I have made this mistake of installing these 3.5 kva inverters with 2 x 100 amp/hr batteries (gel/deep cycle/ AGM). I also work on sites where these 3.5 kva systems have been installed.
I have installed (some longer than 5 years) and currently maintain a bunch of 5 kva axpert type inverters with FLA batteries, we use them in factories to support the IT systems during load shedding and at the customers personal properties.
I have also installed a few bi directional/hybrid systems with lithium batteries.
What have I learnt:
It pays to install a bidirectional/hybrid inverter with lithium batteries and solar panels.
What are the challenges I face with the 3.5 kva 2 battery.
The first complaint is "all that money I spent" ( yet its the cheapest option on the market). You get a 3.5 kw system and it should produce 3.5 kw, well that's where the fight starts.
When load shedding kicks in a 10 pm and your system is pulling 2 kw, it will literally switch off in a couple minutes if you are lucky. Yes you can add batteries @R2500 a pop, taking into consideration that you will be required to add 2 at a time thats now R5000, plus the cabling and sparkie to link them.
Then you add a new challenge overload protection and switch disconnectors, most companies who install these little units dont even consider a DC switch disconnect.
In most cases these "small" systems are installed inside the property, now you have a pile of batteries to consider the safety, with a gas that is released during the charging process, which is not even considered with only 2 batteries, now suddenly becomes a consideration, especial if installed in a confined space. You cant just install an extractor fan because it is a highly flammable gas.
In many cases the installer doesnt split the DB or run dedicated UPS plugs and thats where the fight really gets momentum.
Then there is that little extra (sometime more than expected) added to the bill at the end the month, that wasnt there before the "backup" system was installed. the inverter requires standby power to function, the batteries need power to recharge, so now you have to consider losses and efficiencies. Like leaving all your appliances and TV's chargers for phones, gate batteries, alarm batteries etc etc etc, it all starts adding up, multiple that by 30 days then by 12 months, suddenly those silly amounts become a consideration.