads

  1. Fuel supplies.
    By JohnW1234 in forum South African Politics Forum
    Replies: 6
    Last Post: 23-Dec-21, 10:45 AM
  2. COC including supplies from UPS
    By RegElec in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 11-Nov-21, 06:26 AM
  3. alternate supplies
    By ians in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 31-Jul-20, 12:29 PM
  4. Multiple supplies in one building
    By ians in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 24-Jul-19, 11:50 AM
  5. KA testing on UPS Supplies
    By RegElec in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 22-Jul-14, 06:33 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •