    Hi guy's
    I am in desperate need of some logic to my problem.

    We are using 95mm Wesbraid soft jumpers, from the one panel jumping across the room to another panel VIA a open cable tray, the jumpers are about 6 metres long, we have two of these jumpers in parallel for each phase.

    Now for my problem.
    The RED PHASE each jumper is carrying 250 Amps.
    The WHITE PHASE each jumper is carrying 250 Amps.
    The BLUE PHASE NOW THERE'S MY ISSUE,
    The one jumper is carrying 500 Amps.
    The other jumper is carrying sometimes 1 Amp,
    Sometimes 5 Amp and sometimes 125 Amp,
    Never more than that.

    We looked and the lug to see for over heating and NO the insulation tape still intact.
    We followed the jumper mm by mm to for burning and still intact.

    The jumpers are same length.

    Unfortunately the is a hospital and it's on the ESSENTIAL supply we have taken infrared scans and it is alarming we have on that STUBBY over 110 degrees.

    We are making plans with new jumpers to replace the overheated one and the one that's giving us this issue.

    IF ANYBODY OUT THAT MIGHT AN EXPLANATION IT WOULD BE GREAT.

    THANKS
    FRENCHIE

  2. #2
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Do the jumpers go through individual metal holes or do they all go through the same hole?

    Measure the voltage between the top terminal of the blue phase and the bottom terminal of the blue phase on main switch and circuit breaker in that circuit...and test the voltage on the other phases ...to check if it is the same.
    Comments are based on opinion...not always facts....that's why people use an alias.

  3. #3
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,488
    Thanks
    137
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    It sounds to me that there is a break in the cable, or one of the terminals not crimped properly, or the Busbar or bolt or.... something is mechanically wrong.
    Swapping the physical positions of the terminations on one side then do a current measurement. If the reading changes then the cable is at fault, if the same position cable shoes the low reading then it is the point of termination that is the issue.

    Some pictures of the connection & terminations will help to see if there is anything visual that may be picked up.

    Only way to find out is to remove the said cable and to do a visual check.
    Unfortunately once it is out of circuit, you may not detect the break with using a simple resistance tester, and may require a destructive removal of the plastic of the cable and inspect to see where the break is.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  4. #4
    Full Member
    Join Date
    Nov 2019
    Location
    Alberton
    Posts
    67
    Thanks
    2
    Thanked 4 Times in 4 Posts
    That sounds like a bad crimped lug, if the copper wire is not making good contact with the lug it could give up and down readings as it heats and cools. Or the bolt are not tight. Thats my guess.

  5. #5
    Junior Member
    Join Date
    Jul 2019
    Location
    Margate KZN
    Posts
    19
    Thanks
    0
    Thanked 2 Times in 1 Post
    Thanks Justloadit & Rifrug.
    But Ian yes they are going through individual holes with plastic glands on a aluminium gland plate, and when you said that I must check across the main switch, which because the cables being in parallel I wouldn't get a different reading, but then I realised why there is no sign of a burning faulty crimped plug, is if you agree with me and would be the answer of my problem, is that you take a bus-bar which has a 1000amp going through it and you take a 1.5mm wire from the beginning of the bus-bar and you try and flash to the other end of the bus-bar it will not flash because the current is already going through the bus-bar and not through the 1.5mm wire, if what I am saying makes sense, please tell me what you think.
    Eish sorry for the late call, this issue has had us spinning that we couldn't see any evidence of the fault.

  6. #6
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,662
    Thanks
    3,307
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    To find the point of resistance in the faulty jumper using infrared scanning, you are going to have to disconnect the good jumper (the one that is taking the 500 amps). Obviously this will need some thought on how to load the faulty jumper without causing knock-on effects...

    Without current, the point of resistance isn't going to generate enough energy to show up.

  7. #7
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    The first thing you must do is get rid of the aluminum gland plate...and replace it with a non metalic plate.

    I do the main switch/circuit breaker test to check for bad connections inside the units... when i do thermal inspections and i dont find issues with the actual lug or terminations the next step is to do a voltage test ...i normally compare the reading top to bottom (line to load)...of each phase... and if 2 are 0.54 volts and 1 is 15 volts... i know straight away that the switch is faulty and there is an internal bad connection...or a problem with a point to point cable.

    You can make a up a long tail and do the test at various point in the panel and between panel to pin point bad connections...the beuty about this kind of test ...it can be done without switching off the power.
    Comments are based on opinion...not always facts....that's why people use an alias.

  8. #8
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,262
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Aluminum gland plate is fine as it is non magnetic material and you will not get a heat build up due to eddie currents
    Only happens on magnetic material

  9. #9
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    not being an electrical engineer ...when we start getting into this complex stuff... like eddy currents going around the cable and heat build up due to hysteresis ...circulating current along the cable being compounded by harmonics ...cable configurations and earth separation ...draining ... and all that stuff... personally i have only used bakelite to terminate large single core cables... never even considered aluminum.

    It will be interesting to hear the outcome of this issue.
    Comments are based on opinion...not always facts....that's why people use an alias.

  10. #10
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,262
    Thanks
    34
    Thanked 305 Times in 259 Posts
    We use aluminium especially on the larger generators - You are generally bringing in 120sqmm armour cable ECC which tends to crack Bakelite when there is a bit of movement and at the same time you are bringing in single cores from the alternator. With aluminium you still have earth continuity and a solid base to gland to and the single cores can go through separately without the eddy current problems.

Page 1 of 2 12 LastLast

Similar Threads

  1. Motor running unbalanced amps
    By Ivanjvv in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 26-Feb-19, 10:58 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •