    The earth leakage trips when test button is pressed. The earth leakage tester is plugged on the socket outlet and the 3 LED indicators light up to show that the connections are OK, but when the knob is turned to 30mA, the earth leakage does not trip.
    Can someone explain what could be the problem here?

  2. #2
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    398
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Your earth leakage tester is faulty?

    Sent from my SM-A705FN using Tapatalk
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  3. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,932
    Thanks
    578
    Thanked 936 Times in 757 Posts
    High earth impedance at the socket maybe?

    Those plug in socket testers are notoriously misleading and inaccurate unless you buy an advanced one like this. http://www.socketandsee.co.uk/socket...et-tester.html
    _______________________________________________

    _______________________________________________

  4. #4
    New Member
    Join Date
    Jan 2019
    Location
    Centurion
    Posts
    9
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Thanks guys, I think a different type of EL tester would be a good idea.
    It just that I have been using it all the time and I have never had any problems with it.

  5. #5
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,573
    Thanks
    111
    Thanked 149 Times in 141 Posts
    Check your supply voltage.

    If you are using a Top Tronic TEL1TLB tester, it will not trip the earth leakage relay if the supply voltage is less than 213 volts.

    Have you checked that the socket outlet has actually been wired through the earth leakage ?


    Derek

  6. #6
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts
    Greetings

    Is that circuit wired through the earth leakage?

  7. #7
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    398
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by SeanM View Post
    Greetings

    Is that circuit wired through the earth leakage?
    Very good point

    Sent from my SM-A705FN using Tapatalk
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  8. #8
    New Member
    Join Date
    Jan 2019
    Location
    Centurion
    Posts
    9
    Thanks
    0
    Thanked 0 Times in 0 Posts
    The supply voltage is healthy, measured value is 236V and the earth leakage has been used as a main switch. All the circuits are connected with the earth leakage from one neutral bar.

  9. #9
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Plug in the earth leakage tester...you said all 3 lights are on... now switch off the earth leakage unit and see if the 3 lights on the plug tester switch off... they should go off... if not you have a wring problem.

    Test the voltage:

    live - neutral = 236 v
    live to earth = should be the same (236 v) or about 1-2 volt different
    earth - neutral = should be around less than 5 volts

    do a loop impedance test at the socket outlet ...if the the result is within the required limit ...the plug is wired to the earth leakage unit then ...replace the earth leakage unit.

  10. #10
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,573
    Thanks
    111
    Thanked 149 Times in 141 Posts
    Quote Originally Posted by Philani View Post
    The supply voltage is healthy, measured value is 236V and the earth leakage has been used as a main switch. All the circuits are connected with the earth leakage from one neutral bar.
    Easy.

    Try another tester. If it works, replace the tester.

    If same problem, replace the earth leakage relay.

    Process of elimination with only 2 possible outcomes ( all others have already been eliminated )

    Derek

Page 1 of 2 12 LastLast

Similar Threads

  1. How to isolate an earth leakage problem
    By ians in forum Electrical Contracting Industry Forum
    Replies: 45
    Last Post: 23-Jun-17, 10:53 AM
  2. Earth Leakage
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 10-May-16, 10:11 PM
  3. [Question] Earth Leakage problem has experts stumped
    By Alistair Jones in forum Electrical Contracting Industry Forum
    Replies: 24
    Last Post: 25-Feb-14, 11:38 AM
  4. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM
  5. Random earth leakage problem
    By BillH in forum Electrical Contracting Industry Forum
    Replies: 39
    Last Post: 23-Jan-12, 09:37 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •