Originally Posted by
GCE
You get a 3 phase socket that you can clock the earth pin and thereby stop a normal 5 pin plug top from fitting - My understanding was that these sockets where for machine type equipment installations and exempt from ELU. I stand corrected
Does this help?
6.16.1.6 Where a socket-outlet in accordance with SANS 164-1, SANS 164-2, SANS 164-3, or SANS 60309-1 and SANS 60309-2 is part of the appliance (built-in), the circuit shall be protected by overcurrent and earth leakage protection (see 6.15.) Socket-outlets in accordance with SANS 164-4 shall have overcurrent protection.
The implication seems to be if the socket outlet does not comply with any of those standards, the requirement for earth leakage protection may fall away..? Perhaps under the dedicated socket outlet clauses?
The challenge is whether one falls foul of some other part of the standard.