    Oil filled paper insulated cable

    Morning

    Has anyone experience with the old (1950's) oil filled paper insulated cables.

    A client is redoing a block of flats in stages. He has been told that the main panel is the biggest issue (I disagree but there you go)

    Oil filled cables was long before my time. I know they are used in HV but thats not my area. Is it possible to reterminate these things in the short term.

    The oil has started to leak from some points which i guess means the effectiveness of the insulation is reduced.

    I have suggested we replace them first but someone higher up the food chain (AIA inspector) said the panel is a biggewr problem (it is a big problem but feels like putting cart before the horse)

    He will have to replace them but wants the panel done first.

    Any advice/direction/suggestions appreciated.

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,817
    Thanks
    561
    Thanked 912 Times in 737 Posts
    I wish I could say they're long before my time as well but I was taught how to do wiped lead joints on air and oil pressurised cables as an apprentice. It was a skill I never had a use for in later working life because they were already being replaced with newer generation cables.

    Is the cable a pressurised oil fill or is it just oil impregnated? What material is the outer sheath of the cable? Can you maybe post a few pics of the cable breakout and terminations?

    If it's a pressurised oil cable then leaks won't necessarily mean IR values will be compromised. At the origin of the cable there will be a pressurised oil supply and usually an alarm system that would alert if the pressure or oil reservior level became too low. Even with unpressurised oil impregnated cables the insulation would only usually be problematic if there were underground oil leaks that subsuquently suffered prolonged soaking by water or flooding.

    Oil and paper insulated cables were used across all applications from ELV up to HV. Retermination could be possible but it would require finding someone with appropriate experience and tools.
    _______________________________________________

    _______________________________________________

  3. #3
    Silver Member
    Join Date
    Mar 2008
    Posts
    258
    Thanks
    5
    Thanked 44 Times in 37 Posts
    Hi Andy

    They are not pressurised cables. We manage dto convince teh client just to change.
    If you are going to spend big bucks on a panel why would you keep old cable which may of may not survice the moving/retermination process.

    After doing another site visit the ammount of other problems is 'impressive'

    VIR cable on the risers and the people who worked on the many DB boards really had no idea what they were doing.

    Found a DB board in the downstair kids school with 4 VIR socket circuits jammed into one breaker, no earth leakage and to top it off they used 1.5mm as the bridging cable.

    Think he's going to have to pretty much redo the whole building eventually. It hasn't got much left to give.

Similar Threads

  1. UIF FORM U-19 FILLED OUT BY EX-EMPLOYERS
    By Taitai in forum Labour Relations and Legislation Forum
    Replies: 7
    Last Post: 16-Dec-20, 12:10 PM
  2. COC filled in example
    By ELECT 1 in forum Electrical Contracting Industry Forum
    Replies: 29
    Last Post: 03-May-18, 08:09 AM
  3. [Question] Correspondence Paper 1 and 2
    By PaulG in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 15-Jun-14, 10:15 AM
  4. Paper 1 & 2 in JHB south???
    By IP4X in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 19-Apr-13, 02:32 PM
  5. [Article] Exe cable glands for braided cable
    By Master Electrician in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 26-Aug-10, 02:47 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •