    Hi All,

    Kindly see the 3 attached document, what are your thought?
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	Burners.jpg 
Views:	1795 
Size:	33.2 KB 
ID:	7269   Click image for larger version. 

Name:	Oven.jpg 
Views:	1385 
Size:	58.9 KB 
ID:	7270  
    Attached Files Attached Files

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,935
    Thanks
    582
    Thanked 937 Times in 758 Posts
    They tell you what cable is suitable although my personal preference would be H07RNF which is the uprated neoprene version. I don't see any reason not to follow their recommended size.
    _______________________________________________

    _______________________________________________

  3. #3
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    402
    Thanks
    25
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by AndyD View Post
    They tell you what cable is suitable although my personal preference would be H07RNF which is the uprated neoprene version. I don't see any reason not to follow their recommended size.
    As long as the cable is protected correctly with a 20 amp circuit breaker and not the recommended 25amp
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  4. #4
    Junior Member
    Join Date
    Jul 2015
    Location
    Durban
    Posts
    18
    Thanks
    2
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by AndyD View Post
    They tell you what cable is suitable although my personal preference would be H07RNF which is the uprated neoprene version. I don't see any reason not to follow their recommended size.
    Hi AndyD, thank you for the reply. Did you view the PDF document attached together with these 2 pictures? I would like to hear your response and view on my question and analysis respectively.

  5. #5
    Junior Member
    Join Date
    Jul 2015
    Location
    Durban
    Posts
    18
    Thanks
    2
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Leecatt View Post
    As long as the cable is protected correctly with a 20 amp circuit breaker and not the recommended 25amp
    Hi Leecatt,

    Thank you for your input on the subject matter. I assume your response is based on the burners alone, the burners when they are all operated to maximum at the same time they can draw a maximum current of 25 A. In your recommendation you recommend a 2,5mm2 Cable and a 20A C/B wouldn't this breaker trip when all the burners are turned on to maximum?

  6. #6
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    402
    Thanks
    25
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by @SamboLindoh View Post
    Hi Leecatt,

    Thank you for your input on the subject matter. I assume your response is based on the burners alone, the burners when they are all operated to maximum at the same time they can draw a maximum current of 25 A. In your recommendation you recommend a 2,5mm2 Cable and a 20A C/B wouldn't this breaker trip when all the burners are turned on to maximum?
    I am not taking the load into account at all.
    My concern is simply for the amperage in the cable. Protecting a 2.5mm cable with a 25 amp circuit breaker is incorrect. The maximum rating in the cable is 23 amps, therefore the recommendation to use a 20 amp circuit breaker to protect it.

    Sent from my SM-G570F using Tapatalk
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  7. #7
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,935
    Thanks
    582
    Thanked 937 Times in 758 Posts
    These types of trailing cables are fine stranded conductors plus the CPC is the same CSA as the line conductors and the insulation has a higher temperature rating than standard PVC so they carry a relatively higher current rating than PVC installation cables with solid conductors like flat twin. 2.5mm 3-core H07 for example is usually rated at 25Amps. Data sheet attached below, see page 4.

    I'd personally follow the manufacturers recommendations regarding cable size and overcurrent protection.

    h07rn-f-bs-en-50525-2-21-flexible-rubber-cable.pdf
    _______________________________________________

    _______________________________________________

  8. #8
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,935
    Thanks
    582
    Thanked 937 Times in 758 Posts
    The load of the stove is limited to 3.4 kw (about 15A depending on the actual voltage) at any given time. There will be a mechanism inside the stove to prevent all the elements running simultaneously.
    _______________________________________________

    _______________________________________________

  9. #9
    Junior Member
    Join Date
    Jul 2015
    Location
    Durban
    Posts
    18
    Thanks
    2
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Leecatt View Post
    I am not taking the load into account at all.
    My concern is simply for the amperage in the cable. Protecting a 2.5mm cable with a 25 amp circuit breaker is incorrect. The maximum rating in the cable is 23 amps, therefore the recommendation to use a 20 amp circuit breaker to protect it.

    Sent from my SM-G570F using Tapatalk
    Hi Leecatt,

    In my opinion I wouldn't say using a 25A circuit breaker for a 2.5mm2 cable is incorrect. The maximum protection rating for a 2.5mm2 is indeed 25A. The maximum amount of current that a cable can handle depends on various factors such as the method of installation (Pg 89), the length of the cable, the type of cable (i.e single core,multicore, PVC, armoured, unarmoured, copper,aluminum, etc) see. table 6.2(a), table 6.3(a) and table 6.4(a)....SANS 10142-1

    Please see the attached pdf document and go through the analysis of the scenario there, I would appreciate your comment on the analysis there.

  10. #10
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    402
    Thanks
    25
    Thanked 47 Times in 43 Posts
    You are correct the max rating depends upon the installation method.
    According to your diagram the cable is a 2.5mm twin core and earth and is to be installed into conduit on a wall.
    This means I have to refer to table 6.2(a), installation method 2.
    The maximum current is limited to 24 amps.
    In my world this requires a 20 amp circuit breaker for protection not a a 25 amp.




    Sent from my SM-G570F using Tapatalk
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

Page 1 of 3 123 LastLast

Similar Threads

  1. [Question] Sizing of Electrical components
    By @SamboLindoh in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 16-May-16, 12:08 PM
  2. Sizing Batteries for inverters
    By Tonye in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 24-Feb-16, 11:43 AM
  3. gas stove connection
    By ians in forum General Chat Forum
    Replies: 3
    Last Post: 09-Feb-15, 11:44 AM
  4. COC for a gas stove
    By ians in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 23-Jan-15, 01:24 AM
  5. [Article] Exe cable glands for braided cable
    By Master Electrician in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 26-Aug-10, 02:47 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •