Originally Posted by
Henthel
Plug-in circuits are not part of a CoC. I mention it on the certificate and also to the owner or new occupant.
My favourite rebuttal to that argument is the following from SANS 10124-1:
6.16.1.10 The wiring between different parts of a fixed appliance that are installed separately is part of the fixed installation, even where it is supplied from a socket-outlet, unless such wiring is less than 3 m in length.
You may have excluded all plug-in circuits from your CoC. However, that does not exclude them from the electrical installation if the regs say they are part of the electrical installation.

Originally Posted by
Henthel
However, I have found numerous garage door openers and gate motors on plug-in circuits.
Probably because of this:
6.16.5.1.4 Each motor shall be supplied by a manually operated disconnector or any other manually operated disconnecting arrangement such as a withdrawable circuit-breaker, a removable link, a fuse or by the removal of a plug from a socket-outlet, which provides at least the same isolating distance, for the sake of safety, as a disconnector that is
a) readily accessible and mounted on or next to the motor, or
b) visible from the motor, or
c) lockable in the open position, or
d) housed in a lockable enclosure other than a distribution board.