    I have a customer that called as his main breaker (3 phase 45 amp) trips intermittently.

    So I went out balanced the phases and grade the circuit breakers correctly (breaker from main DB feeding sub DB was the same size as the main breaker)

    Ciruits seem clear when tested.

    I left and the same fault persists, advice please?

  2. #2
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    try a D cure or curve 1 breaker...if that doesnt work then install a PQA and see what time it trips and why it is tripping...overload or fault.

    if you dont have a PQA...then its just a guessing game.

  3. #3
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts
    Thank you

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    Is it normal domestic circuits like stove, geyser, plugs and lights?
    _______________________________________________

    _______________________________________________

  5. #5
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts
    Hi Andy

    The circuits are ups, plugs, lights and aircons. It is a shop at the Waterfront.

  6. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,946
    Thanks
    583
    Thanked 938 Times in 759 Posts
    Eek, 45A per phase isn't much if it's a commercial premises with geyser, air con, probably lots of LED lights with horiffic inrush currents and power factor and gawd knows what else they're plugging in.

    If you don't have access to a PQA or data logger you can prove whether it's a fault or a general overload condition by installing a second temporary 'main breaker' downstream from the existing one and make it a higher current rating. In this case I'd probably go with a 60A breaker but obviously whether this is a viable option or not depends on whether there's space in the DB. If the 60 Amp breaker stays up next time the power trips then it's an overload problem, if it trips simultaneously along with the 45A main breaker then there's a very good chance it's an intermittant fault either somewhere on the installation or on one of the items plugged in.
    _______________________________________________

    _______________________________________________

  7. Thanks given for this post:

    SeanM (04-Jan-19)

  8. #7
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts
    Morning Andy

    This is really good advise, I would never of thought of putting a secondary breaker in.

    An update I changed the main breaker to a 50 amp 3 phase (the main cable is a 10mm) , I am not a fan of just increasing breaker sizes.

    And to date no tripping

Similar Threads

  1. [Opinion] Cable Fault Locators
    By ACEsterhuizen in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 09-Feb-17, 07:49 AM
  2. Debt not my fault - what do I do ?
    By litepod in forum National Credit Act Forum
    Replies: 9
    Last Post: 14-Jan-12, 07:05 PM
  3. fault level
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 14-Sep-11, 02:44 PM
  4. HELP!! Who is liable for electrical fault
    By TemplerML in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 22-Jan-10, 06:54 AM
  5. It's not my fault!
    By Dave A in forum South African Politics Forum
    Replies: 3
    Last Post: 09-Dec-08, 01:43 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •