    Here is the table from the regs for single core PVC insulated wires. The table seems to be for longer runs of wire since the installation methods listed are all about how the wires are fixed. But I'm assuming that the "direct clipped" method in the table will suffice as a worst-case scenario compared to how they are installed in a DB board. According to the table then, 10mm2 should be able to carry 65A in a single-phase installation?

    Click image for larger version. 

Name:	sans.jpg 
Views:	13067 
Size:	62.6 KB 
ID:	8131
    The length or the run becomes a problem because of volt-drop. Yes, if the cable doesn't enter conduit anywhere along its run then and no there derating factors are applicable then a 10mm cable will suffice for a 65A load.
    _______________________________________________

    _______________________________________________

  2. #2
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by AndyD View Post
    The length or the run becomes a problem because of volt-drop. Yes, if the cable doesn't enter conduit anywhere along its run then and no there derating factors are applicable then a 10mm cable will suffice for a 65A load.
    Talking about derating ... I had to do the calculations for an 800 amp supply ... 150 metres long ... everything was on track until the cables got to the underground duct ... that 30 m piece in the ducts makes a huge difference to the cable calculation.
    Comments are based on opinion...not always facts....that's why people use an alias.

  3. #3
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Since back when we didnt even have TV's ( a flippen long time ago)

    I would use the general rule for wire size

    1.5 mm - 10amps
    2.5 mm - 20 amps
    4 mm - 30 amps
    6 mm -40 amps
    10 mm - 50 amps
    16 mm - 60 amps
    25 mm - 80 amps
    35 mm 100 amps

    I dont know of any issues ... i am still doing work for customers since tha 90's

    I have identified more issues (thermal) with loose connections and and dogdey equipment than under rated wire size ... make no mistake i do have find issue with under size wiring ... in fact today ... the aircon which was relocated last week ... the wire size is only 1.5 mm between the indoor unit and compressor ... it is showing signs of over heating ... by discolouring on the copper core and the plastic is not as felxible and the sheat is difficult to remove ... I will create a report and email it to the customer.
    Comments are based on opinion...not always facts....that's why people use an alias.

  4. #4
    Full Member
    Join Date
    Nov 2019
    Location
    Sa
    Posts
    32
    Thanks
    6
    Thanked 2 Times in 2 Posts
    Interesting questions, am I aloud to use silicone insulated wire or panel flex in a db? Some people reckon than you only allowed to us gp wire.

  5. #5
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Frans400 View Post
    Interesting questions, am I aloud to use silicone insulated wire or panel flex in a db? Some people reckon than you only allowed to us gp wire.
    I dont see why you cant use panel flex (so long as it is rated for the the voltage).

    There is some confusion with flexible cables ... panel flex ... welding cable ... automotive cable ... its all about the rating (voltage) some cables are only insulated for up to 50 V other cables up to 1000 V and higher.

    YOu can use flexible cables for just about anything so long as it is correctly rated for the applications ... you can wire inside the DB to motors/ pumps / controls ... you can even use flexible busbars.

    Maybe one of the smart fellas could do a write up expalining the difference.
    Comments are based on opinion...not always facts....that's why people use an alias.

  6. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,945
    Thanks
    582
    Thanked 938 Times in 759 Posts
    Quote Originally Posted by Frans400 View Post
    Interesting questions, am I aloud to use silicone insulated wire or panel flex in a db? Some people reckon than you only allowed to us gp wire.
    Not sure why you'd want to use silicone insulated wire, it would work out expensive and is unnecessary from a temperature rating point of view...

    The regs mention the voltage rating of the insulation must be higher than any voltage found in the DB, they don't specify it must be PVC as far as I know.

    The problem with using silicone wire or any panelflex type wire would be that it's fine stranded conductors which may be against the manufacturers instructions for the types of wire the circuit breaker cage clamp terminations or the neutral bar screw terminations are suitable for....although using it in conjunction with bootlace ferrules may be acceptable.
    _______________________________________________

    _______________________________________________

  7. #7
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,706
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Click image for larger version. 

Name:	20210605_090451.jpg 
Views:	615 
Size:	24.7 KB 
ID:	8226

    Ok, so I measured the cross sectional area of the commercially available busbars pictured above.

    On the left is for dinrail. Top section between breakers 7mm sq.
    Pins going down into breakers 4mm sq.

    On the right is for samite. Top section between breakers 18mm sq.
    Pins going down into breakers 10mm sq.

    So from the above, as far as dinrail is concerned, It seems as if self made bridges using 6mm sq house wire will do a better job than the commercially available buzbar, I also know that if a product has been especially designed for a certain purpose, then it should be used.

    What sayeth the other toppies ?

    Peace out ... Derek

Page 2 of 2 FirstFirst 12

Similar Threads

  1. 3 wire transformer
    By ians in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 15-Oct-20, 11:14 AM
  2. Wire size
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 28-Feb-20, 12:54 PM
  3. GP wire
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 26-May-17, 05:10 AM
  4. No earth wire!
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 27
    Last Post: 02-Jan-16, 08:47 PM
  5. How's this for size?
    By greasemonkey in forum Labour Relations and Legislation Forum
    Replies: 3
    Last Post: 03-Mar-14, 12:37 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •