    Semiconductor tabs are isolated from the heat sink, which is earthed with a membrane for isolation.
    These membranes are rated at 4KV, depending on their thickness.

    There is no reason that there could be an iron filling trapped between the membrane and the semiconductor, which in time can pierce the membrane and cause a path way to earth.
    There is also no reason that could protect an arc between the mounting screw, or tab to earth due to a surge, which then punctures the membrane and create a path to earth.
    Now the devices are switching a DC source to create AC, but there is nothing to stop the arc from continuing on the DC side and creating havoc.

    Of course what I have explained above is exceptional cases, which I have experienced before, but is protection not there for the exceptional cases for additional protection to users?

    Your call.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  2. #2
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    I Found this in a document from Victron.

    "To safeguard against this issue, it is recommended to use long AC, cables of similar length. Always follow the
    recommended cable lengths and thicknesses as listed in the product manual. Do not increase the cross-section
    of the AC cabling more than is recommended in the manual!"


    "AC fusing parallel strings
    For units in parallel it is advised to use one AC fuse for all units on that phase. Both on the input, and on the
    output. Multiple fuses which are mechanically connected are okay to be used, this is counted as one fuse"
    Comments are based on opinion...not always facts....that's why people use an alias.

Similar Threads

  1. Inverters
    By ians in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 27-Jan-21, 05:55 PM
  2. 10mm SWA n parallel as sub main?
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 03-May-18, 10:44 AM
  3. Inverters
    By Sparks in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 15-Jul-15, 06:42 AM
  4. Looking for someone who knows about Inverters
    By HR Solutions in forum Local Ads on TFSA
    Replies: 0
    Last Post: 21-Jan-15, 12:55 PM
  5. Inverters
    By HR Solutions in forum General Chat Forum
    Replies: 33
    Last Post: 11-Dec-14, 01:55 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •