Results 1 to 9 of 9

Thread: Air Conditioner connections

  1. #1
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts

    Air Conditioner connections

    Greetings

    When I did my training it was said that an air conditioner unit upto 16000 BTU can be supplied by a socket.

    I am have been asked to do the electrical for a 24000 BTU. The new air conditioners are a lot more efficient to give you an idea this 24000 BTU is a Samsung, 8 pole inverter unit and uses 8 amps for cooling and 7.7 for heating.

    I see no reason why I cant supply this unit from a socket circuit.

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,934
    Thanks
    579
    Thanked 936 Times in 757 Posts
    If it's a high-wall split or in-ceiling cassette type a/c unit I'd treat it as a fixed appliance but I'd also look towards the manufacturers installation instructions for the supply requirements.
    _______________________________________________

    _______________________________________________

  3. #3
    New Member
    Join Date
    Feb 2019
    Location
    Port Elizabeth
    Posts
    4
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Hi

    the afe way is to mount an isolator at ur unit condenser unit outside.Reason for that is that if any maintance need to be done to the unit a tech can switch it off there and no problem.To have it on a socket is not ideal as someone can be working on the unit and lets say the house owner's kids come home and the want to switch the aircon on and just plug it in.
    or at a office block normally the unit outside is far away and the office guy's just plug it in and switch it on.
    The other reason is that the normal Circuit breaker for a plug is not designed to handle the start up current of a motor.so it may pack up and then u sit with the problem.

  4. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,304
    Thanks
    36
    Thanked 314 Times in 263 Posts
    Hi

    I always prefer having a look through SANS 10142 before making assumptions

    The regulations talks in amps not BTU with regards to Aircons - Have pasted the section below and the requirement for the disconnector device. There are a couple of other references to Fix appliances and disconnection devices in the regulations but the 4 below basically cover the requirements.
    I have found that there are two points that everybody always seems to miss - It is the need to look at 6.16.5.1.4 , that if it is classed as a motor and also that even if the fixed appliance has it own disconnector it still needs another disconnector as part of the fixed installation (6.16.1.4) .

    6.16.4.1 Heating and cooling
    6.16.4.1.1 Dedicated circuits shall be provided for fixed space heating and
    cooling (air-conditioning units) that are rated at more than 16 A. There may
    be more than one unit on each circuit and the power supply to each unit shall
    be controlled by a switch-disconnector.


    6.16.1.2 The power supply to every fixed appliance, except luminaires, shall
    be supplied through
    a) a disconnecting device that disconnects both live conductors in a singlephase
    supply and all phase conductors in a multiphase supply, or
    b) a socket-outlet that is directly accessible at all times that any person is
    exposed to such appliance while the supply is on. In the case of a
    remotely installed appliance, the position of the disconnecting device
    shall be indicated by means of a notice in close proximity to or on the
    appliance.

    6.16.1.4 The disconnecting device shall be positioned
    a) within 1,5 m from the appliance, or
    b) in a distribution board (if the switch-disconnector is capable of being
    locked in the open position).
    Even where a disconnecting device is on the appliance, a separate
    disconnecting device shall be provided in the fixed installation to allow for the
    total removal of the appliance
    .


    6.16.5.1.4 Each motor shall be supplied by a manually operated
    disconnector or any other manually operated disconnecting arrangement
    such as a withdrawable circuit-breaker, a removable link, a fuse or by the
    removal of a plug from a socket-outlet, which provides at least the same
    isolating distance, for the sake of safety, as a disconnector that is
    a) readily accessible and mounted on or next to the motor, or
    b) visible from the motor, or
    c) lockable in the open position, or
    d) housed in a lockable enclosure other than a distribution board

  5. #5
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    A note with regards to Curve 1 or D curve breakers - In the past I always installed a slow curve breaker C1 or D curve...i have noticed that the new invertor A/C units make these breakers hum...I now fit a standard breaker suitably rated for the A/C unit.

  6. #6
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,497
    Thanks
    138
    Thanked 696 Times in 594 Posts
    Blog Entries
    1
    With inverters, standard circuit breakers can be used, and no need to oversize, since the inverters implement soft start which ensures that the motors are never under a high current, there by reducing the current drawn from the supply. In the case of overload of motors, the inverters are so fast, the circuit breaker does not even flinch.

    The humming of the slow curve breaker, tells me that the inverters do not have built in PFC, and hence the high impulse currents which are transmitted to the supply under operation. Strange as this is one of the main issues SABS has with certification and power factor requirement.

    The circuit breaker in this case is purely for protection in the case of a catastrophic failure.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  7. #7
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,587
    Thanks
    113
    Thanked 151 Times in 143 Posts
    Hi All

    If the supply to a split unit is outside at the compressor, through a weatherproof isolator, is it necessary to also install an isolator at the control panel inside ? or will it be sufficient to attach a notice on the control panel inside indicating the position of the isolator as per 6.16.1.3 a ?

    6.16.1.3.a

    In the case of a remotely installed appliance, the position of the disconnecting device shall be indicated by means of a notice in close proximity to or on the appliance.



    Likewise, should the supply be at the control panel inside, through a double pole isolator, can one then attach a notice on the compressor unit outside indicating the position of the isolator ? or

    Must a split unit aircon have 2 isolators ? One at the control unit inside AND one at the compressor unit outside.

    Peace out .. Derek
    Last edited by Derlyn; 17-Jun-21 at 06:05 AM.

  8. #8
    New Member Weserew's Avatar
    Join Date
    Dec 2021
    Location
    Colorado
    Posts
    2
    Thanks
    0
    Thanked 0 Times in 0 Posts
    When my air conditioner broke down, I thought there was a failure in the power grid or a sudden spike.

  9. #9
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Derlyn View Post
    Hi All

    If the supply to a split unit is outside at the compressor, through a weatherproof isolator, is it necessary to also install an isolator at the control panel inside ? or will it be sufficient to attach a notice on the control panel inside indicating the position of the isolator as per 6.16.1.3 a ?

    6.16.1.3.a

    In the case of a remotely installed appliance, the position of the disconnecting device shall be indicated by means of a notice in close proximity to or on the appliance.



    Likewise, should the supply be at the control panel inside, through a double pole isolator, can one then attach a notice on the compressor unit outside indicating the position of the isolator ? or

    Must a split unit aircon have 2 isolators ? One at the control unit inside AND one at the compressor unit outside.

    Peace out .. Derek
    Only one isolator is required ... if the unit is bigger than 12000 BTU then we always fit a weather proof isolator outside next to the unit.

    If the unit is smaller than 12000 BTU ... we fit a single socket outlet next to the indoor unit ... depending on the DB location ... especially in offices where the outdoor unit could be located in a difficult spot.
    Comments are based on opinion...not always facts....that's why people use an alias.

Similar Threads

  1. Dropped connections on Cell C
    By Dave A in forum Technology Forum
    Replies: 5
    Last Post: 30-Sep-11, 07:00 PM
  2. [Question] Connections/junctions (again)
    By Jacques#1 in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 22-Apr-10, 12:12 PM
  3. Bad internet connections kill the joy.
    By Dave A in forum General Business Forum
    Replies: 13
    Last Post: 20-Feb-07, 08:34 AM
  4. Municipal Connections
    By Alan in forum Electrical Contracting Industry Forum
    Replies: 0