    Socket Outlets Wiring

    Can someone please help me with the requirements in South Africa for correct wiring of Socket Outlets and Lighting Circuits.

    Are we supposed to use the British Closed Ring Circuit wiring for sockets Ring Open Circuit or allowed to use other methods?

    E.g. A star configuration, where one central feed for the circuit comes from the DB CB to a junction box in the ceiling and a separate cable runs from there to each socket?

    Or one central feed for the circuit comes from the DB CB and goes along the ceiling, then via multiple junction boxes gets spliced to each socket outlet?

    Are there any other restriction, than not exceeding 5kW on each socket circuit?


    What are the requirements and standards for for Lighting Circuits as well?



    The is tons of information on the net for the other countries but very little regarding the latest SA standards.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    South African standards are based on the IEC
    If you are looking for the standards it is SANS 10142-1 and the latest being edition3 and can be bought on the SABS web store

    All the methods you described above would be acceptable subject to the regulations

  3. #3
    New Member
    Join Date
    Sep 2021
    Location
    Johannesburg
    Posts
    4
    Thanks
    0
    Thanked 1 Time in 1 Post
    Quote Originally Posted by GCE View Post
    South African standards are based on the IEC
    If you are looking for the standards it is SANS 10142-1 and the latest being edition3 and can be bought on the SABS web store

    All the methods you described above would be acceptable subject to the regulations

    I have looked through SANS 10142-1 but I haven't seen anywhere a required method for wiring of plug sockets described. Hence I started this thread. SA complies to IEC standards but that is a very broad term. UK, Germany and France, all compy to IEC standard but all 3 have different methods of wiring for plug sockets.

    So, if all methods described before are acceptable in SA, is there preferred vs non-preferred methods and the reasons for that?

  4. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    I cannot remember every coming across a ring circuit in an installation.

    Some contractors like wiring to a joint box in the roof and then dropping down to each point and the reason is normally to save the cost of the wiring vs a loop in system where you will need to wire down and up the wall.

    To me the loop in system is easier to maintain and fault find -

    Most specifications done by electrical consultants will insist on a loop in system.

  5. #5
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    A loop system also manages the currents flowing in the wire. It is like doubling the copper area.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  6. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,945
    Thanks
    582
    Thanked 938 Times in 759 Posts
    You almost never come across ring final circuits in SA although they're not forbidden. Usually in a domestic installation you'll find straight 20Amp radial socket circuits and 10A or 15A straight radial light circuits with the supply run to each switch and out to the next switch (sometimes called the 2-plate method).
    _______________________________________________

    _______________________________________________

Similar Threads

  1. SANS 163-2 Socket Outlets
    By RegElec in forum Electrical Contracting Industry Forum
    Replies: 14
    Last Post: 13-Jan-20, 07:26 PM
  2. Schneider Electric socket Outlets ST2015WE
    By SiyaM in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 23-Jul-18, 09:50 AM
  3. switched socket outlets or not!
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 18-Aug-16, 11:16 PM
  4. Hobby wiring: Wiring requirements for a DCC railway layout
    By icrob in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 23-Jul-16, 05:29 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •