    I know this topic has been dealt with on numerous occasions but feel we need to make all aware of the regulations & dangers of connecting a VOV generator to an existing fixed electrical installation.

    As load shedding is again part of our daily lives, people are reverting to generators for backup power.
    Please be advised that most portable generators sold in SA are VOV wound and may not be connected to a fixed electrical installation.

    SANS 10142-1 states in clause 7.12.2.7 that a 230 V generator with a V-O-V earth connection (centre tap on winding which is earthed) shall
    not be connected to a fixed electrical installation. Such a generator may only be used as a free-standing unit to provide power to specific appliances
    Read more at
    http://www.prellexpower.co.za/index....er-regulations

    That been said, there are many companys connecting them with a change over switch to fixed installations.
    Should an incident occur, all involved parties will be investigated and the homeowner could attract liability if
    the installation is not safe or is not correctly used.
    It could also invalidate the insurance on the property.

    Note: Remember that any alternate power installation must be executed by a person registered with the DoL.
    The registered person must issue a CoC upon completion of the electrical installation.

  2. Thanks given for this post:

    AndyD (11-Dec-18)

  3. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,786
    Thanks
    557
    Thanked 909 Times in 734 Posts
    I think part of the problem is that it's not easy for an end user/customer to identify the winding arrangement of a generator and they're often mis-sold as being suitable for home power back-up when they're not.

    As a rule of thumb any portable contractors type generator that comes with a steel tubular frame is not suitable for wiring to a DB.


    Click image for larger version. 

Name:	Drawing1.jpg 
Views:	104 
Size:	27.3 KB 
ID:	7325
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  4. #3
    Platinum Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    2,494
    Thanks
    114
    Thanked 206 Times in 180 Posts
    Try tell the customer...like not being allowed to walk on a freeway...there are bus stops on the N2 and various other freeways/national highways...you are not going to stop it...somebody needs to come up with a solution...soon.

    The way to overcome this problem at the moment...you install the change over switch and fit a plug...it is not your problem what is connected to the plug.

Similar Threads

  1. GENERATORS?UPS?INVERTERS?
    By QUINN in forum Electrical Load Shedding Forum
    Replies: 33
    Last Post: 07-Apr-19, 08:40 PM
  2. 3 generators one supply
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 11-Jun-17, 04:03 PM
  3. standby generators
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 17-Nov-12, 09:52 PM
  4. [Question] Generators
    By g20313225 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 25-Aug-10, 09:36 PM
  5. Generators
    By Generator Man in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 26-Jun-08, 08:22 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •