Results 1 to 6 of 6
Thread: When does a Geyser become a Boiler
    Had an interesting question that has me thinking, trying to decide which way is correct.
    On a hostel type environment they have installed a central hot water system with a +/- 500L tank with 3 phase elements in it.
    The consultants are calling it a boiler and saying that it does not need to be on earth leakage unit.
    If they call it a Boiler it may not need an earth leakage at 30mA but it will need a Adit relay.
    The question I am asking is , when does a Geyser become a Boiler according to SANS 10142-1
    Anybody come across the dilemma ?
    New Member MrZakeQina's Avatar
    Jul 2017
    Pretoria
    What's an Adit relay first of all? This is interesting indeed
    Sent from my SM-A305F using Tapatalk
    6.16.2 Water heaters
    NOTE Water heaters include geysers, instantaneous water heaters including units
    for boiling water, heat pumps, solar systems, induction water heaters and the like (see
    also 6.16.1). electrode water heaters, steam generators and boilers are not included
    (refer to 6.16.7)
    From an engineering perspective, the objective of a boiler is to bring the liquid to boiling point...
    A geyser surely is supposed to stop heating well short of boiling point.
    BTW - there's a typo. It should be Electrode (capital E) as it is the first word in the sentence.
    planet earth
    (refer to 6.16.7)
    you must luv reading my posts
    You're not SANAS
    Been meaning to come back and post the findings on the original question I posed
    According to the regulations - "Pressure Equipment Regulations of 15 July 2009 " The description pasted below is excluded from the pressure regulation .
    2(3h) fixed electrical hot-water storage container of water capacity
    from 15 litres to 450 litres operating at a maximum pressure of
    600 kPa manufactured to the requirements of SANS 151, which
    shall be installed in accordance with the requirements of SANS
    10254
    If your consultant decides that his so called boiler falls outside of the above scope and therefore does not need earth leakage unit then he will need to comply to the balance of the Pressure regulations and have the unit registered with the DOL and have the unit pressure tested and inspected on a regular basis , every 36 months. The unit will still need to comply with SANS 10142-1 and have a Earth leakage relay at 10% of rated current.
    Would think it is more cost effective in the short and long run to call it a geyser and be finished with it.
    Dave A (19-Dec-19)
  1. Geyser trips when hot
    Last Post: 05-Aug-21, 02:52 PM
  2. Geyser not heating
    By Bonga Mkhize in forum General Chat Forum
    Last Post: 23-Oct-17, 11:01 PM
  3. Solar Geyser COC
    By julianzimzeni in forum General Regulatory Compliance Forum
    Last Post: 10-Feb-17, 11:52 AM
  4. [Question] Switching off geyser
    By IanF in forum Electrical Load Shedding Forum
    Last Post: 16-Sep-16, 11:12 AM
  5. [Question] Hi Plz help - how do I turn off my Geyser?
    By Poor Student in forum Electrical Contracting Industry Forum
    Last Post: 10-Dec-14, 02:26 PM