Page 2 of 2 FirstFirst 12
Results 11 to 17 of 17

Thread: DB Height

  1. #11
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,934
    Thanks
    579
    Thanked 936 Times in 757 Posts
    I can't see from the picture, is there a main OCPD?
    _______________________________________________

    _______________________________________________

  2. #12
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by AndyD View Post
    I can't see from the picture, is there a main OCPD?
    Obsessive-compulsive personality disorder (OCPD) ...i doubt it

    An over current protective device is not required...the circuit breaker feeding this DB will be suitably rated to protect the cable feeding this DB...well it should be.

    The earth leakage device is being used as a main switch which is normal...just a pain in the butt for the tenant...having to fiddle in the dark trying to find the DB to reset it...unless they are smart like some of us and have a solar system installed with backup power and lighting.

  3. Thanks given for this post:

    Ishmaelmo (25-Oct-18)

  4. #13
    Full Member
    Join Date
    Apr 2018
    Location
    Mpumalanga
    Posts
    43
    Thanks
    14
    Thanked 1 Time in 1 Post
    Quote Originally Posted by GCE View Post
    Hi

    That would fail a COC inspection without labels ( SANS 10142-1 : 4.2 pg 61 ) and no blanks , ( readily accessible live terminals 5.2 pg 63)
    Alright! Thanks.
    I'll ask if he is aware of the labels or not. Maybe he'll bring them along when he come to issue COC.

  5. #14
    Full Member
    Join Date
    Apr 2018
    Location
    Mpumalanga
    Posts
    43
    Thanks
    14
    Thanked 1 Time in 1 Post
    Quote Originally Posted by GCE View Post
    Hi

    That would fail a COC inspection without labels ( SANS 10142-1 : 4.2 pg 61 ) and no blanks , ( readily accessible live terminals 5.2 pg 63)
    Quote Originally Posted by AndyD View Post
    I can't see from the picture, is there a main OCPD?
    I'm lost. What is a OCPD used for?

  6. #15
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,934
    Thanks
    579
    Thanked 936 Times in 757 Posts
    OCPD = over current protective device ie circuit breaker that trips at a predetermined current or could even be a fuse. Some earth leakage breakers don't offer over-current protection, only earth leakage protection.
    _______________________________________________

    _______________________________________________

  7. Thanks given for this post:

    Ishmaelmo (26-Oct-18)

  8. #16
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by AndyD View Post
    OCPD = over current protective device ie circuit breaker that trips at a predetermined current or could even be a fuse. Some earth leakage breakers don't offer over-current protection, only earth leakage protection.
    In most cases...Over current protection is not required in domestic installations...the breaker feeding the DB would generally be a 50 or 60 amp...the cable feeding the db will be a 10 or 16 mm...which protects the cable and the tails from the earth leakage to the top of the breakers.

    Over current protection is "generally" only required in larger 3 phase DB's where there is earth leakage on each phase fed from a supply rated higher than 60 amps....in which case you would fit a 60 amp circuit breaker before the earth leakage.

  9. #17
    Full Member
    Join Date
    Apr 2018
    Location
    Mpumalanga
    Posts
    43
    Thanks
    14
    Thanked 1 Time in 1 Post
    Thanks everyone. I really learned a lot.

Page 2 of 2 FirstFirst 12

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •