Page 2 of 2 FirstFirst 12
Results 11 to 15 of 15

Thread: Power surges and insurance

  1. #11
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by adrianh View Post
    Very nice - R2k isn't bad considering the protection that it offers.

    As an aside - but along similar lines. I have a nice big UPS on my PC. It works really well and it kicks in every time I forget to buy electricity :-)
    but... I have found a really interesting thing with the UPS - When the compressor starts the UPS kicks in. The compressor is of course on a different circuit in the garage and the PC is in the office. I never realized that those motors create such a huge spike that goes all over the house. I really wonder whether equipment doesn't get damaged due to those sort of spikes. Let's say by chance the compressor and the vacuum cleaner are turned on simultaneously - won't the effect be really really bad?
    Old compressor aircon units are also bad news...your lights would dim... it causes a volt drop not a surge in power...they suck electricity.

    We had an incident where every morning a 5 am the entire factory would "blink" causing all the VSD's to reset and a whole lot of other issues...the operators would have to go around and restart everything...it turns out there was a huge compressor which switched on/off causing this "blink" i got to site at 3 am...setup the recorder and waited...at 5 am on the dot ...there was the glitch on the screen ...and you heard the machine all go down.

    As soon as you start adding Aircons...pool pumps...a Jacuzzi...etc etc ...a little more consideration should be taken into the electrical installation...in most cases people dont even consider equipment installed in a domestic installation...everything is considered as general...2.5 for plugs...1.5 for lights etc etc

    Something to consider ...using a VSD to either soften the startup current or to fit a 3 phase motor (not sure if you already have a 3 phase compressor) i have a few customers who have down scaled and moved back home...unfortunately they have 3 phase equipment and only single phase power at home... simple... just use a 230 single phase to 400 3 phase inverter...way cheaper than upgrading to 3 phase power.

  2. #12
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,927
    Thanks
    577
    Thanked 936 Times in 757 Posts
    Quote Originally Posted by adrianh View Post
    ... I have found a really interesting thing with the UPS - When the compressor starts the UPS kicks in. The compressor is of course on a different circuit in the garage and the PC is in the office. I never realized that those motors create such a huge spike that goes all over the house. I really wonder whether equipment doesn't get damaged due to those sort of spikes. Let's say by chance the compressor and the vacuum cleaner are turned on simultaneously - won't the effect be really really bad?
    As a rule of thumb most single phase motors that are direct-on-line will draw about 5x their run current for a very short period of time on start-up. This would include fridge, vacuum cleaner, air-con, irrigation/borehole/pool pump etc.
    The large current draw causes the voltage to drop significantly and not just on that circuit. Your UPS is probably detecting this voltage dip and jumping into battery mode. These voltage dips can cause all sorts of operational issues and reliability issues for electronics.
    The high start current only usually lasts for a few miliseconds so the chances of two motors starting simultaneously is very small in a domestic environment. If it did happen the voltage sag would be more pronounced. Unfortunately under-voltage protection relays don't help with this issue, they're more effective at protection against longer duration low-voltage events. Good practice final-circuit design helps also load balancing if you have a 3-phase supply.
    _______________________________________________

    _______________________________________________

  3. #13
    Diamond Member
    Join Date
    Mar 2010
    Location
    Cape Town
    Posts
    6,328
    Thanks
    426
    Thanked 977 Times in 794 Posts
    Quote Originally Posted by AndyD View Post
    As a rule of thumb most single phase motors that are direct-on-line will draw about 5x their run current for a very short period of time on start-up. This would include fridge, vacuum cleaner, air-con, irrigation/borehole/pool pump etc.
    The large current draw causes the voltage to drop significantly and not just on that circuit. Your UPS is probably detecting this voltage dip and jumping into battery mode. These voltage dips can cause all sorts of operational issues and reliability issues for electronics.
    The high start current only usually lasts for a few miliseconds so the chances of two motors starting simultaneously is very small in a domestic environment. If it did happen the voltage sag would be more pronounced. Unfortunately under-voltage protection relays don't help with this issue, they're more effective at protection against longer duration low-voltage events. Good practice final-circuit design helps also load balancing if you have a 3-phase supply.
    Ahhh OK, so it is the voltage drop that causes the problem.

  4. #14
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by adrianh View Post
    Ahhh OK, so it is the voltage drop that causes the problem.
    I would suggest you do a few calculation and check cable sizes etc...incoming voltage...mains connections etc...my compressor was blinking the lights in workshop...it turns out the fuse on the pole outside my property had a bad connection.

    Even with a single phase motor starting...it shouldnt cause your UPS to switch(depending on the unit it should switch at around 180 volts ...if you have 230 volts (the standard in SA) that would mean it is a 50 volt drop...i would be scratching around for loose connections...looking at cable sizing...cable lengths...loop and line impedance tests at the compressor isolator ...etc etc.

  5. #15
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,495
    Thanks
    138
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    I have 2 few products which address this issue with respect to Surges.
    One can not ever guarantee that after installation there will be no failures.
    One of the characteristics of surge arresters that they fail after a number of accumulative surges.
    In other words when a surge occurs, the surge material cause a short circuit over a certain voltage, if the surge was of sufficient energy which the surge arrester can handle, only a partial part of the arrester is damaged, and is disconnected from the terminals by nature of the surge arrester material. Enough of these surges, and the arrester will no longer operate and fails completely.
    In the case that there is too much energy, then the surge arrester material basically fails as a short circuit and hopefully the circuit breaker trips.

    However with respect to SANAS, the surge arrester once failed, must be removed from the circuit to prevent fires after the surge arrester material has become a short circuit, and sufficient current can flow with out tripping, but could cause fire. So to fall into line, ther is a special thermal fuse that is installed in a number of surge arrester types, which once the material reaches 110Degrees, the thermal fuse will pop, and remove the surge arrester device from the circuit.

    Taking advantage of this factor, LEDs can be placed which light up when the surge arrester is operatinal, and once the fuse pops and the surge arrester is no longer protecting the site, the LED is extinguished.

    This is the reason that you must check your surge arresters regularly or after a storm or supply issues to see if the LED is on, and replace immediately to maintain protection.

    Another interesting fact is that the more arresters are placed on the mains lines, the better the lines will be protected, with out damage to the surge arresters, as each arrester will absorb a portion of the surge, thereby reducing the amount of heat the surge arrester handels.

    In this case the more the merrier.

    My 3P5W Surge protection, has an added feature/option, in which the Earth to Neutral voltage is measured, and if it exceeds a preset value, then it will disconnect the contactor supplying the load.
    Attached Files Attached Files
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

Page 2 of 2 FirstFirst 12

Similar Threads

  1. 700 Volt surges reported from a commercial site
    By Cracker in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 12-Feb-19, 11:20 AM
  2. [Question] Business insurance or Commercial Insurance?
    By SilverNodashi in forum General Business Forum
    Replies: 2
    Last Post: 16-May-17, 01:04 PM
  3. POWER SURGES
    By Phil Cooper in forum General Chat Forum
    Replies: 4
    Last Post: 02-Sep-13, 11:25 AM
  4. power surge insurance
    By murdock in forum General Business Forum
    Replies: 1
    Last Post: 13-Dec-10, 12:06 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •