    Morning all

    I had a fault last week where the earth leakage tripped intermittently, so I arrived tested the earth leakage and tripped at 16ma. This is low so before changing I continued to test and found that the customers motor had condensation on the terminals. Dried out and all ok.

    I then proceeded to changed the earth leakage as I would like it to trip between 20-25ma and to my surprise any earth leakage I tried still tripped at 16ma.

    Any ideas the reason for this?

  2. #2
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Quote Originally Posted by SeanM View Post
    Morning all

    I had a fault last week where the earth leakage tripped intermittently, so I arrived tested the earth leakage and tripped at 16ma. This is low so before changing I continued to test and found that the customers motor had condensation on the terminals. Dried out and all ok.

    I then proceeded to changed the earth leakage as I would like it to trip between 20-25ma and to my surprise any earth leakage I tried still tripped at 16ma.

    Any ideas the reason for this?
    Maybe the measurement instrument is faulty or has a flat battery?
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  3. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Can also be that there are various loads plugged in and leaking slightly to earth , like 4 to 9 ma leaking.
    Your tester is then just adding to the leakage and the unit only needs another 16ma to trip

    If you connected the tester directly to the earth leakage without any other load you may find it then trips at 20-25ma.

  4. #4
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Spend the money and buy a leakage current clamp meter....they cost around 5 k ..best money other than my fluke 1653 i have ever spent.

    I was called in by a company to do power quality checks where a company had done a new installation...there were 12 transformers feeding the building (big industrial site in Newcastle)...as they pressed the start button every leakage current detector tripped...a room full of engineers and electrical contractors couldnt figue out why ...i connected my fluke 435 to one of the panels ...I personally didnt think it was the VSD's causing the problem...however they were paying me to do a power quality check...I took out my leakage current clamp and put it on the earth conductor...imagine that...readings indicated that there was a bad earth...i climbed under the building and checked the earth grid...it had been stolen...replaced the earth grid and all the bonding and bingo...problem solved.

    The tester can be used to identify which wire and circuit is the problem without pumping a 500 volts into the electrical installation using an insulation resistance tester... we all know what happens if you dont disconnect and remove sensitive electronic equipment.

  5. #5
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts
    Greetings All

    Thank you for the comments at least I know I haven't lost the plot.

Similar Threads

  1. Earth Leakage Breaker (RCD) Tripping
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 14-Jul-23, 02:53 PM
  2. earth leakage tripping issue
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 16-Jan-19, 12:13 PM
  3. [Question] If my geyser is tripping the earth leakage do I speak to a sparky or plumber
    By FEB in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 15-Jun-16, 08:46 AM
  4. Earth leakage tripping when plug in snake rack
    By MattyN in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 22-Aug-15, 09:29 AM
  5. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •