    Wiring my grid-tie inverter into the DB

    Hi Guys

    I need some advice from you guys about the proper way to install my 2.5kW Solis single phase grid-tie inverter into my DB board. As per the manual, the inverter should be connected in parallel with the mains (before the earth leakage) and through a disconnecting device and preferably current limit to 15A.

    Click image for larger version. 

Name:	image.png.7f3a436f0c4c3e890a6c78f964c89865.jpg 
Views:	1459 
Size:	38.9 KB 
ID:	8003

    Attached is a photo of my current DB, but I've drawn it as a diagram as well (it's a small townhouse so it's a tiny DB and all circuits are protected by EL, including the geyser).
    Click image for larger version. 

Name:	image.thumb.png.15ae1194fd860b4fba94a17d96daaa1d (1).jpg 
Views:	2348 
Size:	39.2 KB 
ID:	8004 Click image for larger version. 

Name:	dbphoto.jpg 
Views:	4471 
Size:	74.6 KB 
ID:	8006

    Is my understanding correct:

    - Label existing half of DB "GRID" and label new breaker(s) with "Alternate Supply"
    - Add a new mains-rated breaker (63A 2P). 10mm2 Neutral and Live tapped from Earth Leakage input. Label "Alternate Supply"
    - Add new 16A MCB. 10mm2 live tapped from new 63A breaker bottom. Label "Inverter"
    - Connect inverter using live from bottom of new 16 MCB. Neutral from neutral bar. Earth from earth bar. Surfix with 2.5mm2 conductors.
    - CT Clamp in seperate conduit to DB clamped around live from prepaid meter before mains breaker.

    Here is the diagram of what I mean:
    Click image for larger version. 

Name:	dbnew.jpg 
Views:	2011 
Size:	37.5 KB 
ID:	8005

    Lastly, instead of using both a isolator and MCB, can I use just a 16A double-pole MCB to function as over-current and isolator (the poles connected being live and neutral)?

  2. #2
    Junior Member
    Join Date
    Dec 2020
    Location
    Cape Town
    Posts
    12
    Thanks
    0
    Thanked 0 Times in 0 Posts
    1. Treat the installation exactly like any other fixed appliance installation.
    2. A licensed electrician should install.
    3. You can use a 16A double pole to break the live and neutral.
    4. Note that the disconnect must be within the 1.5m distance from the device or the switch must have a lock-out. (see SANS 10142-1 6.16.1.4)
    5. Appropriate registration for an Small Scale Embedded System might need to be done with your local municipality. And the municipality might require a Pro/Eng to sign off, etc.

Similar Threads

  1. Hobby wiring: Wiring requirements for a DCC railway layout
    By icrob in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 23-Jul-16, 05:29 PM
  2. wiring an inverter to DB
    By cje in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 11-Jul-15, 09:09 AM
  3. [Question] CoC for off-grid & gri-tie PV Systems
    By CollenD in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 22-Jul-14, 02:33 PM
  4. Selling back to the grid?
    By duncan drennan in forum Electrical Load Shedding Forum
    Replies: 11
    Last Post: 20-Feb-08, 10:57 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •