    Hi GCE.
    Spoken to GE technician today and this is what he had to say.
    He has commissioned the UPS but warned us that we have a floating neutral but that it will not affect their equipment.

    Now the issue is that the client is a bit confused who is right or wrong.

    We are concerned that we have a floating neutral and that we must sorted it out.
    We have done all our test and per the sans they are all perfect reading.
    But saying that GE technician insists that we have very earth, we did loop impedance test and according to our calculations the earth is fantastic, the other thing is that he does a resistance test and reading fluctuate from 0.5 Ohms to 1.3 Ohms continuously and he maintains that that the reading what ever it is should be stable and not erratic, as we said to him our sans doesn't require us to do that test as our voltage neutral to earth is 0.125 Volt and we far below 25 Volt dangerous level and 50 Volt we disconnect the installation.

    But he still maintains that we have bad earth
    We have done our earth continuity test from the mini sub through the MLVP to the MRI isolator which feeds the UPS and its 0.01 Omh with a 100 Meters of 16mm PVC wire.

    Now we get from the 315KVA mini sub earth bar to the ground earth test 6 Ohms, GE say that we must have 0.00 Ohms.

    We have request that a GE fully pledged electrical guy comes to retest the system, as we are not really satisfied with the previous guy demands.

    Do you perhaps think that maybe that we are not being compliant with our 6 Ohms at the transformer earth.

    We have always been under the impression that 0 Ohms to 10 Ohms unless the Engineers requests a special earth requirement of 0 or 1 Ohms.
    Thanks
    FRENCHIE

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Hi Frenchie

    SANS 10142-2 , asks for an earth resistant reading of less then 1 ohm on a mini sub.So the GE tech could be right that his earth is not sufficient .Have pasted reg below

    6.2 Installation of a neutral earth and bonding
    6.2.1 The earth electrode shall be installed as close as possible to the transformer and shall have
    an earth resistance not exceeding 1 Ω.
    6.2.2 The transformer tank shall be bonded to the earth stud and to the substation earth bar.
    6.2.3 The LV neutral of a transformer shall be bonded to the earth stud.
    6.2.4 The earth stud shall be connected to the earth electrode.
    6.2.5 All bonding and earthing conductors shall be of cross-sectional area at least 70 mm2 copper
    or equivalent, unless it can be shown by calculation that a smaller cross-sectional area will suffice.
    6.2.6 Earthing terminations shall be installed individually and in such a way that they can easily be
    accessed and disconnected for routine earth testing.
    6.2.7 The neutral earth resistance shall not exceed 1 Ω.

Similar Threads

  1. [Question] Neutral split
    By Hotspot in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 19-Nov-22, 06:12 PM
  2. attachment point for neutral
    By Canuck in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 19-Aug-19, 05:35 PM
  3. Voltage between Neutral and Earth - When is it a fault?
    By Justloadit in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 20-Jul-19, 09:23 PM
  4. Neutral leaking 220V to Earth
    By Etienne Swanepoel in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 19-Oct-14, 07:37 PM
  5. 3 core cable running 2 phases and neutral is OK?
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 09-Jan-12, 07:44 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •