    Load shedding from 12pm - 2 pm ... my earth leakage unit tripped again ... went and had a look at the recorder ... let me put it to you like this ... best you check your insurance is going to pay for damages to electronic equipment.

    You need to install surge protection ... a trip connect ... a surge arrestor at each plug point ... a contactor with a delay timer and every other protective device that you can think of ... yes it is that bad.

    It seems the grid cant handle the load switching ... I am sure eskom have installed relay which switch off the power first them energise the new area being powered ... it looks to me like the grid cant handle the switching .. .what they should have in place is a ripple relay system like they did in the old days ... it was mounted inside every ones DB.
    Comments are based on opinion...not always facts....that's why people use an alias.

  2. #32
    Diamond Member
    Join Date
    Mar 2010
    Location
    Cape Town
    Posts
    6,328
    Thanks
    426
    Thanked 977 Times in 794 Posts
    Can't you just install a device to delay the Mains reconnect for a couple of minutes?

  3. #33
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    I changed the settings to dips and swells ... 939 events recorded so far ... all dips ... as low as 151 VAC

    I have been putting some thought into this problem...

    I am at the end of the line (last house on the feed)

    load shedding kicks in ... power switches off .. .the ripple runs down the line and I collect it.

    The power switches on ... the arc on the contact on the load shedding relay as it flashes trying to make contact ... once again a ripple effect down the line.

    But now we have detected a new problem ... voltage dips ... 939 dips recorded since I switched settings on the PQA ... the lights flicker every time I switch on an appliance ... what I think has happened ... there is now a loose connection at the pole or further up stream caused by the load shedding off and on.

    If I look at the trend ... the problem started as the the power switched on after the last stage of load shedding ... it got really bad at 7 pm last night ...dropping as low as 151 VAC for a period of time.

    since then all night you can see the random dips ... destroying my electronic devices.
    Comments are based on opinion...not always facts....that's why people use an alias.

  4. #34
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    I decided to go check the power line feeding my house with the thermal camera ... imagine that a hot spot on the neutral wire ... it looks like a bad connection on the airdac connector.
    Comments are based on opinion...not always facts....that's why people use an alias.

  5. #35
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,497
    Thanks
    138
    Thanked 696 Times in 594 Posts
    Blog Entries
    1
    Could also be a damaged/pitted contact on the supply switching circuit breakers
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  6. #36
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Sine wave is not flat topping anymore ... no more flickering lights ... no more transients on the wave form ... no more tripping earth leakage.

    The electricity department arrived today while I was on site ... wife showed him where the hot spot was ... cut back the wire and replaced the fuse.

    My concern is why is it the fuse and wiring keep burning ... this is not the first time the fuse and wiring has been repaired.

    Besides replacing the fuse and tails ... the light supply cable on the pole burnt off and landed on the the steel arm ... and we all know what happened.
    Comments are based on opinion...not always facts....that's why people use an alias.

  7. #37
    New Member
    Join Date
    Nov 2021
    Location
    SOUTH HILLS JOHANNESBURG
    Posts
    4
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Earth Leakage trips everytime loadshedding ends

    What the second electrician recommanded is the only way to solve your issue. Remember we do have flow of current in small amount even if line power is switched off. Elevated voltages contribute to that as well even some times loose connections on your nuetral lines.My suggestions.

  8. #38
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,304
    Thanks
    36
    Thanked 314 Times in 263 Posts
    Quote Originally Posted by ians View Post

    My concern is why is it the fuse and wiring keep burning ... this is not the first time the fuse and wiring has been repaired.

    Besides replacing the fuse and tails ... the light supply cable on the pole burnt off and landed on the the steel arm ... and we all know what happened.
    Overhead lines are generally aluminum conductors along with aluminum clamps , they use copper wiring directly onto the aluminum instead of using a copper to aluminum lug - There is a reaction between the 2 materials which causes that corrosion and loose connection

  9. #39
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by GCE View Post
    Overhead lines are generally aluminum conductors along with aluminum clamps , they use copper wiring directly onto the aluminum instead of using a copper to aluminum lug - There is a reaction between the 2 materials which causes that corrosion and loose connection
    They use a clamp to hook the copper tail to the ally bundle conductor ... its not a direct connection. The thermal image I took indicated a bad connection at the connector. Maybe they put it on the wrong way.

    The fluke is still recording double figure transients and some really distorted the wave forms.

    The earth leakage has stopped tripping.

    It's time to do a loop impedance test back to the transformer.
    Comments are based on opinion...not always facts....that's why people use an alias.

  10. #40
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    398
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Returning to the original question, my customer had a CBI Earth leakage 3ka which was found to be off whenever the loadshedding finished. I've replaced it with a ACDC 6ka unit and the problem has gone away. Been 3 weeks now.

    Sent from my SM-A705FN using Tapatalk
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

Page 4 of 5 FirstFirst ... 2345 LastLast

Similar Threads

  1. Earth leakage unit trips at 15mA
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 12-May-17, 01:45 PM
  2. Earth Leakage
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 10-May-16, 10:11 PM
  3. Earth leakage trips then stops.
    By Boeriemore in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 21-Dec-13, 04:08 PM
  4. Earth leakage trips when it's raining - pool pump unit the cause.
    By Boeriemore in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 29-Nov-13, 04:25 PM
  5. Earth leakage trips at night??
    By Jongseun in forum Electrical Contracting Industry Forum
    Replies: 18
    Last Post: 18-Jun-12, 10:47 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •