Results 1 to 2 of 2
Thread: inverter installation for Load Shedding
Threaded View
    Email problem Tonye's Avatar
    Mar 2015
    Pretoria
    Inverter installation.
    This installation was designed for a 4,5 hr load shedding period with an average 1kW load
    and based on a 85% inverter efficiency & a 50% depth of discharge on the batteries.
    http://www.prellexpower.co.za/images...tions/mark.jpg
    Option 1 400 battery cycle life at 50% DOD (the one that was installed)
    4KVA 3.2Kw PSS low frequency 48v inverter (weight 53kg & capable of handling high inrush currents)
    8x 110 A/H deep cycle batteries (weighing in at 240 Kg)
    400 cycle life @ 50% DOD
    (Total weight of Inverter, Batteries & cabinet @ 300kg)
    Total cost including installation R46000.
    Option 2 (Solar ready) 5000 battery cycle life at 50% DOD
    5KVA 5Kw Axpert 48v Inverter with built-in MPPT solar charge controller (weight 13.5kg)
    10 KWh Freedom Lite 48v Lithium iron phosphate battery bank. (weight 104 kg)
    (programmable for a 5000 cycle life @ 50% DOD or 3500 cycle life @ 70% DOD
    (Total weight of Inverter & battery bank @ 117.5kg)
    Total cost including installation +- R113000
    (the Lithium iron phosphate batteries are available up to a 2500 KWh battery bank @ R10 Mil)
    Mockup of what the two installations would look like.
    http://www.prellexpower.co.za/images...ark_axpert.JPG
    The inverter feeds a 3 phase DB (with single phase loads) via a 4 pole changeover switch
    Certain loads need to be turned off prior change over to avoid unnessary tripping (All items marked in red)
    Gas geysers will be installed shortly, so that leaves only the underfloor heating (which are permanently turned off), the Jacuzzi, Stove/Oven (Hob is gas) & the swimming pool.
    The upside is that the whole house is powered on inverter mode and have the convenience of turning lights & appliances on in every room in the house.
    (within in the load capacity of the inverter)
    UPS's will be installed in the study & lounge to keep mission critical items on prior the changeover.
    The one concern was whether the three phase earth leakage would trip under earth fault conditions while running on the single phase inverter.
    Tripped at 20ma.
    Three ct's were added for monitoring power consumption either through grid supply or inverter supply.
    This is connected wirelessly to the router and can be monitored via the Efergy engage platform cloud server on a laptop, tablet or smart phone.
    The real time usage is updated every 6 seconds and also gives averages (daily, weekly, monthly & yearly)
    View Demo
    Will be installing an extra CT and transmitter to monitor inverter power seperatley.
    This will give more accurate readings as the grid voltage is +-240v & inverter voltage is +-230v
  1. load shedding
    By wynn in forum General Chat Forum
    Last Post: 18-Dec-14, 10:05 PM
  2. Load shedding