    Quote Originally Posted by GCE View Post

    7.12.2.4 Where the alternative supply is intended to provide a supply to an
    installation that is not connected to the main supply, or to provide a supply
    as a switched alternative to the main supply, the capacity and operating
    characteristics of the alternative supply shall be such that danger or damage
    to equipment does not arise after the connection or disconnection of any
    intended load as a result of the deviation of the voltage or frequency from the
    standard range. Means shall be provided to automatically disconnect such
    parts of the installation, as may be necessary if the capacity of the
    alternative supply is exceeded
    My interpretation of this regulation is the following.

    That danger or damage to equipment does not arise after the connection or disconnection of any
    intended load as a result of the deviation of the voltage or frequency from the
    standard range.


    And

    Means shall be provided to automatically disconnect such
    parts of the installation, as may be necessary if the capacity of the
    alternative supply is exceeded

    I think what they are saying here is that there needs to be overload protection for the alternate power supply
    and not automatically disconnecting of individual circuits

    The Changeover switch is 63A 4pole, adequate for Eskom supply
    Last edited by Tonye; 18-Feb-19 at 11:10 AM.

Similar Threads

  1. How to CoC a changeover switch??
    By deejaypsy in forum Electrical Contracting Industry Forum
    Replies: 39
    Last Post: 08-Mar-20, 06:02 AM
  2. Single phase generator feeding 1 phase of 3 phase db - discuss.
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 03-Jul-18, 10:06 AM
  3. [Question] Changeover switch
    By Clive287 in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 03-Nov-16, 07:00 AM
  4. Three phase to single phase generator advice needed
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 08-Apr-15, 10:12 PM
  5. [Question] Single phase and 3 phase testing course
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 26-Feb-09, 09:14 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •