    Quote Originally Posted by Dave A View Post
    We have a situation - an indoor jacuzzi has a distribution board above it (see the photo).

    Click image for larger version. 

Name:	db above jacuzzi.jpg 
Views:	473 
Size:	40.1 KB 
ID:	7807

    Can the db be there?
    Hi Dave

    Couldn't give a quick answer but after checking the regs and for Ian's entertainment, I found the following.

    Firstly, I think we can agree that the jacuzzi is what is referred to in the regulations as a spa.

    The room that the jacuzzi is situated in, is a bathroom according to the definition.
    Definition 3.6 Bathroom ... a room that contains a bath, shower or spa.

    The regulations for a bathroom thus apply.

    Table 7.1 shows that distribution boards are only allowed outside zone 3.

    The DB board in the photo is in zone 1, so it is illegal and must be moved.


    Cheers and peace out ... Derek


    Added this morning .....

    Reg 7.1.4.3.6

    If a distribution board is installed in a room that contains a fixed bath or shower, it shall be outside zone 3 AND the enclosure shall have a degree of protection of IPX5.
    Last edited by Derlyn; 22-Feb-20 at 06:38 AM.

  2. Thanks given for this post:

    Dave A (23-Feb-20)

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •